    Ray,<br>
    You referenced the wrong chart. Yours was for AGMs. Try
    <a class="moz-txt-link-freetext" href="http://www.surrette.com/content/specifications-renewable">http://www.surrette.com/content/specifications-renewable</a>.<br>
    Allan<br>
    <br>
    Ron,<br>
    At 48V, I could be tempted to pick the 16 golf carts. Disadvantages:
    More cells to water and smaller reservoirs. More interconnects, more
    floor space. Advantages: More capacity for less money. More
    tolerance for abuse. About the same real-world cycle life (just
    based on experience). Lighter gauge and thus less expensive
    interconnects. And two strings isn't too many. Like Ray, I'm not too
    enamored of L16s as a value-based choice, although we use a fair
    number. We typically see 4 1/2 - 7 years from L16s, and about the
    same from golf carts.<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 9/16/2011 8:37 PM, Ray Walters wrote:
    <blockquote cite="mid:4E7407E0.6080308@solarray.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      Here's the Rolls chart for cycle life:<br>
      <a moz-do-not-send="true" class="moz-txt-link-freetext"
        href="http://www.surrette.com/content/agm-faqs?q=node/81&php">http://www.surrette.com/content/agm-faqs?q=node/81&php</a><br>
      The cycle life is considered to be the point before the capacity
      begins being reduced. <br>
      I'm not seeing anything close to 800 cycles at 80%DOD. It looks
      like a typical L16, not over 500 cycles.<br>
      Are you using a different chart than what Rolls is posting on
      their website?<br>
      <br>
      Ray<br>
      <br>
      7 PM, Ron Young wrote:
      <blockquote
        cite="mid:2F90A461-17D4-40ED-AEAF-D1974F253928@solareagle.com"
        type="cite">Hi All,
        <div>Not sure where the 4 - 5 strings or more drifted into this
          conversation but the setup is basically in two strings of 16
          GC batteries (48v) vs. 8 L-16 batteries in one string that I
          am recommending. With 7 year warranty for the Surrettes vs 1
          year for the US Batt.; half the number of cells to water and
          check - and this is important as the maintenance on these 4
          systems is being done by a third party who is not always
          reliably taking care of business; half the number of
          connections; half the footprint ... </div>
        <div><br>
        </div>
        <div>The only reason I can see someone recommending GC batteries
          in this scenario has to do with the company who set the
          systems up - Xantrex and their rationale seems to be the easy
          availability of the GC batteries e.g. in automotive stores
          etc. vs the more specialized distribution of the L-16's.
          Xantrex want to sell "arrive and drop" systems that will be
          sold through mass retailers from what I can see.</div>
        <div><br>
        </div>
        <div>The Rolls d.o.d. at 80% shows 800 cycles for the 4000
          series batteries vs. 675 on the U.S. Battery chart but the
          U.S. battery chart doesn't differentiate between GC batteries
          and L-16's or any other type so I find it a bit suspect.</div>
        <div><br>
        </div>
        <div>Ron Young</div>
        <div>
          <div><span class="Apple-style-span" style="border-collapse:
              separate; color: rgb(0, 0, 0); font-family: 'Comic Sans
              MS'; font-size: medium; font-style: normal; font-variant:
              normal; font-weight: normal; letter-spacing: normal;
              line-height: normal; orphans: 2; text-indent: 0px;
              text-transform: none; white-space: normal; widows: 2;
              word-spacing: 0px;"><span class="Apple-style-span"
                style="border-collapse: separate; color: rgb(0, 0, 0);
                font-family: 'Comic Sans MS'; font-size: medium;
                font-style: normal; font-variant: normal; font-weight:
                normal; letter-spacing: normal; line-height: normal;
                orphans: 2; text-indent: 0px; text-transform: none;
                white-space: normal; widows: 2; word-spacing: 0px;"><span
                  class="Apple-style-span" style="border-collapse:
                  separate; color: rgb(0, 0, 0); font-family: 'Lucida
                  Grande'; font-size: medium; font-style: normal;
                  font-variant: normal; font-weight: normal;
                  letter-spacing: normal; line-height: normal; orphans:
                  2; text-indent: 0px; text-transform: none;
                  white-space: normal; widows: 2; word-spacing: 0px;">
                  <div><span class="Apple-style-span"
                      style="font-family: Helvetica; font-size: 12px;">
                      <div style="margin: 0px; font: 12px Helvetica;
                        min-height: 14px;">earthRight Products - <a
                          moz-do-not-send="true"
                          href="http://Solareagle.com">Solareagle.com</a></div>
                      <div style="margin: 0px;"><font style="font: 12px
                          Helvetica;" size="3" face="Helvetica">Alternative

                          Energy Solutions ~ Renewable Energy Products</font></div>
                      <div style="margin: 0px;"><br>
                      </div>
                    </span></div>
                </span></span></span> </div>
          <br>
          <div>
            <div>On 2011-09-16, at 1:06 PM, RM You wrote:</div>
            <br class="Apple-interchange-newline">
            <blockquote type="cite">forwarded from earth2<br>
              <br>
              <br>
              Begin forwarded message:<br>
              <br>
              <blockquote type="cite"><b><span style="font-family:
                    Helvetica; color: rgb(108, 108, 108);">From: </span></b><span
                  style="font-family: Helvetica;">Ray Walters <<a
                    moz-do-not-send="true"
                    href="mailto:ray@solarray.com">ray@solarray.com</a>><br>
                </span><b><span style="font-family: Helvetica; color:
                    rgb(108, 108, 108);">Date: </span></b><span
                  style="font-family: Helvetica;">September 16, 2011
                  1:03:43 PM PDT<br>
