    Here is Robin's 2 cents worth on this subject....<br>
    <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">In

        a PV input circuit to a charge controller that has a 63 or 80
        amp DC-GFP, it is perfectly legal to use a small wire. That is
        because you will also have the appropriate sized breaker in
        series with the DC-GFP breaker. If you want to use 10AWG wire,
        you will need a 30 amp DC breaker in series with your 63 or 80
        amp DC-GFP breaker. The DC-GFP is being used as a switch, not as
        a breaker. I used to use an 80 amp switch on the dual Outback
        DC-GFP rather than a breaker, but it really does not matter if
        it is a breaker or a switch. The real over-current disconnect
        breaker is the device that should determine your wire size. <o:p></o:p></span></p>
    <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I’m

        not sure why Outback changed the DC-GFP to the battery circuit?
        It will work, but you still are required to have another breaker
        in series with it. The NEC intends for the DC-GFP to be
        installed in the PV circuit. <o:p></o:p></span></p>
    <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">If

        you need a 100 amp DC-GFP, then you will need to use a Classic.
        I cannot think of any system today that would require a 100 amp
        DC-GFP though.<o:p></o:p></span></p>
    <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Robin
        Gudgel<o:p></o:p></span></p>
    <span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">MidNite
      Solar</span><br>
    <br>
    <br>
    <br>
    <br>
    <br>
    <blockquote
      cite="mid:833BC721-4252-4F01-850B-755C8FA4645F@gmail.com"
      type="cite">
      <blockquote type="cite">
        <div>
          <blockquote
            cite="mid:6.0.1.1.2.20120417180352.02904358@millersolar.com"
            type="cite">
            <blockquote type="cite" class="cite" cite=""> <br>
              On 4/17/2012 11:08 AM, Nathan Stumpff wrote: <br>
              <blockquote type="cite" class="cite" cite="">Wrenches,<br>
                 <br>
                In a job coming up I have a customer with an existing
                FM60 controller,  520 watt (!!) array. We are doing a
                ton of work, including adding a 4 kW solar array with
                Classic 150 charge controller. I am trying to figure out
                how to handle the GFP.<br>
                 <br>
                For the Classic, I need a 90 or 100 A output breaker
                minimum. 80 A is not an option. The OutBack dual GFP is
                80 A, and so it not an option.<br>
                 <br>
                Is there a 100 A GFP breaker assembly I have just never
                seen? Is there a way to use the Classic’s GFP to run an
                external relay via AUX (to trip the FM60 output breaker
                at the same time)? Any ideas?<br>
                 <br>
                Thanks,<br>
                -Nathan<br>
                 <br>
                --<br>
                Nathan J. Stumpff - Arctic Sun, LLC<br>
                NABCEP Ceritified PV Installer #091209-175<br>
                <a moz-do-not-send="true"
                  href="mailto:nathan@arcticsun-llc.com">nathan@arcticsun-llc.com</a><br>
                Office: 907/457-1297<br>
              </blockquote>
              <br>
            </blockquote>
          </blockquote>
        </div>
      </blockquote>
    </blockquote>
  </body>
</html>