Happy Friday, all~<br><br>Allan & Todd were discussing the issue where a "reset type" amp hour battery monitor (such as TriMetric) never gets to "reset to full" when operating on a GTWBB "grid tie with battery backup" system...because the battery stays in float and the monitor never sees a bulk charge voltage. <br>

<br>The problem here seems to reside more with the chicken than with the egg. A battery in "float" for long intervals will actually still undergo some self discharge,  so it needs an occasional "rebulk" charge to restore full state of charge. <br>

<br><b>Inverter manufacturers please take note that a simple addition to your code base could cause a GTWBB inverter to rev up the battery charge voltage back through the bulk/absorption phase on a calendar basis such as once per month. </b>Victron Energy already does this with their inverter/chargers but Victron is not certified for US terrestrial and it's not set up for grid tie.<br>

<br>If the inverter system would do an occasional "rebulk", that would also cause the battery capacity monitor to reset. Until that function becomes automatic within the inverter(s), the next best suggestion is for the client to manually simulate a power company blackout once per month by cycling the input AC breaker off, then on. This kicks up a bulk cycle, ensures good SOC on the battery, stirs up the electrolyte if the batteries are floodies, and resets the battery capacity monitor all with a single intervention. <br>

<br>The same manual intervention might also serve as a good time for the owner to check water levels on a flooded pack, near the end of the charge cycle. <br><br>The Wrench List is the bomb! Jolliness,<br><br clear="all">