    Todd<br>
    <br>
    Sounds like everything is probably working normally. The power
    factor of the grid interactive inverter is probably close to 1.0 so
    when you are exporting power the power factor will go down.
    Actually, I'm assuming that the power factor is normally somewhat
    reasonable to begin with. It is possible, but unlikely, that the
    power factor without the solar system operational was nearly zero.
    The attached file demonstrates what is going on. In addition to the
    solar system exporting 1.0 kW, you had a load of 2.03 kW at a power
    factor of 0.65. The solar system reduced the load the utility meter
    sees to 1.03 kW, but it didn't change the kVAR.<br>
    <br>
    Since they have provided you with a fancy meter, check out what it
    says just after you turn off the inverter.<br>
    <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>

</pre>
    On 5/7/2012 7:46 PM, <a class="moz-txt-link-abbreviated" href="mailto:toddcory@finestplanet.com">toddcory@finestplanet.com</a> wrote:
    <blockquote cite="mid:1336445214.195718736@webmail.finestplanet.com"
      type="cite"><font face="arial" size="4">
        <div id="SafeStyles1336443436">
          <div>
            <div class="gmail_quote">
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">wrenches,</blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">i have
                a question about my home's system. i was one of the
                first net metered systems in our area, so the utility
                company installed a fancy dual register meter which also
                displays kvar/power factor.</blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">when
                selling 1 kW today the power factor was .40 and the kvar
                was 2.37.</blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">this
                sounds horrible. <span style="font-size: 14pt;">question:
                  is this a concern?</span></blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">todd</blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;"><br>
              </blockquote>
            </div>
          </div>
        </div>
      </font><br>
      <br>
    </blockquote>
  </body>
</html>