face="Times New Roman">Wrenches,<BR><BR>I answered Richard off-list, 
but other wrenches may find this information about old SW4048s and 
batteries useful.</FONT></FONT></DIV>
<DIV><FONT size=2 face=Arial><FONT size=3 
face="Times New Roman"></FONT></FONT> </DIV>
<DIV><FONT size=2 face=Arial><FONT size=3 face="Times New Roman">The SW4048 is a 
solid machine. We've been using one since 1998 and have sold hundreds of them 
for both on and off grid systems. We would leave what's working alone and 
replace and expand the battery bank to meet the client's expected grid outage 
hours. Our system has only 4 kWh of sealed batteries because we live in an area 
that gets almost no power outages and did not want to bother watering batteries. 
See info and wiring diagram at </FONT><A 
href="http://www.solarsolar.com/oursys.html"><FONT size=3 
face="Times New Roman">http://www.solarsolar.com/oursys.html</FONT></A><FONT 
size=3 face="Times New Roman"> <BR><BR>On the other hand, one of our clients in 
Malibu on the grid had an off-grid 5 kW PV system for backup power with 75 kWh 
of IBE flooded lead-acid batteries (2 parallel strings of 24 each 2-volt cells). 
We installed the system in 1993 but no one maintained the batteries properly. So 
in 1996 the dead IBE battery bank was replaced with a maintenance-free, sealed 
Absolyte battery bank that only lasted 4 years because of 40 F to 90 F 
temperature swings in the equipment room. A few years ago, we upgraded the 
system with a 31 kW array, 6 Sunny Boys, 2 Sunny Islands, and went back 
to a new set of 75 kWh of IBE cells like before. Now the batteries are 
inspected and watered every 2 to 6 months. We are still determining the right 
service period.<BR><BR>I have learned to buy good batteries, install them where 
the temperature stays 60 to 70 degrees F. as much as possible, inspect and water 
flooded batteries at least 2 times per year. All things being equal, sealed 
lead-calcium batteries cost twice as much and last half as long as flooded 
lead-antimony batteries. Most importantly, batteries are electro-chemical things 
just like living organisms. Keep them clean, fed (fully charged as much as 
possible), properly watered, at 70 degrees F, don't over-work them (deeply 
discharged without fully charging promptly), and they will last 6 to 8 years 
easily and often 12 years before old-age (high self-discharge) sets in. Battery 
bank owners that take care of themselves, their families, their animals, and 
their vehicles carry those good habits over to taking care of their battery 
banks. It's sad but true that people who are unhealthy and have vehicle problems 
all the time almost always have battery problems.<BR><BR>Best regards,<BR>Joel 
Davidson</FONT><BR><BR><BR></DIV></FONT>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=allan@positiveenergysolar.com 
  href="mailto:allan@positiveenergysolar.com">Allan Sindelar</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</A> 
  </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Sunday, November 20, 2011 8:21 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Convert Grid 
  Tie SW4048 to Backup System; Add New Inverter, AC Coupled</DIV>
  <DIV><BR></DIV>Kirk,<BR>I think there are a couple of subtleties that you're 
  missing in your post. All of the SW series that we installed in grid-tied mode 
  prior to Trace/Xantrex losing its 1741 listing - mostly Y2K installations - 
  are still in use legally, as they were grandfathered in. Once Xantrex lost its 
  listing and went to the GTI models (firmware rev. 4.10 and above), only with a 
  GTI were they 1741, and the earlier inverters couldn't be retrofit.<BR><BR>So 
  if Richard's customer's SW4048 is pre-GTI and is currently legitimately 
  utility-interactive, it could be argued that it's grandfathered in. Of course, 
  I'd avoid arguing anything that esoteric with any governing body. <BR><BR>But 
  it's a moot issue anyway. Reviewing the other Wrenches' suggestions, none 
  advised continuing to use the SW as an interactive inverter, but only as a 
  charging source for a battery bank. One Wrench suggested putting the SW's AC 
  input on a weekly timer, which is a good idea. Jay is correct that the SW was 
  a terrible inverter for grid-tie. One primary weakness of the SW series was 
  that as long as the grid was up, it tried to maintain float voltage to the 
  batteries continuously (this was the "lack of silent sell" issue). This 
  brought overall sell efficiency down to around 55%, as I recall, rather than 
  the 93+% efficiency of today's inverters. But if the inverter is only being 
  used as a charging source, it's not selling and thus neither the poor 
  efficiency nor the lack of a GTI is relevant.<BR><BR>Personally, I wouldn't 
  get rid of the SW if the customer wants battery backup. The inverters have 
  proven generally reliable, and this one is likely to last for decades as an 
  occasional battery charger. Plus it's already paid for, and does a good job as 
  both a battery charger and a backup inverter during outages. I'd use sealed 
  batteries to deal with the customer's maintenance concerns. The Honda 3000i is 
  a good choice at sea level, as the SW can hard-limit the AC amp draw from an 
  undersized generator and avoid overloading it (and nuisance-tripping its 
  output breaker). But note that the SW can take up to about 5,200 watts from an 
  AC source, and sealed batteries prefer high charging C/rates, so you might 
  want to use a generator of around 6kW (at 120V) instead for better efficiency 
  and less runtime.<BR><BR>Good thing Richard reposted - the second time got a 
  bunch of us responding. Kinda fun...<BR><BR>Allan<BR><BR>
  <DIV class=moz-signature><FONT face="Times New Roman, Times, serif"><B>Allan 
  Sindelar</B></FONT><BR><SMALL><A 
  href="mailto:Allan@positiveenergysolar.com"><FONT color=#000099 
  face="Times New Roman, Times, serif"><U>Allan@positiveenergysolar.com</U></FONT></A></SMALL><FONT 
  face="Times New Roman, Times, serif"><BR><SPAN style="FONT-SIZE: 10pt">NABCEP 
  Certified Photovoltaic Installer<BR>NABCEP Certified Technical Sales 
  Professional<BR>New Mexico EE98J Journeyman Electrician<BR><B>Positive Energy, 
  Inc.</B><BR>3201 Calle Marie<BR>Santa Fe, New Mexico 87507<BR><B>505 
  424-1112</B><BR><A href="http://www.positiveenergysolar.com/" 
  target=_blank><U>www.positiveenergysolar.com</U></A><O:P></O:P></SPAN></FONT> 
  <P style="MARGIN-RIGHT: 722.25pt" class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt"><FONT 
  face="Times New Roman, Times,             serif"><ST1:PLACE 
  w:st="on"><ST1:CITY w:st="on"></ST1:CITY><ST1:STATE 
  w:st="on"></ST1:STATE><ST1:POSTALCODE 
  w:st="on"></ST1:POSTALCODE></ST1:PLACE></FONT><B><BR></B></SPAN></P><SPAN 
  style="FONT-SIZE: 10pt"><BR></SPAN></DIV><BR>On 11/20/2011 4:33 AM, Kirk 
  Herander wrote: 
  <BLOCKQUOTE cite=mid:000d01cca778$3f799af0$be6cd0d0$@vtsolar.com type="cite"><PRE wrap="">PS - Richard, does it have a Trace / Xantrex GTI interface installed? If
not, it's not code-legal to be tied to the grid anyway. Get rid of the 4048
whatever you do.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner


