    Steve,<br>
    <br>
    A PV system GFDI integrated into the charge controller certainly
    simplifies charge controller installations. Unfortunately every
    charge controller that has done that has failed to correct a serious
    flaw in the operation of the GFDI: under a ground fault
    circumstance, the energized PV negative wire (and all those wires
    that are still connected to it) remains a serious safety hazard. I
    can tolerate that hazard in the PV system wiring; the PV modules are
    energized by sunlight so there will be energized wires. But
    energized wiring running past the GFDI should not be tolerated. NEC
    690.5(C) requires a label that is visible from the batteries warning
    that, if a ground fault is indicate, normally grounded wires may be
    energized. That's a good warning for someone that might be doing
    maintenance on the batteries. Trouble is the dc wiring to the
    inverters, lights, refrigerator, or anything else may also be
    energized. It's a dangerous circumstance that isn't necessary and
    shouldn't be allowed. If the external GDFI device were to simply
    open both PV+ and PV- conductors, there would be no hazard except
    between the GFDI and the PV array. The NEC, as now written, even
    allows both conductors to be opened. It's an easy fix, at least with
    the external GFDI it is an easy fix, to a design flaw that has the
    potential to kill someone. Outback shouldn't simply put a GFDI in
    the charge controller, they should design one that is safe too.<br>
    <br>
    It is safe to return to the list now. The rant is over.<br>
    <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
    <br>
    On 5/23/2012 12:18 PM, Steve Higgins wrote:
    <blockquote
cite="mid:8AD915B7D0FD164A800605B95BC387030C4A4080@mbx024-w1-ca-1.exch024.domain.local"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.18999">
      <div dir="ltr" align="left"><span class="434411319-23052012"><font
            color="#0000ff" face="Arial" size="2"> </font></span></div>
      <div dir="ltr" align="left"><span class="434411319-23052012"><font
            color="#0000ff" face="Arial" size="2">From what I
            understand, future controllers from Outback Power will
            incorporate the Ground Fault detection into the controller.
          </font></span></div>
      <div dir="ltr" align="left"><span class="434411319-23052012"></span> </div>
      <div dir="ltr" align="left"><span class="434411319-23052012"></span> </div>
      <div align="left"><font face="Arial" size="2">
          <div align="left"><font face="Arial" size="2">Steve Higgins</font></div>
          <div align="left"><font face="Arial" size="2">Sales
              Application Engineering Mgr</font></div>
          <div align="left"><font face="Arial" size="2">Direct
              360-618-4313</font></div>
          <div align="left"><font face="Arial" size="2">Outback Power
              Technologies </font></div>
          <div align="left"><font face="Arial" size="2">5917 195th
              Street N<span class="727134612-11072011">E</span>
              Arlington, Washington 98223</font></div>
          <div align="left"> </div>
        </font></div>
      <div> </div>
      <br>
      <div dir="ltr" class="OutlookMessageHeader" align="left"
        lang="en-us">
        <hr tabindex="-1">
        <font face="Tahoma" size="2"><b>From:</b>
          <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
          [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
          <b>On Behalf Of </b>William Miller<br>
          <b>Sent:</b> Wednesday, May 23, 2012 11:22 AM<br>
          <b>To:</b> RE-wrenches<br>
          <b>Subject:</b> Re: [RE-wrenches] Finding ground faults<br>
        </font><br>
      </div>
      Steve:<br>
      <br>
      IMHO, a brilliant suggestion.<br>
      <br>
      William Miller<br>
      <br>
      <br>
      At 11:19 AM 5/23/2012, you wrote:<br>
      <blockquote class="cite" cite="" type="cite">Steve,<br>
        <br>
        It would be appropriate for the GFDI to have 80-amp rated
        contacts that do not have an over-current trip mechanism. IMHO,
        the fact that they can trip on over-current and unnecessarily
        interrupt the dc system bond is a serious design flaw.<br>
        <br>
        <pre>Kent Osterberg