    I have a related question to this. Does setting up a pair of Outback
    GVFXs with the balancing transformer and allowing one inverter to go
    to sleep at lower AC output improve efficiency?  It seems we would
    be reducing electronic loads, but adding transformer losses.   Any
    comments? I have a recently commissioned double Outback system with
    200 AH @48v battery bank.  He's reporting efficiency at 77% DC in to
    AC out.  I'd love to improve that, as his aging array of Sharp
    modules seems to be under performing as well, (4.08 KW STC rated,  3
    Kw actual out)  I haven't gone back and done testing with my
    insolation meter, so I'm not sure exactly what is happening, but his
    overall efficiency (STC rated to AC out) is only 56% .<br>
    <br>
    Ray<br>
    <br>
    On 1/4/2012 7:55 PM, Maverick Brown [Maverick Solar] wrote:
    <blockquote cite="mid:A4F08B3A7C2746219FA24FD632D8CB46@MSE002"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.19170">
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">Please use the 90% of
            the CEC or PTC rating of the PV module at most.</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">Among several systems
            that I monitor daily, I have an example 11.760kw (STC)
            system that has a 500Ah battery bank and it peaks at 77-80%
            of the STC rating each day.</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">Peak is defined as the
            top of  the bell curve that forms from the graphing watts
            output versus nameplate watts.</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">If I use the CEC
            rating (10.54kw), it peaks at 86-90% of the CEC rating each
            day.</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">If I go to the CEC
            list and copy & paste into a spreadsheet and enter the
            values for the STC versus PTC, I <em>might</em>  find I
            would loose 10% (or more) in the PV rating.</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2"><a
              moz-do-not-send="true"
              href="http://www.gosolarcalifornia.org/equipment/pv_modules.php">http://www.gosolarcalifornia.org/equipment/pv_modules.php</a> (go
            ahead, find your modules and divide PTC by Nameplate).</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">I also have a
            grid-interactive system that has a very large battery bank
            (2600Ah @ 48V, with 9kw STC Array) and it only has a peak
            efficiency rating of 69% because of the load of the
            batteries. The larger the battery bank, the happier
            customers are for outage situations, but the larger the
            battery bank, the more current goes into "Floating" the
            batteries during selling. For that system, I may lower "Grid
            Support/SellRE" and use Auto EQ to keep the batteries
            fresh...</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">Anyway, keep in mind
            that you cannot simply assume:</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">12kw Array x 6 hours
            of sun =  72kwh of generation each day. The brand of PV, the
            size of the battery bank and even the charge controller's
            Absorb & Float settings can greatly reduce what the
            inverter thinks it can sell. With multiple inverters and
            charge controllers it gets even more complicated (worse).</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span><span
          class="683282302-05012012"></span><span
          class="683282302-05012012"><font color="#0000ff" face="Arial"
            size="2">Good luck,</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"><font
            color="#0000ff" face="Arial" size="2">Maverick</font></span></div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <div dir="ltr" align="left"><span class="683282302-05012012"></span> </div>
      <br>
      <div dir="ltr" class="OutlookMessageHeader" align="left"
        lang="en-us">
        <hr tabindex="-1">
        <font face="Tahoma" size="2"><b>From:</b>
          <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
          [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On
            Behalf Of </b><a class="moz-txt-link-abbreviated" href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a><br>
          <b>Sent:</b> Wednesday, January 04, 2012 5:14 PM<br>
          <b>To:</b> RE-wrenches<br>
          <b>Subject:</b> Re: [RE-wrenches] DC to AC derate<br>
        </font><br>
      </div>
      On 1/4/2012 3:01 PM, All Solar, Inc. wrote:
      <blockquote
        cite="mid:B5CBE3E26B764CC9987DB55BA8FD7972@SrvcTagGV13VB1"
        type="cite">
        <meta name="GENERATOR" content="MSHTML 8.00.6001.19088">
        <style></style>
        <div><font face="Arial" size="2">Wrenches,</font></div>
        <div><font face="Arial" size="2">Once again I am trying to size
            a grid tie w/battery system and I struggle a little with the
            efficiencies of them.</font></div>
        <div><font face="Arial" size="2">With PV Watts (v.1), is
            changing the DC to AC derate an accurate method for getting
            the output?</font></div>
        <div> </div>
        <div><font face="Arial" size="2">Thanks in advance!</font></div>
        <div> </div>
        <div><font face="Arial" size="2">Jeremy</font></div>
      </blockquote>
      <br>
      <br>
      If you keep the batteries charged  to a voltage just above their
      resting voltage,<br>
      say, 52 volts for a 48V system, and the battery bank isn't too
      large, (~225 A-hours,<br>
      maybe a bit more), about 90%  PV to grid AC efficiency is in the
      ball park.<br>
      <br>
      That's what we figured in the early days of GFX inverters at OB. 
      That's giving<br>
      5% for the electronics and 5% for keeping up the batteries.<br>
      Different and/or more accurate information may have come along
      since<br>
      that time.<br>
      <br>
      boB<br>