    Wrenches,<br>
    What are you using when you need a shunt larger than the standard
    500A/50mV?<br>
    <br>
    The application: four Sunny Islands and a Radian in a large grid-tie
    with backup system. Total current flow through B- is rated 850A
    (using 125A SI DC breakers) or 1,050A (using 175A DC breakers) on a
    single large battery bank. Given uncertain continuous amperage, I
    should use a 1,000A shunt or even a 1,200A shunt, as Deltec
    recommends never exceeding 67% of a shunt's current rating for long.
    Deltec makes both; see <a class="moz-txt-link-freetext" href="http://www.deltecco.com/MKC-DC.html">http://www.deltecco.com/MKC-DC.html</a>. The
    shunt will be installed inside of a Nottagutter-8, with a Midnite
    shunt bus on each side. The shunt will be used with the Sunny Island
    master to control overall SOC and charging parameters; there's no
    plan for a Tri-Metric in this system, as a Sunny Webbox will handle
    online monitoring per the customer's wishes.<br>
    <br>
    The 1,000 and 1,200A series MKC Deltec shunts are the same physical
    dimensions as the common 500A/50mV units. However, the larger units
    are still 50mV. Ralph Heisey of Bogart Engineering, in his
    "Information on Shunts" reference article
    (<a class="moz-txt-link-freetext" href="http://www.deltecco.com/MKC-DC.html">http://www.deltecco.com/MKC-DC.html</a>), tells us to match the ratio
    of voltage drop to current - that is, just as a 500A shunt drops
    50mV, a larger shunt with 1,000A flowing through it should drop
    100mV. But all of the larger Deltec shunts are still rated 50mV.<br>
    <br>
    Who has done this and resolved the issue? What shunt did you use?<br>
    <br>
    Thank you,<br>
    Allan <br>
    <div class="moz-signature">-- <br>
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          Founder and Chief Technology Officer<br>
          <b>Positive Energy, Inc.</b><br>
          3209 Richards Lane (note new address)<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
  </body>
</html>