<DIV><FONT size=2 face=Arial>I am helping a client troubleshoot a 
complaint about underproduction of his on-grid system installed about 6-8 years 
ago. At first I thought I might encounter the bad Kyocera KC120 issue but 
it turns out they have BP170's, 40 of them for an STC power rating of 6.8kW. 
</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Ratings of the BP modules: PTC=150.7, Vmp=35.4, 
Voc=44.2, Imp=4.8, Isc=5</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>The system has four panels of ten modules wired in 
series for a nominal rating of about 350v, 4.8a per string.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>At the DC disconnect (first accessible combiner) I 
measured: All strings right at about 375v(oc), 4.7a(mp). After the strings 
are combined, at the DC input of the SB6000 (with the AC power to the inverter 
OFF) I measured about 375V as expected. Once the AC 
power is connected, the SB6000 starts up, and MPP operation is 
initiated, the DC voltage drops to about 280V, and amps sit between 14 
& 15A.  I didn't think the voltage was supposed to drop upon MPP 
tracking...especially this much. This voltage drop would account for the 
observed power loss between actual and rated production values. I'm going to 
check with SMA but I wanted to ask the experts here too, as someone may advise 
something like, "Oh yeah, BP modules have a similar defect as the 
Kyocera..."</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>My questions:</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Is the DC voltage supposed to drop significantly in 
MPP mode on these inverters?</FONT></DIV>
<DIV><FONT size=2 face=Arial>If not, does this indicate a bad 
inverter?</FONT></DIV>
<DIV><FONT size=2 face=Arial>Anyone know of problems with BP modules 
manufactured around 2006-2008?</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>The Kyocera modules showed good volts and amps 
until a load was connected. Seems like a similar issue here.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Eric Stikes<BR>SunHarvest Solar<BR>A Sustainable 
Energy Group Partner<BR>+1 (530) 798 - 3738<BR><A 
href="http://www.harvesthesun.com">www.harvesthesun.com</A></FONT></DIV></BODY></HTML>