Well the size of the subpanel sounds like a limiting factor, unless you find someway  around that via a bus/breaker size difference or upgrading to something larger.  And the AHJ/utility may want the PV disconnect by the main as you mentioned. However, 705.12(7) allows connecting to panelboards connected in series; and additional labeling requirements in 690.54 and 690.56(B) would apply if the PV system disconnecting means is not located with the service disconnecting means.<div>
<br><div class="gmail_quote">On Wed, Apr 11, 2012 at 10:09 AM, Aladdin Solar <span dir="ltr"><<a href="mailto:cpickard@aladdinsolar.com">cpickard@aladdinsolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<u></u>





<div bgcolor="#ffffff">
<div><font face="Arial">Wrenches:</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">There's probably an obvious answer but please help 
me think this through. Here's the situation--comes up all the time: The PV array 
and grid-tied inverter will be located on a detached building (garage or pole 
barn, etc.). The existing power to the building is a 240V 60A 
subpanel connected to the main panelboard at the house or main 
building via buried cable. If we obey buss bar loading and wire sizing, etc, is 
there any reason why we can't or shouldn't install the small grid tied PV system 
and tie it into the garage subpanel instead of trenching new lines 
back to the house and hit the main panel there? One hitch I see is 
that if we want a PV system AC disconnect near the main meter, 
the whole garage would end up on that. Have I overlooked an NEC 
or inverter requirement?</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">Thanks for your comments.</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">Charlie Pickard</font></div>
<div><font face="Arial">Aladdin Solar</font></div><br>
<br>
__________ Information from ESET NOD32 Antivirus, version of virus signature database 7045 (20120411) __________<br>
<br>
The message was checked by ESET NOD32 Antivirus.<br>
<br>
<a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br>


</div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div>========================</div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installer™ R031508-59<div>IREC ISPQ Certified Affiliated Instructor/PV US-0132<br>
<div>PV Curriculum Developer and Instructor<div>Solar Energy International<br>Carbondale, CO 81623<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div><br>
</div>