Nick,<br>
<br>
It does sound like a ground fault, which leaves the question: why
doesn't the SB5000 see enough current to trip? Maybe it is something
else. I'd disconnect PV+ and PV- and then measure the string voltage.
Even with a ground fault it should be within normal range; if not there
is something besides a ground fault. Then measure PV+ to ground and PV-
to ground. These two numbers should add up to Voc. The ratio PV-/Voc
times the number of modules will tell you about how many modules are
between the fault and where the array is normally grounded. Caution:
normally grounded conductors, in fact all the conductors, may be
energized in reference to ground. Use appropriate personal protective
gear.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>
<br>
<br>
<br>
Nick Vida wrote:
<blockquote
 cite="mid:1309491359.76072.YahooMailRC@web112306.mail.gq1.yahoo.com"
 type="cite">
  <style type="text/css"><!-- DIV {margin:0px;} --></style>
  <div
 style="font-family: Courier New,courier,monaco,monospace,sans-serif; font-size: 12pt;">
  <div>Hi wrenches.<br>
  <br>
I had an interesting case today that I have been thinking about since
it happened. I dont have all the details because the homeownter had to
leave before I was done with the service call, but here is what I do
know. SB5000 with 2 strings of 15 modules. String one was 437 vdc, and
string 2 was 247vdc. I decided to look for a ground fault, and I turned
off the inverter. I measured for ground faults and found no evidence of
anything wrong in that regard. As the homeowner was out of time and
wanted me to go, I re-landed the wires in the dc disco, and when I
replaced the fuses, I noticed a minor arc when one of the fuses was
going it. Although I had no time to measure it, I think that there
might be a partial short circuit, possibly with one complete string and
some panels of the other string, and the remaining panels on the second
string. My mind was racing with how I could have measured for a partial
short circuit without seeing it as an arch. I can imagine such a thing
on a bigger system being a dramatic electrical event. <br>
needless to say, I cant wait to get back there and go through the
signal path properly and find out what the electrician did. And of
course i realized that replacing the fuses in such a questionable
situation was probably not the best idea.<br>
Do any of you have any thoughts on how one would measure for such a
thing?<br>
  <br>
nick vida<br>
  <br>
  </div>
  </div>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
</blockquote>
</body>
</html>