I would use a 200A sub panel with 8 x 25A breakers to accumulate the PV output, as I doubt you could install 8 3Ph breakers in your main panel, and why would you want to?<div>You shouldn't need to observe the 120% rule for the main breaker on the main panel as there are no loads. Same for the panel rating.</div>
<div>The main panel would need a 200A breaker for the PV input and 120% comes into play. Be careful that breaker is rated as bi-directional.</div><div><br></div><div>Chris</div><div><br><br><div class="gmail_quote">On Mon, Jun 25, 2012 at 10:39 PM, Jesse Dahl <span dir="ltr"><<a href="mailto:dahlsolar@gmail.com" target="_blank">dahlsolar@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><br>
All,<br>
<br>
I'm looking for ideas on the electrical integration of the following system:<br>
<br>
800A service<br>
PV system employing enphase 215W inverters broken down into 8 output circuits.  Each circuit will be 208V 3 phase 20A.<br>
<br>
The question is on how to grid tie this.  My first thought is a sub panel for PV intertie only.  I saw a similar diagram on the enphase website, using 5 circuits and a 125A panel....<br>
<br>
What are people doing in situations like this?<br>
<br>
Thanks as always.<br>
<br>
<br>
Jesse<br>
Sent from my iPad!!!<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>Cell: 264.235.5670</div>
<div>Skype: netconcepts</div><br>
</div>