                </span><b><span style="font-family: Helvetica; color:
                    rgb(108, 108, 108);">To: </span></b><span
                  style="font-family: Helvetica;">RE-wrenches <<a
                    moz-do-not-send="true"
                    href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
                </span><b><span style="font-family: Helvetica; color:
                    rgb(108, 108, 108);">Subject: </span></b><b><span
                    style="font-family: Helvetica;">Re: [RE-wrenches]
                    battery cycle life, US Battery<br>
                  </span></b><b><span style="font-family: Helvetica;
                    color: rgb(108, 108, 108);">Reply-To: </span></b><span
                  style="font-family: Helvetica;">RE-wrenches <<a
                    moz-do-not-send="true"
                    href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
                </span><br>
                Larry, <br>
                <br>
                I totally agree, that's a ridiculous # of batteries and
                strings. If that's really the case, it seems L16s will
                still need 4 to 5 strings, which is also crazy. I see
                only one solution to this battery bank, and that is the
                HUP or other large 2 v cell battery. Comparing golf cart
                batteries to L16s isn't even on the plate for good
                design in this case. For me, HUPs become a no brainer,
                as soon as the required amp hours gets into the 1000 AH
                or higher range. BTW, don't ever use the 100 hr rate for
                the Rolls, as they are way too optimistic. The 20 hr
                rates are much closer to reality. The Rolls S-530
                becomes a 400 AH battery at the 20 hr rate, also they
                list cycles @50% DOD, when everyone else is looking at
                80%DOD, be aware.<br>
                Here's some quicky math, with costs pulled off the
                internet:<br>
                3 strings of S530s (@24v) would get you 1200 AH for
                $4200. cycle life at 80% DOD about 450 to 500 cycles.<br>
                HUPs group 25 have 1270 AH and cost $7392, but last 2100
                cycles to 80%DOD. <br>
                That's about 11.5 cents/ kwh for the life of the battery
                compared to about 29.2 cents/ kwh for the Rolls S-530s.
                <br>
                This quicky calculation doesn't even include the extra
                maintenance required for watering the L16 type battery,
                nor the fact that you will have 4 battery replacements
                for the same time the HUPs just have one replacement. <br>
                Its very fair to say that the HUPs are more cost
                effective by about a 3 to1 ratio.<br>
                <br>
                Ray<br>
                <br>
                <br>
                <br>
                 Having 6-8 parallel strings of golf cart batteries is a
                terrible idea no matter how much better the GC2 may be.<span
                  style="color: rgb(0, 61, 159);"><br>
                  <br>
                  Larry <br>
                  <br>
                  <br>
                  On Sep 16, 2011, at 10:01 AM, Ray Walters wrote:<br>
                </span><span style="color: rgb(0, 80, 13);">The real
                  point is that the Xantrex guy is correct from a
                  scientific stance. Experimental battery cycle life
                  data shows that some golf cart batteries (T105) do
                  have more rated cycles to 80%DOD than the Trojan L16.
                  (750 vs about 600) A really crappy golf cart battery
                  (some have cycle life below 400 cycles) isn't as good
                  as an L16, yes. You have to base your decision, and
                  your mouth, on test data for the batteries considered.
                  Also, you must always compare at 80% DOD, for an
                  apples to apples comparison. Its usually a clue if a
                  manu doesn't publish their cycle life data. Of course
                  you must temper the golf cart vs L16 decision with
                  good paralleling technique.<br>
                  We use golf cart batteries (never more than 4
                  strings), jump straight to the HUPs for larger banks,
                  and skip the L16s all together. They just don't make
                  sense when you look at the cost/ amp hr vs their
                  lifespan.<br>
                  The only time I could see using L16s, was if the
                  battery bank requirements were beyond 4 strings of
                  golf cart batteries, and the customer just could not
                  afford the HUPs, or were going to sell the property
                  soon, and wouldn't appreciate their long term value.<br>
                  I've spent a lot of time looking at cycle life data,
                  comparing costs, adding in maintenance and replacement
                  labor, etc..<br>
                  L16s are serious losers on a $/ kwh operating cost
                  comparison, so this is a chance to up sell the
                  customer to HUPs (or equivalent) and make both of you
                  happier in the long run.<br>
                  <br>
                  Ray Walters<br>
                  <br>
                  <br>
                </span>_______________________________________________<br>
                List sponsored by Home Power magazine<br>
                <br>
                List Address: <a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Options & settings:<br>
                <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                <br>
                List rules & etiquette:<br>
                <a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out participant bios:<br>
                <a moz-do-not-send="true"
                  class="moz-txt-link-abbreviated"
                  href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
                <br>
              </blockquote>
            </blockquote>
          </div>
          <br>
        </div>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>