    Bill,<br>
    Jay's idea of trying the other AC input is a good one, if you're not
    also grid-connected and if you're not using the inverter to send a
    start signal, either manually or automatically.<br>
    The 8.5 RMY has very good regulation, so if it tests out for voltage
    and frequency, that's probably not the issue. And even at high
    elevation, the 8.5 can easily handle max AC input that the SW4024
    can draw - which Christopher Freitas tells me calculates out to 5647
    W.<br>
    <br>
    If you end up replacing it, either one would work fine. But why not
    consider a Magnum MS4024PAE, which has split-phase 120/240. Then the
    transformer is taken out of the system completely. Generally panels
    set up for straight 120 VAC can handle 120/240 without a hitch. The
    8.5 can easily be reconfigured to split-phase as well.<br>
    <br>
    As a rule of thumb, it takes about 2 kW of sine-wave inverter
    capacity per pump HP; 2.5 kW if mod-square, like DR. That's for a
    standard 3-wire capacitor-start submersible. <br>
    <br>
    I'd be interested in knowing where other Wrenches are finding SW
    parts and service. We haven't had need for it recently, but still
    expect to be able to get service through Inverter Service Company in
    Albuquerque, a division of Direct Power & Water. Where else is
    service available, assuming someone has kept the original box for
    shipping?<br>
    <br>
    I have a good used takeout unit if that's your customer's
    preference, although no box. Contact me off-list if this is of
    interest, and you have a box.<br>
    <br>
    Allan<br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 4/14/2012 7:21 PM, frenergy wrote:
    <blockquote cite="mid:1F3C37D6EED74425A26FBDA7945A61A2@D8XG8YH1"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta content="MSHTML 6.00.2900.6197" name="GENERATOR">
      <style></style>
      <div>Wrenches,</div>
      <div> </div>
      <div>        I have a customer that may be having some issues with
        the reliability of his 11 year old Trace4024.  If my current fix
        doesn't solve the problem, I have suggested having the unit
        fixed, which I think still happens on these puppies. I have also
        suggested replacing it with either an Outback 3524 or a Magnum
        MS 4024.  He is now running a 1 HP Submersible pump ala
        autoformer along with the usual array of  house loads.</div>
      <div> </div>
      <div>        The issue is the inverter accepting and then
        rejecting the generator power, which I have been watching recent
        comments here regarding this issue.  I have not thoroughly
        checked out pump wiring (was apparently already done by the
        well/pump guy, whom is reputable), but have checked the output
        of the Kohler 8.5 genny and Hz and voltage appear stable with
        and without load.  So far I've gone the route of programming in
        a few less amps on the "battery charging" and "AC2 IN"
        functions.   The inverter seems to be happy with new settings,
        this new programming was just done a few hours ago.</div>
      <div> </div>
      <div>        So this may be a more generic question for those with
        more experience than I: Are both the OB and Magnum inverters
        considered equally capable of replacing the Trace? I guess I'm
        thinking mainly of that pump, but are there other
        considerations?</div>
      <div> </div>
      <div>        Thanks Folks</div>
      <div> </div>
      <div>Bill</div>
      <div>Feather River Solar Electric<br>
        4291 Nelson St.<br>
        Taylorsville, CA  95983<br>
        530-284-7849/6544 fax</div>
      <div><font size="1"><em>solar powered since 1982</em></font></div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>