-----Original Message-----
From: <A class=moz-txt-link-abbreviated href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A>
[<A class=moz-txt-link-freetext href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</A>] On Behalf Of Richard L
Ratico
Sent: Friday, November 18, 2011 6:53 PM
To: <A class=moz-txt-link-abbreviated href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</A>
Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New
Inverter, AC Coupled

Jay, Marv, Chris, Ray, Joel & Maverick,

Thanks tremendously for your input. Each of you provided interesting
suggestions, all of which I find thought provoking and helpful. I greatly
appreciate your taking the time to share your experience.

Dick
Solarwind Electric


--- You wrote:
We redid one in a very similar situation recently. In that case the 
customer wanted super backup and so we put in Grid tie Outbacks and a 
new battery bank, added modules, and kept the SWs as battery chargers 
from the generator. He had the option with bypass switches to use the 
SWs, if the Outbacks went out. This guy wanted a "keep the power going, 
no matter what" system, but I can't claim that was optimal.  The right 
answer depends on what the customer wants.
I probably wouldn't trash everything though as Jay suggested, since the 
existing modules are already racked and wired. (unless it's a bogus 
install, then yep, salvage it all)
You could probably easily rewire the parallel 48 v sets of modules all 
in series in 15 minutes in the combiner box to get the voltage up, and 
use a small GT only inverter, too. I guess it would also depend on how 
close the 2 different types of modules are in voltage or current, but it 
doesn't have to be perfect; as these were modules headed to the scrap 
heap otherwise.
In honor of modules that are well installed and still performing 
correctly, I do try and reuse them. Being able to brag: "these have been 
working for 30 years..." is great for the solar industry as a whole, but 
only if it makes sense.

