    Joel,<br>
    Use a Magnum PAE system for this. Their MS4448PAE with current
    firmware has frequency-shift capabilities, to allow control of the
    Enphases' output when the grid is down. The GT output should not
    exceed 80% of the Magnum(s) rated output; stacking is allowed here
    if needed. They still recommend a dump load as a fail-safe, although
    they're working on a diversion load accessory. I think there's
    technical material on Magnum's website showing how to do this.<br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 4/13/2012 6:07 PM, Joel Davidson wrote:
    <blockquote cite="mid:F65C1D177A804E0C8548B8DFAC9B731D@JOEL"
      type="cite">Wrenches,
      <br>
      I have a customer who wants solar modules and Enphase inverters,
      but he also wants PV and battery backup power during a grid
      outage. Are any wrenches doing this? How? Thanks for sharing your
      knowledge.
      <br>
      Joel Davidson
      <br>
      <br>
      _______________________________________________
      <br>
      List sponsored by Home Power magazine
      <br>
      <br>
      List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
      <br>
      <br>
      Options & settings:
      <br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
      List-Archive:
      <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
      List rules & etiquette:
      <br>
      <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
      <br>
      <br>
      Check out participant bios:
      <br>
      <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
      <br>
      <br>
      <br>
    </blockquote>
  </body>
</html>