<div>Question about the 10'/10% rule - the exception states "adjacent portions of a circuit."  How does this apply to an underground conduit run, where there are two ends exposed to higher ambient temperatures than the length in the ground?  </div>
<div><br></div><div>For example, what if there is 100 feet in the trench, and 7 feet above grade on either side? Can the exception be applied? How about 200 feet in the trench and 7 feet above grade on either end?</div><div>