<DIV><FONT color=#008000 size=4 face=Arial>I am having similar issues, but with 
an older system with an 8.5RMY Kohler. However we replaced a control board on it 
several months ago. As this system goes back to Y2K, starting with a Trace Power 
Panel, and converting to the XW when they were first available, it had always 
connected to the Gen. with no issues. But recently, we've been getting fault 
codes when it exercised, which we thought were related to starting battery 
issues. Then, after lighting storms, the XW no longer accepted AC1, grid power, 
so we replaced the control board, which fixed AC1 . But in verifying system 
operation, we noticed that AC2 - Gen.- would not actually transfer and charge if 
started manually at the system control panel thru the AGS, nor would it exercise 
properly, as the generator shuts off after a minute or two, never having 
actually connected to the XW. Voltage at AC2 is 120 each leg. We have talked 
with every tech support at Schneider------------</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial></FONT> </DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Yesterday we did the firmware 
upgrade, which means for this older system, that the AGS senses the 'generator 
on' with out a separate sense wire, like was originally needed. But we are 
getting the same failure to connect and charge. We do get a sound like it is 
trying to connect, but only momentarily. We still have the same generator 
shutdown after a minute or two. The fault code on the SCP, says the generator 
turned off<STRONG>    at the 
generator .</STRONG></FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Now, since we just went thru the east 
coast hurricane, grid was down for this customer for 7 days. so when the 
generator is started    <STRONG>at the generator, manual start 
switch  </STRONG>the XW accepts the AC2 power perfectly, starting to charge 
within seconds, and going thru the regular bulk charge cycles properly I 
believe. So noise from the Kohler, at least this one, seems 
unlikely.</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial></FONT> </DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Next week, we'll be back there after 
discussing this with Kohler tech support.</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial></FONT> </DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Anyone else have something to add 
?</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial></FONT> </DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Thanks for your collective 
wisdom</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Ken Schaal</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial>CommonWealth Solar</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial>Ashland Va</FONT></DIV>
<DIV><FONT color=#008000 size=4 face=Arial><A 
href="http://www.commonwealthsolar.com">www.commonwealthsolar.com</A></FONT></DIV>
<DIV> </DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #008000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message -----   </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=william@millersolar.com href="mailto:william@millersolar.com">William 
  Miller</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, September 09, 2011 12:40 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] Help me understand 
  Gen vs XW</DIV>
  <DIV><BR></DIV>Friends:<BR><BR>Working yesterday on a newer XW system with a 
  new Kohler RES15 generator.  This is the first time I have tested the 
  inverter with this generator.  The inverter would not maintain a transfer 
  to the generator.  After about an hour on the phone with tech support, 
  the tech searched previous calls and announced that there is a known 
  incompatibility between the Kohler RES15 and a certain version of the XW 
  firmware.  I was advised to upgrade the firmware.<BR><BR>I wonder how 
  this can be.  Voltage and frequency even in the moment the inverter did 
  try to connect are well within specifications. After some thought, all I can 
  guess is that there might be some noise on the AC signal that the inverter 
  might reject.<BR><BR>Has anyone else experienced this?  Any insight to be 
  offered?<BR><BR>Thanks in advance.<BR><BR>William Miller<BR><BR><X-SIGSEP>
  <P></X-SIGSEP><FONT size=3>William Miller <BR>Miller Solar<BR>Voice 
  :805-438-5600<BR>email: william@millersolar.com<BR><A 
  href="http://millersolar.com/" 
  eudora="autourl">http://millersolar.com<BR></A>License No. 
  C-10-773985<BR></FONT>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>