    Darryl,<br>
    As best I can tell, it's not related to the size of the load, but to
    the zero crossing of the waveform. I have also seen that the Magnum
    will start surprisingly large loads because it allows a greater AC
    voltage drop - I have seen down to 80 VAC on a 120 VAC output, where
    other inverters would hold to a greater voltage drop limit, but
    would shut down due to overload instead.<br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 3/26/2012 6:16 PM, Darryl Thayer wrote:
    <blockquote
      cite="mid:1332807404.15702.YahooMailNeo@web39304.mail.mud.yahoo.com"
      type="cite">
      <div style="color: rgb(0, 0, 0); background-color: rgb(255, 255,
        255); font-family: arial,helvetica,sans-serif; font-size: 12pt;">
        <div><span>I am puzzled because I have used and found the Magnum
            to start loads that other equally sized inverters could not
            start.  I wonder if the hot surface ignitor is not acting
            like a resistor but somehow non linear.  For the washer
            dryer the wave form was being distorted by the load and
            interfering with the controls?  I have started a two HP pump
            with a single Magnum, but I never looked at the wave
            shape.  </span></div>
        <div><span>Darryl  </span></div>
        <div><br>
        </div>
        <div style="font-family: arial,helvetica,sans-serif; font-size:
          12pt;">
          <div style="font-family: times new roman,new york,times,serif;
            font-size: 12pt;">
            <div dir="ltr"> <font size="2" face="Arial"> <b><span
                    style="font-weight: bold;">From:</span></b> "Larry
                Crutcher, Starlight Solar Power Systems"
                <a class="moz-txt-link-rfc2396E" href="mailto:larry@starlightsolar.com"><larry@starlightsolar.com></a><br>
                <b><span style="font-weight: bold;">To:</span></b>
                <a class="moz-txt-link-abbreviated" href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>; RE-wrenches
                <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a> <br>
                <b><span style="font-weight: bold;">Sent:</span></b>
                Monday, March 26, 2012 4:26 PM<br>
                <b><span style="font-weight: bold;">Subject:</span></b>
                Re: [RE-wrenches] Wood boiler ignition issue<br>
              </font> </div>
            <br>
            <div id="yiv1172450075">
              <div>
                <div>In the case of the Splendide washer/dryer (see link
                  in my previous post), it was definably the Magnum
                  Energy inverter. I could not start that load (no pun).
                  Since then we have tested several inverters with these
                  washers and all work fine except for the Magnum. I
                  must say that, other than this one fault, the Magnum
                  has been an exceptional, US made inverter and I
                  heartily recommend them.<br>
                  <div>
                    <span style="color: rgb(0, 0, 0); text-transform:
                      none; text-indent: 0px; letter-spacing: normal;
                      word-spacing: 0px; white-space: normal;
                      border-collapse: separate; orphans: 2; widows: 2;"
                      class="yiv1172450075Apple-style-span"><span
                        style="color: rgb(0, 0, 0); text-transform:
                        none; text-indent: 0px; letter-spacing: normal;
                        word-spacing: 0px; white-space: normal;
                        border-collapse: separate; orphans: 2; widows:
                        2;" class="yiv1172450075Apple-style-span">
                        <div style="word-wrap: break-word;"><span
                            style="color: rgb(0, 0, 0); text-transform:
                            none; text-indent: 0px; letter-spacing:
                            normal; word-spacing: 0px; white-space:
                            normal; border-collapse: separate; orphans:
                            2; widows: 2;"
                            class="yiv1172450075Apple-style-span"><span
                              style="color: rgb(0, 0, 0);
                              text-transform: none; text-indent: 0px;
                              letter-spacing: normal; word-spacing: 0px;
                              white-space: normal; border-collapse:
                              separate; orphans: 2; widows: 2;"
                              class="yiv1172450075Apple-style-span">
                              <div style="word-wrap: break-word;">
                                <div><br
                                    class="yiv1172450075Apple-interchange-newline">
                                  Larry Crutcher</div>
                                <div>Starlight Solar Power Systems</div>
                              </div>
                            </span></span>
                          <div>(928) 342-9103</div>
                          <span style="color: rgb(0, 0, 0);
                            text-transform: none; text-indent: 0px;
                            letter-spacing: normal; word-spacing: 0px;
                            white-space: normal; border-collapse:
                            separate; orphans: 2; widows: 2;"
                            class="yiv1172450075Apple-style-span"><span
                              style="color: rgb(0, 0, 0);
                              text-transform: none; text-indent: 0px;
                              letter-spacing: normal; word-spacing: 0px;
                              white-space: normal; border-collapse:
                              separate; orphans: 2; widows: 2;"
                              class="yiv1172450075Apple-style-span">
                              <div style="word-wrap: break-word;">
                                <div><u><br>
                                  </u></div>
                                <div><u><br>
                                  </u></div>
                              </div>
                            </span></span></div>
                      </span></span>
                  </div>
                  <br>
