<DIV dir=ltr align=left><SPAN class=515124919-06092011><FONT color=#0000ff 
size=2 face=Arial>The idea of "within the array" goes to the idea that the 
conductors will be located on the underside of an array of traditional 
framed moduled and will be afforded a modicum of protection from physical damage 
by the module itself.</FONT></SPAN></DIV>
<DIV><FONT color=#0000ff size=2 face=Arial></FONT> </DIV>
<DIV><SPAN class=515124919-06092011><FONT color=#0000ff size=2 face=Arial>So the 
issue is one of physical protection of the conductors. That is what tha AJH 
should be looking to. If he has cold feet about approving a non-standard method 
using un-listed componets based on local conditions, then he is 
understandably going to ask for a solution utilizing listed materials and 
standard methods.</FONT></SPAN></DIV>
<DIV><SPAN class=515124919-06092011><FONT color=#0000ff size=2 
face=Arial></FONT></SPAN> </DIV>
<DIV><SPAN class=515124919-06092011><FONT color=#0000ff size=2 face=Arial>What 
kind of support are you getting from Lumeta around this?</FONT></SPAN></DIV>
<DIV><SPAN class=515124919-06092011><FONT color=#0000ff size=2 
face=Arial></FONT></SPAN><BR><SPAN lang=en-us><FONT size=2 face=Arial>Mark 
Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley Solar 
Electric Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>303 
Redbud Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada 
City,  CA 95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>(530) 401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial> </FONT></SPAN> </DIV>
<DIV> </DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
</B>wirewiz@gmail.com<BR><B>Sent:</B> Tuesday, September 06, 2011 12:44 
PM<BR><B>To:</B> re-wrenches@lists.re-wrenches.org<BR><B>Subject:</B> 
[RE-wrenches] 690.31(B) "within the photovoltaic array"<BR></FONT><BR></DIV>
<DIV></DIV>Wrenches,<BR><BR>I am installing Lumeta peel and stick modules 
(similar to laminates) on a flat EPDM roof. No racking. NEC2008 690.31(B) says 
single conductor cable listed and labeled as PV wire shall be permitted in 
exposed outdoor locations..."within the array". 690.2 defines array as a 
mechanically integrated assembly of modules or panels within a support 
structure...to form a direct-current power producing unit. With the Lumeta's 
there is no support structure. If you look at the diagram in the NEC 2008 (page 
70-576) it shows a box around the modules or panels and labels that box as the 
"Array or photovoltaic power source". <BR><BR>My AHJ was at first not sure but 
then told me I had to install all the PV wire in a listed raceway because the 
interconnects between the Lumeta's were not within the array. But if you draw a 
box around all the Lumeta's it would look like the array diagram that I referred 
to above.<BR><BR>Because of my roof layout, it would be much easier to install 
an unlisted wire management system within the array rather than conduit which I 
will do but in reading the NEC it just wasn't clear to me what "within the 
array" means.<BR><BR clear=all>Any thoughts would be appreciated.<BR><BR>Thank 
you.<BR><BR>Larry Liesner<BR>Design and Installations<BR>Elektron Solar, 
LLC<BR>16 Ketchum St.<BR>Westport, CT 06880<BR>203-557-3127 
(office)<BR>203-644-2404 (cell)<BR>203-549-0977 (fax)<BR><A 