Ray

On 11/17/2011 5:51 PM, jay peltz wrote:
</PRE>
    <BLOCKQUOTE type="cite"><PRE wrap="">HI Richard,

I'll chime in, although you won't like it.

Dump the system and start over with a new battery less system and a genny
</PRE></BLOCKQUOTE><PRE wrap="">as
back up.
</PRE>
    <BLOCKQUOTE type="cite"><PRE wrap="">Told you, you wouldn't like it.

The SW parts are basically gone and it was a terrible  grid tied inverter
</PRE></BLOCKQUOTE><PRE wrap="">anyway.
</PRE>
    <BLOCKQUOTE type="cite"><PRE wrap="">The modules are usable but why at $1.5 watt keep them?
Client doesn't want MX, so that means no batteries.

You'll need a genny as back up anyway for long power outages during
</PRE></BLOCKQUOTE><PRE wrap="">storms, so
get a natural gas/propane unit as back up instead of batteries.
</PRE>
    <BLOCKQUOTE type="cite"><PRE wrap="">OK you asked,

jay

peltz power
On Nov 17, 2011, at 4:03 PM, Richard L Ratico wrote:

</PRE>
      <BLOCKQUOTE type="cite"><PRE wrap="">Hi Wrenches,

This is a repost. No replies the first time, so I'm trying one last time.

I may be "adopting" an eleven year old, Y2K, grid tie with battery
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">back-up
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">system. It consists of 12 - Astro-Power 120 modules, installed in 2000,
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">12 -
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">Evergreen  EC-110 modules installed in 2004, only one MX60, which
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">controls
BOTH
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">sub-arrays, one SW4048 in SELL mode through a dedicated load sub-panel.
Existing, seven year old battery is shot (8-Trojan L-16). Initial bank of
unknown batteries was replaced after only four years.

Recent long, nearby, utility outages have the client requesting a
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">proposal to
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">include a new back-up generator and to restore the system selling to the
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">grid.
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">Client may decide go straight grid tie to eliminate the batteries. They
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">have
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">found the maintenance to be a hassle.

My thoughts so far:

1)To take advantage of most of the existing hardware, I wonder if it
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">makes
sense
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">to try to improve the system efficiency by relegating the SW to a manual
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">back-up
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">mode only, where, say, by means of a timer controlling grid availability
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">through
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">AC1, it would only charge a smaller battery bank once a week. The battery
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">bank
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">would be small,
a single string of either, sealed gel units or T-105s with the new Trojan
watering system.
2) Provide new grid-tie inverter/s (appropriate string type or Enphase
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">190s)
to
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">handle the net metering.
3) Provide a way to AC couple the new inverter/s to the SW in the event
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">of an
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">outage.
4) Provide a new Honda 3000 inverter type generator connected to AC2 in
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">the
SW.
</PRE>
    <BLOCKQUOTE type="cite">
      <BLOCKQUOTE type="cite"><PRE wrap="">5)Provide a way to lockout the grid tie inverter/s when the generator is
operating.

Any thoughts or suggestions would be greatly appreciated.

Thanks in advance,

Dick Ratico
Solarwind Electric
Bradford, VT
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE wrap="">--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: <A class=moz-txt-link-abbreviated href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A>

Options & settings:
<A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A>

List-Archive:
<A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A>

List rules & etiquette:
<A class=moz-txt-link-abbreviated href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A>

Check out participant bios:
<A class=moz-txt-link-abbreviated href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</A>

_______________________________________________
List sponsored by Home Power magazine

List Address: <A class=moz-txt-link-abbreviated href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A>

Options & settings:
<A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A>

List-Archive: <A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A>

List rules & etiquette:
<A class=moz-txt-link-abbreviated href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A>

Check out participant bios:
<A class=moz-txt-link-abbreviated href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</A>


</PRE></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 