                  <div>
                    <div>On Mar 26, 2012, at 1:49 PM, Allan Sindelar
                      wrote:</div>
                    <br class="yiv1172450075Apple-interchange-newline">
                    <div> Kristopher,<br>
                      I have experienced this as well, but have no
                      solution to advise. My last direct experience with
                      this was about four years ago, when we installed a
                      system using a Magnum 4448 inverter in a home
                      system in which a high-efficiency
                      electronically-controlled hydronic boiler was also
                      installed at the same time. The particular boiler
                      proved unable to start up reliably on the
                      inverter, but would run reliably off of a
                      generator. Initially we assumed that the problem
                      was due to incorrect wiring by the heating
                      contractor (the AC input line and neutral had been
                      reversed). After this was corrected the problem
                      persisted. Before we could dig deeper the
                      contractor changed out the boiler to an equivalent
                      model of a different brand. The problem went away.<br>
                      <br>
                      You may end up having to either change the
                      inverter or change the boiler. Magnum's tech
                      support showed some interest in pursuing this,
                      even attempting to duplicate the problem, but we
                      never got that far. You might wish to contact them
                      about this - it's a legitimate problem.<br>
                      <br>
                      On a related note - has anyone had any issues with
                      powerline-carrier lighting controls run off of a
                      Radian? We haven't installed equipment yet, so
                      have no way to test until then. We're supplying
                      uninterruptible power to an upscale residential
                      observatory that will have this type of lighting
                      control. We have cautioned the GC that there's a
                      possibility of incompatibility, and no database of
                      collected data out there, and we don't assume
                      liability for incompatibilities. But it sure would
                      be nice to know if anyone else has seen issues. I
                      don't yet have a lighting brand.<br>
                      <br>
                      Thank you,<br>
                      Allan<br>
                      <br>
                      <div class="yiv1172450075moz-signature">
                        <title></title>
                        <font face="Times New Roman, Times, serif"><b>Allan
                            Sindelar</b></font><br>
                        <small><a moz-do-not-send="true"
                            href="mailto:Allan@positiveenergysolar.com"
                            rel="nofollow" target="_blank"
                            ymailto="mailto:Allan@positiveenergysolar.com"><font
                              color="#000099" face="Times New Roman,
                              Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
                          face="Times New Roman, Times, serif"><br>
                          <span style="font-size: 10pt;">NABCEP
                            Certified Photovoltaic Installer<br>
                            NABCEP Certified Technical Sales
                            Professional<br>
                            New Mexico EE98J Journeyman Electrician<br>
                            <b>Positive Energy, Inc.</b><br>
                            3201 Calle Marie<br>
                            Santa Fe, New Mexico 87507<br>
                            <b>505 424-1112</b><br>
                            <a moz-do-not-send="true"
                              href="http://www.positiveenergysolar.com/"
                              rel="nofollow" target="_blank"><u>www.positiveenergysolar.com</u></a></span></font>
                        <div style="margin-right: 722.25pt;"
                          class="yiv1172450075MsoNormal"><span
                            style="font-size: 10pt;"><b><br>
                            </b></span></div>
                        <span style="font-size: 10pt;"><br>
                        </span> </div>
                      <br>
                      On 3/26/2012 12:51 PM, Kristopher Schmid wrote:
                      <blockquote type="cite">
                        <div>Esteemed wrenches,</div>
                        <div>I am assisting in troubleshooting a stand
                          alone system with three stacked Magnum 4448
                          PAE inverters.  The electric ignition of LP
                          for the wood boiler will not fire from
                          inverter power.  As soon as we fire up the
                          generator, the boiler ignites.  Has anyone
                          seen this before?  Is there a solution?  The
                          boiler is a Central Boiler E-Classic 2400.</div>
                        <div>Thanks in advance!</div>
                        <div>----------<br>
                          Shine On!</div>
                        <div>Kris Schmid<br>
                          Legacy Solar, LLC<br>
                          864 Clam Falls Trail<br>
                          Frederic, WI 54837<br>
                          715-653-4295<br>
                          <a moz-do-not-send="true"
                            href="http://www.legacysolar.com/"
                            rel="nofollow" target="_blank">www.legacysolar.com</a><br>
                          NABCEP Certified PV Installer<br>
                          BSEE </div>
                      </blockquote>
                    </div>
                  </div>
                  <br>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
            <br>
            <br>
          </div>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>