Mark:<br><br>
I would respectfully disagree, based on my reading.  If you have
code citations that inform me otherwise, I would be very grateful to
expand my knowledge.<br><br>
Pending hearing otherwise from you, here is what I know, based on 2008
code, and assuming load side connection  (2008 citations in
italics):<br><br>
1. <i>690.64(B)(1) Dedicated Overcurrent and Disconnect. Each 
source<br>
interconnection shall be made at a dedicated circuit breaker<br>
or fusible disconnecting means.<br><br>
</i>Each inverter will require a 40 amp circuit breaker.  The value
of that breaker is calculated by adding a 25% continuous duty rating to
the maximum AC output, which is 25 amps: 25 * 1.25 = 31.25.  The
next breaker size up is 40 amps, so you need 40 amp breakers.<br><br>
<i>2. 690.64(B)(2) Bus or Conductor Rating. The sum of the ampere<br>
ratings of overcurrent devices in circuits supplying power<br>
to a busbar or conductor shall not exceed 120 percent of the<br>
rating of the busbar or conductor.<br><br>
</i>The designer must add the values of the circuit breakers to determine
the back-feed value.  We just calculated the circuit breaker size in
step 1, above.  Four inverters means four 40 amp circuit breakers,
therefore: 4 * 40 = 160.  <br><br>
3. <i>In systems with panelboards<br>
connected in series, the rating of the first overcurrent<br>
device directly connected to the output of a utility interactive<br>
inverter(s) shall be used in the calculations for<br>
all busbars and conductors.<br><br>
</i>Therefore the designer must use 160 amps as the total back-feed value
for all panels and feeders in series all the way back to the
service.<br><br>
Mark, I would really appreciate it if you could reply today with any
information I am missing.  I could use my new-found knowledge to
modify the permit application I am submitting tomorrow morning.<br><br>
Sincerely,<br><br>
William Miller<br><br>
PS:  I used to think, erroneously, that I need only consider the
actual maximum AC amperage from a given inverter.  Some time ago I
bid on and started a job based on that fallacy.  Mid-way into the
job the AHJ informed me that my calculations were incorrect, that I
needed to use the breaker value.  This job used SB6000 inverters and
the value required was 40 amps.  I researched this thoroughly and
discovered they were right.  In order to comply with 690.640(B), I
had to downgrade the main breaker at my own expense.  The breaker
was not inexpensive, so this is a lesson I learned the hard 
way.<br><br>
This is why I am very interested in any knowledge that might prove
otherwise in this scenario.<br><br>
Wm<br><br>
<br>
At 10:36 AM 1/22/2012, you wrote:<br>
<blockquote type=cite class=cite cite>William,<br><br>
The SMA6000 @ 240V has an AC output rating of 25A. 4 times 25 times
1.25<br>
equals 125 A. If the solar accumulation panel is a dedicated load
center,<br>
then the load center, feeder and feeder breaker need only be rated to 125
A.<br>
If the dedicated load center is located in the same building as the
service,<br>
then the dedicated load center can be main lug without main breaker. If
the<br>
dedicated load center is located on a buidling remote from the the
service,<br>
then it will need a main breaker rated at 125A.<br><br>
 <br>
Mark Frye<br>
Berkeley Solar Electric Systems<br>
303 Redbud Way<br>
Nevada City,  CA 95959<br>
(530) 401-8024<br>
<a href="http://www.berkeleysolar.com/" eudora="autourl">www.berkeleysolar.com</a>
<br><br>
-----Original Message-----<br>
From: re-wrenches-bounces@lists.re-wrenches.org<br>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of William<br>
Miller<br>
Sent: Sunday, January 22, 2012 10:20 AM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] Paralleling Multiple Inverter<br><br>
Rich:<br><br>
Here is the first consideration you might want to make:  You state a value<br>
of 100 Amps for this system, which I assume is the maximum AC output at 240<br>
VAC (25 Amps) times four inverters.  The value of 25 amps per inverter is<br>
irrelevant to your design, however.  You must take the 25 amps times 1.25<br>
(for continuous duty) which means your required breaker is 40 amps (unless<br>
you can find 35 amps breakers).  40 Amps is the relevant value.  40 times 4<br>
equals 160 amps.  Therefore, for purposes of 690.64(B) calculations, you<br>
have a 160 amp system.<br><br>
Others on this list will no doubt provide advise on how to deal with that<br>
160 amps.<br><br>
William Miller<br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br><br>
No virus found in this incoming message.<br>
Checked by AVG - <a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.454 / Virus Database: 271.1.1/4158 - Release Date: 01/21/12 19:34:00</blockquote>
<x-sigsep><p></x-sigsep>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</body>
</html>