<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;">William,<br><br>The tap conductor ampacity must not be less than the rating of the breaker<br>protecting that circuit, which in this case (if I understand the configuration<br>correctly) would be the main breaker in the panelboard.<br><br>Any smaller gauge would require its own OCP device of appropriate rating<br>if it's to be code-compliant.<br><br>Dan<br><br><br><br>--- On <b>Tue, 10/25/11, William Miller <i><william@millersolar.com></i></b> wrote:<br><blockquote style="border-left: 2px solid rgb(16, 16, 255); margin-left: 5px; padding-left: 5px;"><br>From: William Miller <william@millersolar.com><br>Subject: Re: [RE-wrenches] Feeder without a dedicated breaker<br>To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org><br>Date: Tuesday, October 25, 2011, 2:54 PM<br><br><div id="yiv643002018">
<div>
<font size="3">Jamie:<br><br>
Thanks for getting me started.  I did not think to consider this as
a tap, but it appears to match the criteria.<br><br>
William Miller<br><br>
<br><br>
At 11:38 AM 10/25/2011, you wrote:<br>
</font><blockquote type="cite" class="yiv643002018cite" cite=""><font size="3">William, I would start with Article
240.21(B).<br><br>
<b>Jamie Johnson</b></font><b></b></blockquote></div>
</div><br></blockquote></td></tr></table>