If you install a combiner panel that can supply additional branch circuits, it becomes part of the building distribution system. Note that Enphase recommends you install a branch circuit to supply power to the Envoy device right from the combiner panel. If that is the case, the panel is certainly part of the building distribution system and is obviously capable of supplying branch circuits, in which case the 120% rule would apply. I don't like it and I don't necessarily agree with it, but based on my strict interpretation of the code I can see why an AHJ would require application of this section in this case.<div>

<div><br clear="all">Jason Szumlanski<div>Fafco Solar</div><div><br></div><br>
<br><br><div class="gmail_quote">On Wed, Jun 27, 2012 at 10:59 AM, Chris Mason <span dir="ltr"><<a href="mailto:cometenergysystems@gmail.com" target="_blank">cometenergysystems@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

I don't think this is expressed in the code, but in my opinion, the 120% applies to the building distribution equipment, not to parts of the solar system. In the case where a panel is being used to combine multiple inverter outputs, the panel is part of the solar system only. The 120% rule was an accommodation to allow solar to feed a building distribution panel and is not applicable to solar system components. It would be good if the code could indicate this more clearly.<div>

<div class="h5"><br>
<br><div class="gmail_quote">On Wed, Jun 27, 2012 at 8:29 AM, Jason Szumlanski <span dir="ltr"><<a href="mailto:jason@fafcosolar.com" target="_blank">jason@fafcosolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">


Kirk,<div><br></div><div>That's basically what I said. Unfortunately, your opinion holds no weight with my local AHJ's. I've argued the point till blue in the face. Although, I have never had the instance where all available slots were filled in the combiner panel - I might be able to argue that case successfully.</div>


<span><font color="#888888">

<div><br></div></font></span><div><span><font color="#888888">Jason Szumlanski<div>Fafco Solar</div><div><br></div><br>
<br><br></font></span><div class="gmail_quote"><div><div>On Tue, Jun 26, 2012 at 4:53 PM, Kirk Herander <span dir="ltr"><<a href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>></span> wrote:<br>
</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div>

<div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="color:#1f497d">Jason,<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal">




<span style="color:#1f497d">In your email below you state:<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1f497d">“</span>You DO need to observe the 120% rule for the combining subpanel, regardless of whether there are loads present, at least in jurisdictions where I have worked. I've heard that some inspectors will allow you to ignore it if it is labeled as a PV combiner with "add no loads" notation.<span style="color:#1f497d">”<u></u><u></u></span></p>




<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1f497d">NEC 705.12 (D) states that the distribution equipment (in this case the combiner panel, fed by multiple inverters and a utility source) must be “capable of supplying multiple branch circuits or feeders or both” for (D)(1) through (7) to apply. If you fully populated a combiner panel with inverter breakers, leaving no slots for load breakers, it is not capable of supplying branch circuits or feeders, and IMO the 120% rule does not apply to the combiner buss or the conductors back to its point of utility interconnect. I have argued this point as well as label combiners “load circuits prohibited” (with or without available slots) and received AHJ approval.<u></u><u></u></span></p>




<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1f497d">You could also just lock shut a combiner that had spare slots as a deterrent to adding load breakers.<u></u><u></u></span></p>




<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>




<p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Kirk Herander<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">VT Solar, LLC<u></u><u></u></span></p>




<p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">dba Vermont Solar Engineering<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">NABCEP<sup>TM </sup>Certified installer Charter Member<u></u><u></u></span></p>




<p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">NYSERDA-eligible Installer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d">VT RE Incentive Program Partner<u></u><u></u></span></p>




<p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><a href="tel:802.863.1202" value="+18028631202" target="_blank">802.863.1202</a></span><span style="font-size:18.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u><u></u></span></p>




<p class="MsoNormal"><span style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Jason Szumlanski<br>




<b>Sent:</b> Tuesday, June 26, 2012 8:28 AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] Enphase grid tie question<u></u><u></u></span></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">I'll email you off-list a 1-line diagram from a system with 164 microinverters broken down into 8 strings in a 208V system. This particular system used two subpanels to accumulate PV, but that was only because we had to backfeed two existing subpanels due to the size of existing 480/208V transformers. You will have to look at the utility service and all existing equipment.<u></u><u></u></p>




<div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Regarding the breakers in the subpanel, you will only need a maximum of a 20A breaker for each string. The max inverters per string is 25 and the calculation for OCPD is:<u></u><u></u></p>




</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">215W / 208V x 25 inverters / 1.732 x 1.25 = 18.65A<u></u><u></u></p></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">




<span style="color:#1f497d">“</span>You DO need to observe the 120% rule for the combining subpanel, regardless of whether there are loads present, at least in jurisdictions where I have worked. I've heard that some inspectors will allow you to ignore it if it is labeled as a PV combiner with "add no loads" notation.<span style="color:#1f497d">”</span><u></u><u></u></p>




</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Use a MLO panel with a fusible disconnect between the subpanel and the interconnection point. If you use a 225A panel, you can feed it with 270A. With eight 20A backfed PV circuits, you would need to protect the line side of the panel with a 100A fusible disconnect. That probably isn't going to work. You may be best off from a cost perspective using two 225A subpanels and two 60A fusible disconnects. Anything larger than a 60A 3P disconnect and the price skyrockets. It all depends on your circuit calculations and the existing equipment. Of course, you would need two spaces for your interconnection point.<u></u><u></u></p>




</div><div><div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Jason Szumlanski<u></u><u></u></p><div><p class="MsoNormal">Fafco Solar<u></u><u></u></p></div></div></div><p class="MsoNormal" style="margin-bottom:12.0pt">




<u></u> <u></u></p></div></div></div><br></div></div><div>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></div></blockquote></div><br></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div></div></div><div class="im">-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>

</div><div>
Cell: <a href="tel:264.235.5670" value="+12642355670" target="_blank">264.235.5670</a></div><div>Skype: netconcepts</div><br>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>