<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">Both cases started with new batteries: Trojan L16s. One was a 24 v system that tapped for 12 v lighting, the other was a 48 v system that charged with a 24 v Bergey added later. The problem seems to come up when you have more than one parallel string. I could see the Vanner working on a single string. The imbalance showed up just barely at first, and got much worse with time. In the end, the L16s died in less than 5 years, and never provided their full rated amp hours even the first year.<div>DC to DC converters from Solar Converters, Inc. seem to work pretty well, but I always under load them (maybe 5 to 10 amp load on a 20 amp rated unit)</div><div>THese days I just go all AC and avoid multiple DC voltages in the first place. There is almost always another solution.</div><div>A fair bit of our rewire work these days involves converting DC circuits (lighting, etc.) to AC under the K.I.S.S. principle.<br><div><br><div>
<span class="Apple-style-span" style="border-collapse: separate; border-spacing: 0px 0px; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; text-align: auto; -khtml-text-decorations-in-effect: none; text-indent: 0px; -apple-text-size-adjust: auto; text-transform: none; orphans: 2; white-space: normal; widows: 2; word-spacing: 0px; "><div>R. Walters</div><div><a href="mailto:ray@solarray.com">ray@solarray.com</a></div><div>Solar Engineer</div><div><br class="khtml-block-placeholder"></div><div><br class="khtml-block-placeholder"></div><br class="Apple-interchange-newline"></span>
</div>
<br><div><div>On Sep 3, 2011, at 9:10 PM, boB Gudgel wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite">
  
    <meta content="text/html; charset=ISO-8859-1" http-equiv="Content-Type">
  
  <div bgcolor="#FFFFFF" text="#000000">
    On 9/3/2011 7:57 PM, Darryl Thayer wrote:
    <blockquote cite="mid:1315105057.78859.YahooMailNeo@web39305.mail.mud.yahoo.com" type="cite">
      <div style="color:#000; background-color:#fff; font-family:arial,
        helvetica, sans-serif;font-size:12pt">
        <div style="RIGHT: auto"><span style="RIGHT: auto">I have had
            one experiance with equalizers, the batteries be came very
            unequal.  (over time of course)<var id="yui-ie-cursor"></var><br style="RIGHT: auto" class="yui-cursor">
          </span></div>
        <div><br>
        </div>
        <div style="FONT-FAMILY: arial, helvetica, sans-serif;
          FONT-SIZE: 12pt">
          <div style="FONT-FAMILY: times new roman, new york, times,
            serif; FONT-SIZE: 12pt"><font face="Arial" size="2">
              <b><span style="FONT-WEIGHT: bold">From:</span></b> R Ray
              Walters <a class="moz-txt-link-rfc2396E" href="mailto:ray@solarray.com"><ray@solarray.com></a><br>
              <b><span style="FONT-WEIGHT: bold">To:</span></b>
              RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a><br>
              <b><span style="FONT-WEIGHT: bold">Sent:</span></b>
              Saturday, September 3, 2011 5:55 PM<br>
              <b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re:
              [RE-wrenches] unique battery bank design question<br>
            </font><br>
            Systems I tried years ago with Vanner equalizers, still
            ended up being unequal. I pulled them all years ago. It
            seems to be about as much a problem as not balancing your
            battery cables so each battery string has the same wire
            resistance,<br>
            I know that you couldn't imagine a few amps on 12" of 2/0
            making a difference, but after 5 years the battery damage is
            very consistent and identifiable.<br>
            The only load I would consider tapping would be metering, or
            maybe a low milliamp relay. I wouldn't go over 100 mA, and
            even then I bet you would see some long term imbalance. I've
            seen imbalances due  to some batteries just being closer to
            a cold outside wall.<br>
            <br>
            R. Walters<br>
            <a moz-do-not-send="true" href="mailto:ray@solarray.com" ymailto="mailto:ray@solarray.com">ray@solarray.com</a><br>
            Solar Engineer<br>
          </div>
        </div>
      </div>
    </blockquote>
    <br>
    <br>
    Has anyone that has used battery balancers checked the individual
    battery voltages or SG during charge and/or discharge to<br>
    see how well the balancers worked ??<br>
    <br>
    Could it be that the batteries themselves were just not quite the
    same age at the start ??<br>
    <br>
    I would think that a decent balancer system that makes things share
    should work pretty well.  Maybe the balancer<br>
    itself does a bit of unbalaced charge/discharge ?<br>
    <br>
    boB<br>
    <br>
    <br>
  </div>

_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></blockquote></div><br></div></div></body></html>