<DIV><FONT size=2 face=Arial>Allan,</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Thanks for reprinting the discussion. The retired 
engineer and his SW4048 are still both alive and doing well. Aside 
from the Trace SW4048 grid-tie low dc-to-ac efficiency (~65%), it is still one 
of the finest inverters ever made. In case I outlast my 13 year old SW4048, 
what new inverter has the same rugged durability but higher grid-tie 
efficiency?</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=allan@positiveenergysolar.com 
  href="mailto:allan@positiveenergysolar.com">Allan Sindelar</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</A> 
  </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Tuesday, November 22, 2011 8:07 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Convert Grid 
  Tie SW4048 to Backup System; Add New Inverter, AC Coupled</DIV>
  <DIV><BR></DIV>Nathan,<BR>I neither stated nor implied that the SW series 
  could be AC-coupled, because I don't know, friend. I have never had reason to 
  try this. The issue was discussed on this forum several years ago, and I have 
  found two key posts from David Katz of AEE about this topic in my email 
  Wrenches archives. David only addresses compatibility with early Sunny Boys. 
  The SW is true modified sine waveform, so whether is would be capable of 
  providing a reference signal to which a modern grid-tie inverter could latch 
  would be subject to several variables, and would likely vary among inverter 
  brands and models. Here's what David wrote on 4/15/2005, excerpted:<BR>
  <BLOCKQUOTE>I have connected Sunny Boy inverters directly to the output of 
    Xantrex SW inverters and Outback inverters. It works well. The Sunny Boy 
    operates when it sees the SW or Outback output.  Sometimes it shuts off 
    when a large load, like a pump is applied to the circuit, because it looks 
    like a grid failure. If the SB shuts off, it waits 5 minutes to turn 
    on.  If there is no AC load on the system and the SB is supplying 
    power, you will charge the batteries connected to the SW.  You need to 
    put a voltage controlled switch to turn of the AC between the Sunny Boy and 
    the sub panel if the battery voltage gets too high.<BR><BR>The SW is 
    bi-directional. if you put ac into the output, it charges the battery. The 
    AC in terminal is connected directly to the output through a relay. The 
    inverter is quite amazing. If you connect the output of the SB and the SW to 
    the same sub panel and turn off all loads you will see it charge the 
    battery. If you turn on loads to the point you are drawing more than the SB 
    is supplying, it will begin to draw power from the battery and supply the 
    excess that the SB is not supplying. I use an outback for backup power on my 
    grid connected house this way. As long as the SW in turned on, there is a 
    sine wave present at the AC output. This makes the SB think the grid is 
    present. I hope this answers your question. If not let me know and I will 
    try to draw a diagram. <BR>By the way, if you connect the AC input of the SW 
    or (FX) to a breaker in the main panel in a grid connected system it will 
    become your connection from the main panel to the sub panel (120VAC) and the 
    inverter will turn on whenever the grid fails and keep the SB running. If 
    you are using a 240 V SB, you will need an autotransformer or a second SW. 
    <BR>David <BR></BLOCKQUOTE>You mention the GTI below, but have not indicated 
  whether the SW you are considering is or isn't a GTI-equipped model. If it is 
  4.10/GTI-equipped, I'd suspect it's incompatible with AC-coupling. When one of 
  these is not selling (such as at night), has no loads on it but is 
  grid-connected, it is continually drifting between buy and sell by an amp or 
  two. Note that I have only observed this on the SW's meter display, which is a 
  pretty crude measurement. But I would expect that this would interfere with 
  any GT inverter's latching function, given the mandatory 5-minute waiting 
  period.<BR><BR>This is all based on observing one system that we installed 
  around 2002 for a well-known retired movie star. The system remains fully 
  operational today. We had an SW5548 (for most loads) and an SW 4048 (for 
  background loads with surge, like pumps) that were not series-stacked, in a 
  GTWB system, small by today's standards at 4.4kW of PV. Both inverters had 
  GTIs, but only one was set to sell, in order for the two SWs not to argue with 
  each other and to minimize their inherent float inefficiency previously noted. 
  <BR><BR>I'd guess your chances of AC-coupling would be better with a pre-GTI 
  unit. Others here may have had more experience with this question. 
