The latest Outback product guide very specifically identifies the
maximum PV wattage for the FM60 and 80 at each nominal voltage. But
I see it's also in their website (middle column FM80, right column
FM60):<br>
<br>
<table cellspacing="1">
<tbody>
<tr>
<th>Maximum Solar Array STC Nameplate</th>
<td>12 VDC systems 1250 Watts / 24 VDC systems 2500 Watts / 48
VDC systems 5000 Watts / 60 VDC systems 6250 Watts</td>
<td>12 VDC systems 900 Watts / 24 VDC systems 1800 Watts / 48
VDC systems 3600 Watts / 60 VDC Systems 4500 Watts</td>
</tr>
<tr class="alt">
<th>NEC Recommended Solar Array STC Nameplate</th>
<td>12 VDC systems 1000 Watts / 24 VDC systems 2000 Watts / 48
VDC systems 4000 Watts / 60 VDC Systems 5000 Watts</td>
<td>12 VDC systems 750 Watts / 24 VDC systems 1500 Watts / 48
VDC systems 3000 Watts / 60 VDC Systems 3750 Watts</td>
</tr>
</tbody>
</table>
Allan<br>
<br>
<div class="moz-signature">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<title></title>
<font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
<small><a href="mailto:Allan@positiveenergysolar.com"><font
color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
face="Times New Roman, Times, serif"><br>
<span style="font-size: 10pt;">NABCEP Certified Photovoltaic
Installer<br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
<b>Positive Energy, Inc.</b><br>
3201 Calle Marie<br>
Santa Fe, New Mexico 87507<br>
<b>505 424-1112</b><br>
<a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
<p class="MsoNormal" style="margin-right: 722.25pt;"><span
style="font-size: 10pt;"><font face="Times New Roman, Times,
serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
style=""><br>
</b></span></p>
<span style="font-size: 10pt;"><br>
</span> </div>
<br>
On 11/19/2011 9:17 PM, <a class="moz-txt-link-abbreviated" href="mailto:maverick@mavericksolar.com">maverick@mavericksolar.com</a> wrote:
<blockquote
cite="mid:F975E80B-69DD-48A3-8DE5-A859AA4399F9@mavericksolar.com"
type="cite">
<div>Wow!</div>
<div><br>
</div>
<div>The most I have in one Outback install is 8 MX60s and 8
VFX3648s.</div>
<div><br>
</div>
<div>Overall the customer has been happy with the performance and
the stacking power save feature helps with idle power draw. <br>
<br>
As for the OPs request, the most PV still remains to be about
5000 watts gross power per controller (80A x 50V / 0.80), even
if they slice it up as high voltage or not high voltage type
controller. </div>
<div><br>
</div>
<div>Another curious idea is the cost per volt<span
class="Apple-style-span" style=""> when comparing 150V input,
80A Output controllers to the new high voltage input
controllers. That cost consideration spreadsheet is still
under construction.</span></div>
<div>
<div><br>
</div>
<div>Thank you,</div>
<div><br>
</div>
<div>Maverick</div>
<div><br>
</div>
<div><br>
</div>
<div>Maverick Brown</div>
<div>BSEET, NABCEP Certified Solar PV Installer ®</div>
<div>President & CEO</div>
<div>Maverick Solar Enterprises, Inc.</div>
<div>Office: 512-919-4493</div>
<div>Cell: 512-460-9825</div>
<div><br>
</div>
Sent from my HondaJet!</div>
<div><br>
On Nov 19, 2011, at 10:20 AM, Darryl Thayer <<a
moz-do-not-send="true" href="mailto:daryl_solar@yahoo.com">daryl_solar@yahoo.com</a>>
wrote:<br>
<br>
</div>
<blockquote type="cite">
<div>
<div style="color: rgb(0, 0, 0); background-color: rgb(255,
255, 255); font-family: arial,helvetica,sans-serif;
font-size: 12pt;">
<div><span>Hi </span></div>
<div><span>I have a system in operation since 2003 using 13
paralleled Outback MX 60 CC and I have measured over 600
Amps at 48 Volts.on the common bus. Outback and I
replaced the fans in the MX 60s but we have had no
failures. This power is converted to 60 hZ using 12
Outback inverters, I have had an inverter trip off on
the DC side just the other day and I will check it out
this comming week but no problems. </span></div>
<div><span>DT</span></div>
<div><br>
</div>
<div style="font-family: arial,helvetica,sans-serif;
font-size: 12pt;">
<div style="font-family: times new roman,new
york,times,serif; font-size: 12pt;"><font size="2"
face="Arial"><b><span style="font-weight: bold;">From:</span></b>
"Larry Crutcher, Starlight Solar Power Systems" <<a
moz-do-not-send="true"
