Todd,<br><br>Article 250.52(a)(3) from the 2008 Code states this....<br><br>(3) Concrete-Encased Electrode. An electrode encased<br>by at least 50 mm (2 in.) of concrete, located horizontally<br>near the bottom or vertically, and within that portion of a<br>
concrete foundation or footing that is in direct contact with<br>the earth, consisting of at least 6.0 m (20 ft) of one or more<br>bare or zinc galvanized or other electrically conductive<br>coated steel reinforcing bars or rods of not less than 13 mm<br>
(1⁄2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of<br>bare copper conductor not smaller than 4 AWG. Reinforcing<br>bars shall be permitted to be bonded together by the<br>usual steel tie wires or other effective means. Where multiple<br>
concrete-encased electrodes are present at a building<br>or structure, it shall be permissible to bond only one into<br>the grounding electrode system.<br><br>It would be wise to consult the local AHJ if this is permisssble with the rebar. You want to make sure that you have the best grounding system possible with the chance of a lighting strike.<br>
<br>Good Luck!<br><br><br><div class="gmail_quote">On Thu, Sep 29, 2011 at 4:10 PM,  <span dir="ltr"><<a href="mailto:toddcory@finestplanet.com">toddcory@finestplanet.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<font face="arial" size="4"><p style="margin:0;padding:0"><span style="font-family:arial;font-size:14pt">Does anyone know if it is ok to use the rebar in a pole mount foundation as a ufer ground? I need to ask the </span><span style="font-family:arial"><span style="font-size:19px">inspector </span></span><span style="font-family:arial;font-size:14pt">too, but thought I'd ask here first.</span></p>

<p style="margin:0;padding:0;font-family:arial;font-size:14pt"> </p>
<p style="margin:0;padding:0;font-family:arial;font-size:14pt">Todd</p>
<p style="margin:0;padding:0;font-family:arial;font-size:14pt"> </p>
<p style="margin:0;padding:0;font-family:arial;font-size:14pt"> </p>
<div style="font-family:arial;font-size:14pt"></div></font><br><br><br>Sent from Finest Planet WebMail.<br><br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>