    <div class="moz-cite-prefix">Mick,<br>
      <br>
      The SunExtender technical manual says to charge at 2.385 ± 0.015
      volts per cell at 25°C until the charge current drops to 0.5% of
      the battery capacity. That's 28.6 ±0.2 volts for a 24 volt system
      and 28.8 volts is the top end of that range. If you are seeing
      signs that the batteries have vented, the voltage probably has
      been too high. Since venting causes permanent water loss, with
      these batteries it's probably better to have the absorption
      voltage a little on the low side rather than on the high side of
      the recommended range. It's really important to have a temperature
      sensor and a temperature compensated charge controller too. <br>
      <br>
      It takes a lot more than one hour of absorption time for the
      current to drop down to 0.5% of capacity; three or maybe four
      hours might do it.<br>
      <br>
      If the end amps is set to 45, then the battery capacity should be
      9000 amphours, otherwise it'll be terminating the charge too soon.
      Realistically, you may as well disable the end amps feature.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>


</pre>
      On 7/7/2012 2:53 PM, Mick Abraham wrote:<br>
    </div>
    <blockquote
cite="mid:CABOJ=XQpVaoxuMAnvXuhxMAUAxN60=R0W7ETNtFs1GkXNjYT1g@mail.gmail.com"
      type="cite">Greetings, All~<br>
      <br>
      My client's string of SunXtender two volt AGM's won't hold a
      charge...after only two years! The prior AGM batteries also turned
      to toast prematurely. There must be a better way, so could we
      review the Outback charge setpoints? <br>
      <br>
      Side note: Delta-v from the highest 2v cell to the lowest shows a
      gap of only .148v during a charge cycle so cell imbalance is not
      the likely problem. I think they're all working together equally
      bad. <br>
      <br>
      A small amount of dry powder--light green color resembling
      verdegris finish on copper--can be seen around 30% of the +/-
      posts, in an amount smaller than 1/8 teaspoon. From this sign, I
      suspect that the cells have vented and dried out. The property is
      vacant 90% of the time so I am mostly focused on the MX60 solar
      charge controller as the culprit.<br>
      <br>
      This is an early vintage Outback controller, firmware version
      5.11. Temperature compensation is in place; automatic EQ is
      defeated. Bulk & absorption setpoints exactly match those
      requested by Concorde/SunXtender: 28.8 volts bulk/absorption &
      26.4 volts Float. The controller does regulate at these voltage
      points so it's technically "working"--just grinding up batteries
      on a regular basis.<br>
      <br>
      The Concorde people do not furnish suggestions regarding
      absorption time or "rebulking" so that may be the source of
      trouble. Controller setpoints have the Absorption Time Limit set
      for "0 minutes minimum & 1 hour maximum". The controller is
      also set to "rebulk" the battery at a 23 volt trigger and there's
      an inscrutable setpoint called "End" that's set for 45 amps. I
      have a theory about the meaning of that but I'll keep the noise
      level down...<br>
      <br>
      If I recall correctly, the Outback end of charge routine in early
      days was to start a clock & see how long it takes to move the
      battery to the bulk/absorption voltage then apply an equal amount
      of time for an absorption charge before shifting to float. Steve
      Higgins may confirm if that is indeed the protocol for a version
      5.11 controller but: has that method now been changed in the newer
      version Flexmax controllers? It seems those now have an absorption
      duration value that can be changed so maybe that's what we need--a
      replacement controller along with good information on the
      absorption duration and/or float setpoints, etc. <br>
      <br>
      I see that some controllers can even be set to not Float at all.
      Maybe that's better: run the charge then stop it all for the rest
      of the day. OR: thinking outside the box here...what about a
      controller that won't initiate charge cycle at all unless the
      battery voltage crests down to a trigger point. All I know for
      sure is that two sets of valuable batteries have now been ruined
      so "normal" charge setpoints are not working well in this
      situation.<br>
      <br>
      If some better electronics (such as blending in the Outback
      capacity monitor gizmo) might help, I'm all ears. Next time maybe
      I'll suggest flooded cells to the client instead of AGM's, but the
      cells are in a crawlspace that gets freezing cold at times. <br>
      <br>
      Thanks in advance for advice & suggestions. A second off grid
      client has a similar setup so I need to hotfoot it out there and
      tweak that (more recent) Outback controller to match the suggested
      setpoint revisions...before bad things happen again. <br>
      <br>
      Jolliness,<br>
      <br clear="all">
      Mick Abraham, Proprietor<br>
      <a moz-do-not-send="true" href="http://www.abrahamsolar.com"
        target="_blank">www.abrahamsolar.com</a><br>
      <br>
      Voice: <a moz-do-not-send="true" href="tel:970-731-4675"
        value="+19707314675" target="_blank">970-731-4675</a><br>
      <br>
    </blockquote>
    <br>
    <br>
  </body>
</html>