<font size=3>Jay:<br><br>
I disconnected the AGS and the problem persisted.  Adding a load may
help but I did not test this.  This would require a permanent load
and might not be desirable.<br><br>
William<br><br>
<br><br>
At 07:36 AM 9/9/2011, you wrote:<br>
<blockquote type=cite class=cite cite>Hi William,<br><br>
is the problem the actual connection or the AGS?<br><br>
if its the actual connection, have you tried putting a load ( say 1000
watt heater) on the generator directly  to stabilize the volt/hz
from the genny?<br>
if for a test if nothing else.<br><br>
jay<br><br>
peltz power<br><br>
On Sep 8, 2011, at 9:40 PM, William Miller wrote:<br><br>
<blockquote type=cite class=cite cite>Friends:<br><br>
Working yesterday on a newer XW system with a new Kohler RES15
generator.  This is the first time I have tested the inverter with
this generator.  The inverter would not maintain a transfer to the
generator.  After about an hour on the phone with tech support, the
tech searched previous calls and announced that there is a known
incompatibility between the Kohler RES15 and a certain version of the XW
firmware.  I was advised to upgrade the firmware.<br><br>
I wonder how this can be.  Voltage and frequency even in the moment
the inverter did try to connect are well within specifications. After
some thought, all I can guess is that there might be some noise on the AC
signal that the inverter might reject.<br><br>
Has anyone else experienced this?  Any insight to be
offered?<br><br>
Thanks in advance.<br><br>