  <BR><BR>Just to stir the pot some more, here is an email from Lloyd Gomm, then 
  at Xantrex, about the GTI/listing issue from 11/17/2003:<BR>
  <BLOCKQUOTE>Joel Davidson Wrote: 
    <BLOCKQUOTE style="COLOR: rgb(0,0,0)" type="cite">November 15, 2003 one of 
      our customers (maybe more) with a line-tie SW in Southern California 
      Edison territory got a notice from Xantrex dated October 22, 2003 about a 
      required firmware update. Anyone else get this notice? </BLOCKQUOTE>Joel, 
    this firmware update is necessary for SW inverters tested / listed by 
    UL.  This batch of SW's were produced by Xantrex between Q4 2000 and Q4 
    2001 and, to be clear, were de-listed by UL in November 2001. <BR><BR>This 
    firmware update is NOT required for ETL or CSA marked SW's tested to UL 1741 
    under the NRTL program.  Everything produced after Q4 2001 are CSA 
    marked, GTI compatible SW's.  Everything produced before Q4 2000 was 
    listed by ETL and is unaffected.  <BR>We have been working with SCE, 
    SDG&E, and PG&E to minimize impact on home owners and dealers.  
    The firmware update is easy to accomplish and we are compensating dealers to 
    do the work ( 2hrs per SW @ $65 per hour plus a $50 per site 
    allowance).  The compensation is paid by check within 2 weeks of 
    receipt of our form.  We have contacted all dealers who have customers 
    with an inverter that requires the update. <BR><BR>Joel Davidson Wrote: 
    <BLOCKQUOTE style="COLOR: rgb(0,0,0)" type="cite">This particular customer 
      is a retired aerospace engineer whose SW4048 was working fine, but still 
      had to get a GTI and now has to get some firmware. </BLOCKQUOTE>Joel, if 
    this customer has a GTI he does not require the firmware update.  
    Please contact me so we can update his information.  This will allow us 
    to close the loop with his utility. <BR><BR>If anyone requires any further 
    information on this program please contact me off list. <BR>Lloyd Gomm 
    <BR>Director, Marketing </BLOCKQUOTE>Allan<BR><BR>
  <DIV class=moz-signature><FONT face="Times New Roman, Times, serif"><B>Allan 
  Sindelar</B></FONT><BR><SMALL><A 
  href="mailto:Allan@positiveenergysolar.com"><FONT color=#000099 
  face="Times New Roman, Times, serif"><U>Allan@positiveenergysolar.com</U></FONT></A></SMALL><FONT 
  face="Times New Roman, Times, serif"><BR><SPAN style="FONT-SIZE: 10pt">NABCEP 
  Certified Photovoltaic Installer<BR>NABCEP Certified Technical Sales 
  Professional<BR>New Mexico EE98J Journeyman Electrician<BR><B>Positive Energy, 
  Inc.</B><BR>3201 Calle Marie<BR>Santa Fe, New Mexico 87507<BR><B>505 
  424-1112</B><BR><A href="http://www.positiveenergysolar.com/" 
  target=_blank><U>www.positiveenergysolar.com</U></A><O:P></O:P></SPAN></FONT> 
  <SPAN style="FONT-SIZE: 10pt"><BR></SPAN></DIV><BR>On 11/22/2011 8:10 AM, 
  Nathan Jones wrote: 
  <BLOCKQUOTE 
  cite=mid:1321974619.14258.yint-ygo-j2me@web113604.mail.gq1.yahoo.com 
  type="cite"><PRE wrap="">Bill,
I believe Allans post indirectly answered my question.  While he did not specifically state the SW could be used in an AC coupled arrangement, I believe it was implied. Since the listing issue, as I understand it, was due to failure to drop out of sell mode in a certain set of circumstances and never had anything to do with the behavior of the inverter in any of its "incoming AC only" settings as far as disconnecting there should not be any question as to its suitability for AC coupling there. The only question would be how they would react and manage backfed AC from a GTI in event of a grid failure. That question is unknown to me and has not been specifically answered yet. Any one have an answer to that?
Nathan Jones
Power Source Solar
Springfield, Mo
R
417-827-0738</PRE></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>