    Kristopher,<br>
    I have experienced this as well, but have no solution to advise. My
    last direct experience with this was about four years ago, when we
    installed a system using a Magnum 4448 inverter in a home system in
    which a high-efficiency electronically-controlled hydronic boiler
    was also installed at the same time. The particular boiler proved
    unable to start up reliably on the inverter, but would run reliably
    off of a generator. Initially we assumed that the problem was due to
    incorrect wiring by the heating contractor (the AC input line and
    neutral had been reversed). After this was corrected the problem
    persisted. Before we could dig deeper the contractor changed out the
    boiler to an equivalent model of a different brand. The problem went
    away.<br>
    <br>
    You may end up having to either change the inverter or change the
    boiler. Magnum's tech support showed some interest in pursuing this,
    even attempting to duplicate the problem, but we never got that far.
    You might wish to contact them about this - it's a legitimate
    problem.<br>
    <br>
    On a related note - has anyone had any issues with powerline-carrier
    lighting controls run off of a Radian? We haven't installed
    equipment yet, so have no way to test until then. We're supplying
    uninterruptible power to an upscale residential observatory that
    will have this type of lighting control. We have cautioned the GC
    that there's a possibility of incompatibility, and no database of
    collected data out there, and we don't assume liability for
    incompatibilities. But it sure would be nice to know if anyone else
    has seen issues. I don't yet have a lighting brand.<br>
    <br>
    Thank you,<br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 3/26/2012 12:51 PM, Kristopher Schmid wrote:
    <blockquote
cite="mid:CAJB-iS_vuZsbn42qY_g6qNTY11PERms=mm60QJNsWtmxMTvEkg@mail.gmail.com"
      type="cite">
      <p>Esteemed wrenches,</p>
      <p>I am assisting in troubleshooting a stand alone system with
        three stacked Magnum 4448 PAE inverters.  The electric ignition
        of LP for the wood boiler will not fire from inverter power.  As
        soon as we fire up the generator, the boiler ignites.  Has
        anyone seen this before?  Is there a solution?  The boiler is a
        Central Boiler E-Classic 2400.</p>
      <p>Thanks in advance!</p>
      <p>----------<br>
        Shine On!</p>
      <p>Kris Schmid<br>
        Legacy Solar, LLC<br>
        864 Clam Falls Trail<br>
        Frederic, WI 54837<br>
        715-653-4295<br>
        <a moz-do-not-send="true" href="http://www.legacysolar.com">www.legacysolar.com</a><br>
        NABCEP Certified PV Installer<br>
        BSEE </p>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>