I could be wrong, but I thought the FM60 and FM80 charge controllers have adjustable current limits that apply to battery charging, and I think when integrated with GVFX inverters in sell mode and a Mate controller, you will be able to accomplish what you need to do without a relay. I always thought when the charge controller indicated GT Mode and was in bulk charging mode that the current limit would be essentially ignored because the battery voltage is above the sell voltage and any available DC current would be inverted and sold to the grid. In other words, the batteries are full, so they are not being charged - the FM60 and GVFX communicate and balance the current available for selling.<div>

<br></div><div>You may want to talk to Outback about that, because I don't think it is documented all that well, and again, I could be wrong. I've never installed that much solar on a small battery, so it never came up! Incidentally, I have someone that came in today looking for a 5kW grid-interactive system and a small battery to handle critical loads. I was leaning to an AC coupled system to get away from the issue you describe, but now I am second-guessing that theory. I'd be interested to learn what you discover.</div>

<div><br></div><div>Most inverter manufacturer's have a minimum battery size, but that seemingly is there to address the maximum possible current out of the battery, not the charging rate because that can be limited, too.<br>

<div><br clear="all">Jason Szumlanski<div>Fafco Solar</div><div><br></div><br><div class="gmail_quote">On Thu, Jul 19, 2012 at 5:20 PM, Drake <span dir="ltr"><<a href="mailto:drake.chamberlin@redwoodalliance.org" target="_blank">drake.chamberlin@redwoodalliance.org</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
Hello Wrenches,<br><br>
Where can I get a device that will measure current through a shunt and
create a signal to trigger a relay?   <br><br>
We want to be able to use a 2 kW array with four, 200 AH sealed batteries
on an Outback system.  2 kW of PV would be too much amperage for the
batteries.  The idea is to open relays to disengage strings in
conditions of high current to the batteries.<br><br>
The reason for this is to create backup systems where power will be
abundantly available when the sun shines. The system will normally
connect to the grid, except during outages.  In normal charging
conditions the power will go straight to the grid.  When the grid is
down, power will be available for loads and battery charging, but
batteries will be protected from overcharge?<br><br>
Any suggestions on ways to accomplish this are welcome!<br><br>
Thanks<br><br>
Drake <br><br>
<br>
<a name="138a11e49f5d8cd3__MailAutoSig"></a>Drake Chamberlin<br>
<i>Athens Electric LLC<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified Solar PV Installer<br>
<a href="tel:740-448-7328" value="+17404487328" target="_blank">740-448-7328</a><br>
</i><a href="http://athens-electric.com/" target="_blank">http://athens-electric.com/</a>
<br>
</div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>