<html>
<body>
Romex sheath is not generally considered much protection.  The
intent of the code is that the tap wires that are not adequately
protected by the feeder over current protective device have hardened
physical protection.  My read is that they need to be in conduit or
some substantial enclosure. <br><br>
<br>
<blockquote type=cite class=cite cite="">Also at issue is the question:
is the romex wire protected "by other means"?  Judgement
call.<br><br>
See citation below from 240.21(B):<br><br>
<i>(2) Taps Not over 7.5 m (25 ft) Long. Where the length of<br>
the tap conductors does not exceed 7.5 m (25 ft) and the tap<br>
conductors comply with all the following:<br>
(1) The ampacity of the tap conductors is not less than<br>
one-third of the rating of the overcurrent device protecting<br>
the feeder conductors.<br>
(2) The tap conductors terminate in a single circuit breaker<br>
or a single set of fuses that limit the load to the ampacity<br>
of the tap conductors. This device shall be permitted<br>
to supply any number of additional overcurrent devices<br>
on its load side.<br>
(3) The tap conductors are protected from physical damage<br>
by being enclosed in an approved raceway or by other<br>
approved means.<br><br>
</i>End of citation<br><br>
William Miller<br><br>
<br><br>
<br><br>
<br><br>
At 01:06 PM 10/25/2011, you wrote:<br>
<blockquote type=cite class=cite cite="">William,<br><br>
The tap conductor ampacity must not be less than the rating of the
breaker<br>
protecting that circuit, which in this case (if I understand the
configuration<br>
correctly) would be the main breaker in the panelboard.<br><br>
Any smaller gauge would require its own OCP device of appropriate
rating<br>
if it's to be code-compliant.<br><br>
Dan<br><br>
<br><br>
--- On <b>Tue, 10/25/11, William Miller
<i><william@millersolar.com></i></b> wrote:<br>
<blockquote type=cite class=cite cite=""><br>
From: William Miller <william@millersolar.com><br>
Subject: Re: [RE-wrenches] Feeder without a dedicated breaker<br>
To: "RE-wrenches"
<re-wrenches@lists.re-wrenches.org><br>
Date: Tuesday, October 25, 2011, 2:54 PM<br><br>
Jamie:<br><br>
Thanks for getting me started.  I did not think to consider this as
a tap, but it appears to match the criteria.<br><br>
William Miller<br><br>
<br><br>
At 11:38 AM 10/25/2011, you wrote:<br>
<blockquote type=cite class=cite cite="">William, I would start with
Article 240.21(B).<br><br>
<b>Jamie
Johnson</b></blockquote></blockquote>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a><br><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.454 / Virus Database: 271.1.1/3972 - Release Date: 10/24/11
18:35:00</blockquote><br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">
http://millersolar.com</a><br>
License No. C-10-773985<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font size=2>Drake
Chamberlin<x-tab>        </x-tab>
<br>
ATHENS ELECTRIC LLC<br>
OH License
44810<x-tab>        </x-tab><br>
CO license 3773<br>
NABCEP Certified PV<br>
</font></body>