<br><br>On Sunday, September 2, 2012, Richard L Ratico  wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">If the clients have a Trimetric or similar meter, perhaps they could be trained<br>

to power some loads with their inverter, while simultaneously charging their<br>
batteries and minding the charge rate, rather than tweaking the CC setup. Make<br>
hay while the sun shines so to speak, particularly when the battery is small<br>
relative to the array.<br>
<br>
Dick<br>
<br>
--- You wrote:<br>
Thanks Dan/Dick and Larry $E2Ai<br>
<br>
My concern was too high a charge rate, particularly when the batteries are<br>
cycled during or after an outage when the controllers are delivering maximum<br>
current and the inverter is not selling, yet not wanting to limit the charge<br>
controllers when we$E2Aore back in grid tied mode. Outback noted that you can<br>
just limit the controllers during extended outages, but I would prefer that<br>
customers not have to make adjustments to the charge rates.<br>
<br>
What I failed to consider is the particularly high charge rates that AGMs are<br>
able to withstand compared to FLAs. With a few tweaks to the system design we<br>
can easily hit a ~ .25C rate which is ideal for the batteries.<br>
<br>
I like the perspective of the inverter as diversion controller when it$E2Aos in<br>
sell mode.<br>
<br>
Thanks again for your help!<br>
<br>
Rich<br>
<br>
<br>
<br>
From: <a href="javascript:;" onclick="_e(event, 'cvml', 're-wrenches-bounces@lists.re-wrenches.org')">re-wrenches-bounces@lists.re-wrenches.org</a><br>
[mailto:<a href="javascript:;" onclick="_e(event, 'cvml', 're-wrenches-bounces@lists.re-wrenches.org')">re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of<br>
<a href="javascript:;" onclick="_e(event, 'cvml', 'dan@foxfire-energy.com')">dan@foxfire-energy.com</a><br>
Sent: Sunday, September 02, 2012 11:01 AM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] Grid tie with BB<br>
<br>
<br>
<br>
I'm with Dick. I liken grid tied inverters to diversion controllers. MPPT charge<br>
controllers (In Grid Tie Mode / talking to a HUB), pretty much just track a max<br>
power from the array. Good luck.<br>
<br>
<br>
<br>
db<br>
<br>
<br>
<br>
<br>
Dan Brown<br>
Foxfire Energy Corp.<br>
Renewable Energy Systems<br>
(802)-483-2564<br>
<a href="http://www.Foxfire-Energy.com" target="_blank">www.Foxfire-Energy.com</a><br>
NABCEP #092907-44<br>
<br>
<br>
<br>
-------- Original Message --------<br>
Subject: Re: [RE-wrenches] Grid tie with BB<br>
From: <a href="javascript:;" onclick="_e(event, 'cvml', 'Richard.L.Ratico@VALLEY.NET')">Richard.L.Ratico@VALLEY.NET</a> (Richard L Ratico)<br>
Date: Sun, September 02, 2012 9:16 am<br>
To: <a href="javascript:;" onclick="_e(event, 'cvml', 're-wrenches@lists.re-wrenches.org')">re-wrenches@lists.re-wrenches.org</a><br>
<br>
Rich,<br>
<br>
If I understand your question, I think you're missing the functioning of the<br>
inverter. Working independently of the charge controller, it will sell to<br>
prevent overcharging the batteries. Correctly configuring the inverter's voltage<br>
thresholds accomplishes this.<br>
<br>
Dick Ratico<br>
<br>
<br>
--- You wrote:<br>
Wrenches,<br>
<br>
I'm have a mental block with battery backup systems such as the Outback<br>
Radian. Perhaps someone can help me get over it!<br>
<br>
Essentially these systems sell back power off the top of the battery bank<br>
and the array is maintaining the state of charge of the battery bank through<br>
traditional charge controllers. If you have a modest battery bank sized for<br>
limited use on critical circuits and a good size array for the benefit of<br>
net metering I would think it would be necessary to limit the current the<br>
charge controllers are capable of delivering to the battery bank to prevent<br>
damage to the batteries when the controllers are Bulking or Absorbing, but<br>
then it would seem that we limiting the utility of the larger array. If the<br>
current from the controllers was not limited they will self-limit as voltage<br>
rises, plus I suppose they will mostly be in float mode except when the<br>
batteries are cycled but again it seems that we are limiting the capability<br>
of the array compared to a straight grid tied system with a traditional grid<br>
tied only inverter.<br>
<br>
An example would be a 8000 watt array using a couple of flexmax80<br>
controllers with a string of 8 - L16 AGMs feeding a Radian.<br>
<br>
What am I missing here?<br>
<br>
Thanks<br>
<br>
Rich<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="javascript:;" onclick="_e(event, 'cvml', 'RE-wrenches@lists.re-wrenches.org')">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>