    Wrenches,<br>
    More on the monitoring of GTWB systems, using a TriMetric, from
    Ralph Heisey, the developer of the TriMetric. Please include Ralph
    (<a class="moz-txt-link-abbreviated" href="mailto:bogart@bogartengineering.com">bogart@bogartengineering.com</a>) in any further discussion.<br>
    Allan<br>
    <br>
    <div class="moz-forward-container">Hi Allan
      <div>For grid tie systems that are only quite occasionally
        discharged, I have suggested that people set the TriMetric <br>
        voltage setpoint to just below the FLOAT voltage setting, and
        set the amps setpoint to a LOW value that is a little above the
        float current.  Then it will stay at 100%  during float, and
        when occasionally the batteries are used the "% full" display
        will be useful. But after an occasional partial discharge, the
        voltage will go to absorb (presumably) but the meter won't reset
        to "100" until the amps decline, and the system goes back to
        float.</div>
      <div><br>
      </div>
      <div>I don't have this kind of system myself-- so I would be
        interested in knowing if this seems like a good solution-- or if
        not, why it is not.</div>
      <div><br>
      </div>
      <div>Ralph<br>
        <div><br>
          <div class="gmail_quote">
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div bgcolor="#FFFFFF" text="#000000">
                <div> -------- Original Message --------
                  <table border="0" cellpadding="0" cellspacing="0">
                    <tbody>
                      <tr>
                        <th align="RIGHT" nowrap="nowrap"
                          valign="BASELINE">Date: </th>
                        <td>Fri, 10 Aug 2012 13:54:20 -0700 (PDT)</td>
                      </tr>
                      <tr>
                        <th align="RIGHT" nowrap="nowrap"
                          valign="BASELINE">From: </th>
                        <td><a moz-do-not-send="true"
                            href="mailto:toddcory@finestplanet.com"
                            target="_blank">toddcory@finestplanet.com</a></td>
                      </tr>
                      <tr>
                        <th align="RIGHT" nowrap="nowrap"
                          valign="BASELINE">To: </th>
                        <td>RE-wrenches <a moz-do-not-send="true"
                            href="mailto:re-wrenches@lists.re-wrenches.org"
                            target="_blank"><re-wrenches@lists.re-wrenches.org></a></td>
                      </tr>
                    </tbody>
                  </table>
                  <br>
                  <br>
                  <font face="arial" size="4">
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">actually this is not the
                        problem i have with amp hour meters on grid tie
                        with battery systems. </span></p>
                    <p style="margin:0;padding:0"><br>
                      a floated battery does <span
                        style="text-decoration:underline">not</span>
                      need an occasional bulk charge. it is being float
                      charged which compensates for any internal self
                      discharge. the only thing needed is an occasional
                      eq to stir the electrolyte.</p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">here is how the meter
                        inaccuracy problem happens:</span></p>
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">amp hour meters treat
                        charge and discharge differently. normally this
                        is a good thing, because batteries are not 100%
                        efficient. on a grid tie system, the batteries
                        are floated nearly the whole time... but there
                        are still small charge and discharge currents
                        going in and out of the battery. with an amp
                        hour meter set at 99% efficiency, it will still
                        take 101 amp hours of charging to off set 100
                        amp hour of discharging. <span
                          style="text-decoration:underline">this is what
                          leads to the inaccuracy</span> (where the
                        meter progressively shows an increasing
                        discharge to the battery). if there was the
                        ability to set an amp hour meters efficiency at
                        100% the inaccuracy would not accumulate... but
                        when the grid is down, the meter will falsely
                        show faster recharge because the batteries are
                        probably around 90% efficient... so that is not
                        a great solution either.</span></p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">this is why my idea to
                        leave the amp hour meter set to automatically
                        determine battery efficiency, and use a time
                        delay relay to short out the shunt when the grid
                        is up. when the grid is down the shunt would be
                        back in the circuit and the meter would perform
                        accurately. the time delay feature on the relay
                        would allow for a couple of hours of recharging
                        after the grid is restored before the shunt was
                        taken out of the circuit again.</span></p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">it seems strange to have
                        to come up with hackey solutions like this for
                        more and more common battery back-up grid tie
                        systems.</span></p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"><span
                        style="font-size:14pt">todd</span></p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0"> </p>
                    <p style="margin:0;padding:0">On Friday, August 10,
                      2012 7:51am, "Mick Abraham" <a
                        moz-do-not-send="true"
                        href="mailto:mick@abrahamsolar.com"
                        target="_blank"><mick@abrahamsolar.com></a>
                      said:<br>
                      <br>
                    </p>
                    <div>
                      <p style="margin:0;padding:0">Happy Friday, all~<br>
                        <br>
                        Allan & Todd were discussing the issue where
                        a "reset type" amp hour battery monitor (such as
                        TriMetric) never gets to "reset to full" when
                        operating on a GTWBB "grid tie with battery
                        backup" system...because the battery stays in
                        float and the monitor never sees a bulk charge
                        voltage. <br>
                        <br>
                        The problem here seems to reside more with the
                        chicken than with the egg. A battery in "float"
                        for long intervals will actually still undergo
                        some self discharge,  so it needs an occasional
                        "rebulk" charge to restore full state of charge.
                        <br>
                        <br>
                        <strong>Inverter manufacturers please take note
                          that a simple addition to your code base could
                          cause a GTWBB inverter to rev up the battery
                          charge voltage back through the
                          bulk/absorption phase on a calendar basis such
                          as once per month. </strong>Victron Energy
                        already does this with their inverter/chargers
                        but Victron is not certified for US terrestrial
                        and it's not set up for grid tie.<br>
                        <br>
                        If the inverter system would do an occasional
                        "rebulk", that would also cause the battery
                        capacity monitor to reset. Until that function
                        becomes automatic within the inverter(s), the
                        next best suggestion is for the client to
                        manually simulate a power company blackout once
                        per month by cycling the input AC breaker off,
                        then on. This kicks up a bulk cycle, ensures
                        good SOC on the battery, stirs up the
                        electrolyte if the batteries are floodies, and
                        resets the battery capacity monitor all with a
                        single intervention. <br>
                        <br>
                        The same manual intervention might also serve as
                        a good time for the owner to check water levels
                        on a flooded pack, near the end of the charge
                        cycle. <br>
                        Jolliness,<br>
                        <br>
                        Mick Abraham<br>
                      </p>
                    </div>
                  </font></div>
              </div>
            </blockquote>
          </div>
        </div>
      </div>
      <br>
      <br>