href="mailto:larry@starlightsolar.com">larry@starlightsolar.com</a>><br>
<b><span style="font-weight: bold;">To:</span></b>
RE-wrenches <<a moz-do-not-send="true"
href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
<b><span style="font-weight: bold;">Sent:</span></b>
Friday, November 18, 2011 12:35 PM<br>
<b><span style="font-weight: bold;">Subject:</span></b>
Re: [RE-wrenches] High-power MPPT/Charge Controllers?<br>
</font><wbr>
<div id="yiv1967174141">
<div>Sounds like a project for Sunny Island and the
Boy's.<wbr>
<div>
<span style="font: 16px Helvetica; color: rgb(0,
0, 0); text-transform: none; text-indent: 0px;
letter-spacing: normal; word-spacing: 0px;
white-space: normal; border-collapse: separate;
orphans: 2; widows: 2;"
class="yiv1967174141Apple-style-span"><span
style="font: 16px Helvetica; color: rgb(0, 0,
0); text-transform: none; text-indent: 0px;
letter-spacing: normal; word-spacing: 0px;
white-space: normal; border-collapse:
separate; orphans: 2; widows: 2;"
class="yiv1967174141Apple-style-span">
<div style="word-wrap: break-word;">
<div><br
class="yiv1967174141Apple-interchange-newline">
Larry Crutcher</div>
<div>Starlight Solar Power Systems</div>
<div><br>
</div>
</div>
</span></span><br
class="yiv1967174141Apple-interchange-newline">
</div>
<wbr>
<div>
<div>On Nov 18, 2011, at 10:49 AM, Exeltech wrote:</div>
<wbr>
<blockquote type="cite">
<table border="0" cellpadding="0"
cellspacing="0">
<tbody>
<tr>
<td style="font: inherit;" valign="top">Need
info on MPPT/charge controllers able to
output up to 500A at 48Vdc.<br>
High-voltage DC input (up to 300Vdc)
preferred. Units will connect to a<br>
20-24 kW PV array and 150 kW-h battery
for a large off-grid system.<br>
Not locked into 48Vdc. Can go up to
108Vdc (nominal) if needed.<br>
<br>
Any such CC units available?<br>
<br>
If not, what's been the collective
Wrench experience in paralleling
multiple<br>
controllers of whatever max output
amperage exists on the market? I
realize<br>
a paralleled configuration of this
nature would entail multiple separate
arrays<br>
in use on the input. That won't be a
problem. Just need to be able to feed<br>
the common battery bank.<br>
<br>
Thanks.<br>
<br>
Dan<br>
<br>
</td>
</tr>
</tbody>
</table>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a moz-do-not-send="true"
href="mailto:RE-wrenches@lists.re-wrenches.org"
rel="nofollow" target="_blank"
ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a moz-do-not-send="true"
href="http://www.re-wrenches.org/etiquette.htm"
target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a moz-do-not-send="true"
href="http://www.members.re-wrenches.org"
target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
<wbr></div>
</div>
<wbr>_______________________________________________<wbr>List
sponsored by Home Power magazine<wbr><wbr>List Address:
<a moz-do-not-send="true"
href="mailto:RE-wrenches@lists.re-wrenches.org"
ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><wbr><wbr>Options
& settings:<wbr><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><wbr><wbr>List-Archive:
<a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><wbr><wbr>List
rules & etiquette:<wbr><a moz-do-not-send="true"
href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><wbr><wbr>Check
out participant bios:<wbr><a moz-do-not-send="true"
href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><wbr><wbr><wbr><wbr></div>
</div>
</div>
</div>
</blockquote>
<blockquote type="cite">
<div><span>_______________________________________________</span><br>
<span>List sponsored by Home Power magazine</span><br>
<span></span><br>
<span>List Address: <a moz-do-not-send="true"
href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
<span></span><br>
<span>Options & settings:</span><br>
<span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>List rules & etiquette:</span><br>
<span><a moz-do-not-send="true"
href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
<span></span><br>
<span>Check out participant bios:</span><br>
<span><a moz-do-not-send="true"
href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
<span></span><br>
</div>
</blockquote>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</body>
</html>