    Dan,<br>
    <br>
    While the battery box, or maybe the whole room they are in, do fit
    the definition of a Class 1 Division 2 location, I don't think it is
    consistent with the intent of that section. Wring methods for
    hazardous locations are specifically designed to keep the wiring
    isolated from the hazard. That notion doesn't work batteries - they
    are the source of the hazard and the wires do run to, and into,
    them. To be complaint with the requirements for hazardous locations
    the batteries would have to have integrated gas tight junction boxes
    enclosing the terminals. And interior of the battery would still
    remain an explosive environment with energized conductors no matter
    what is done to wiring on the exterior of the battery. Batteries are
    a special hazard and wiring methods specified for Class 1 Division 2
    locations won't mitigate that hazard.<br>
    <br>
    It takes a lot of ventilation to keep the H2 levels below the
    explosive threshold.<br>
    <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882</pre>
    <br>
    On 12/14/2011 4:46 PM, <a class="moz-txt-link-abbreviated" href="mailto:dan@foxfire-energy.com">dan@foxfire-energy.com</a> wrote:
    <blockquote
cite="mid:20111214174641.720a661d8db719b1f2ad39509c9edaa3.d5b0a341c0.wbe@email14.secureserver.net"
      type="cite"><span style="font-family:Verdana; color:#000000;
        font-size:10pt;">
        <div>I've mentioned it in the past, and got the impression it
          went over like a fart in church, but it seems to me buttoning
          up a battery box tighter than a bull's ass in fly season, and
          (hoping) mechanical ventilation mitigates this creation of a
          hazardous environment creates a Class I, Division 2 location.
          (NEC 500.5 (B)(2)(2)). </div>
        <div>Any takers?</div>
        <div>db<br>
        </div>
        <div><br>
        </div>
        <div><br>
          Dan Brown<br>
          Foxfire Energy Corp.<br>
          Renewable Energy Systems<br>
          (802)-483-2564<br>
          <a moz-do-not-send="true" href="http://www.Foxfire-Energy.com">www.Foxfire-Energy.com</a><br>
          NABCEP #092907-44</div>
        <div><br>
          <br>
        </div>
        <blockquote id="replyBlockquote" webmail="1" style="border-left:
          2px solid blue; margin-left: 8px; padding-left: 8px;
          font-size:10pt; color:black; font-family:verdana;">
          <div id="wmQuoteWrapper">
            -------- Original Message --------<br>
            Subject: Re: [RE-wrenches] NEC 480 - battery enclosure
            question<br>
            From: Ray Walters <<a moz-do-not-send="true"
              href="mailto:ray@solarray.com">ray@solarray.com</a>><br>
            Date: Wed, December 14, 2011 11:52 am<br>
            To: RE-wrenches <<a moz-do-not-send="true"
              href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
            <br>
            110.11 Deteriorating Agents. Unless identified for use in<br>
            the operating environment,<font color="#6600cc"> no </font>conductors
            or <font color="#6600cc">equipment<br>
              shall be located in damp</font> or wet <font
              color="#6600cc">locations; where exposed to</font><br>
            gases, fumes,<font color="#6600cc"> vapors</font>, liquids,
            or other agents <font color="#6600cc">that have a</font><br>
            <font color="#6600cc">deteriorating effect</font> <font
              color="#6600cc">on the conductors or equipment</font>; or<br>
            where exposed to excessive temperatures.<br>
            Informational Note No. 1: See 300.6 for protection against<br>
            corrosion.<br>
            <br>
            110.18 Arcing Parts. Parts of electrical equipment that in<br>
            ordinary operation produce arcs, sparks, flames, or molten<br>
            metal shall be enclosed or separated and <font
              color="#6600cc">isolated from all<br>
              combustible material.</font><br>
            <br>
            300.6 Has a lot of good info on corrosion that we in the
            solar biz should be all over, as well.<br>
            <br>
            So that's 3 pretty specific code references.<br>
            <br>
            Ray Walters<br>
            <br>
            On 12/13/2011 7:03 PM, <a moz-do-not-send="true"
              target="_blank" class="moz-txt-link-abbreviated"
              href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a>
            wrote:
            <blockquote cite="mid:4EE8040C.7060303@midnitesolar.com"
              type="cite">On 12/13/2011 5:47 PM, Dan Fink wrote: <br>
              <blockquote type="cite" style="border-left: blue 2px
                solid; margin-left: 8px; padding-left: 8px;">Esteemed
                Wrenches; <br>
                An email question from my recent Home Power article on
                charge controllers that I'm unsure of. <br>
                Does NEC specifically forbid mounting other gear, such
                as charge controllers, inside a battery enclosure? How
                about shunts? <br>
                It's not in 480 that I can see, and 480 doesn't seem to
                treat the interior of a battery enclosure as
                particularly explosive, because as per 480 it has to be
                adequately vented anyway. <br>
                Of course there are a zillion common-sense reasons not
                to actually DO that -- even an MX60 has a relay that can
                spark-- and of course corrosion on the controller
                terminals, circuit board, etc. Bad news all around and I
                never do it.  I learned this as an apprentice back in
                the 1990s, and I just don't do it. But I do put shunts
                in there sometimes...is this a no-no? The shunt
                terminals are brass, I've never seen any really nasty
                corrosion build up, but I'm quite curious. <br>
                BUT I'm wondering  if I'm missing something obvious in
                some other NEC section etc. <br>
                <br>
                Thanks in advance! <br>
                <br>
              </blockquote>
              <br>
              <br>
              Hi Dan.   Nice article, BTW ! <br>
              <br>
              <br>
              The NEC doesn't say that you CAN do this, but it does not
              dis-allow it either. <br>
              <br>
              It will come down to what the battery manufacturer says,
              is what we have found. <br>
              <br>
              Sealed batteries are the only ones that can be mounted in
              a battery box with <br>
              arc and spark equipment. <br>
              <br>
              Look at UPS's that you buy from COSTCO for instance.  They
              are UL listed, usually. <br>
              <br>
              boB <br>
              <br>
              <br>
              _______________________________________________ <br>
              List sponsored by Home Power magazine <br>
              <br>
              List Address: <a moz-do-not-send="true" target="_blank"
                class="moz-txt-link-abbreviated"
                href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
              <br>
              <br>
              Options & settings: <br>
              <a moz-do-not-send="true" target="_blank"
                class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
              <br>
              <br>
              List-Archive: <a moz-do-not-send="true" target="_blank"
                class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
              <br>
              <br>
              List rules & etiquette: <br>
              <a moz-do-not-send="true" target="_blank"
                class="moz-txt-link-abbreviated"
                href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
              <br>
              <br>
              Check out participant bios: <br>
              <a moz-do-not-send="true" target="_blank"
                class="moz-txt-link-abbreviated"
                href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
              <br>
              <br>
              <br>
              <br>
              <br>
            </blockquote>
            <hr>_______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
          </div>
        </blockquote>
      </span>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>