<p class="MsoPlainText">The funny thing about requiring a disconnect on both
sides of the meter is that the meter is only energized from one source - the utility.  And for that matter, 230.82 permits a meter
to be on the supply side of a service disconnect (it sounds like you were proposing the meter would be on the load side of the PV System Disconnect).  Anything having to do with the
arrangement between a meter and a disconnect (or disconnects) is either a local amendment,
utility requirement or an incentive program requirement.  Couldn't you even have a meter with no disconnect (as far as the NEC is concerned)?</p><p class="MsoPlainText">Isaac Opalinsky</p>