    OK, nevermind...   That'll teach me to respond before I know the
    question even after reading it<br>
    more than 3 times.<br>
    <br>
     For some reason I read the Voc's as being close in voltage as you
    said here, Nick.<br>
    <br>
    But yes, 247V Vs. 437V would certainly cause a back feed !<br>
    <br>
    Must be late.<br>
    <br>
    boB<br>
    <br>
    <br>
    <br>
    <br>
    <br>
    On 7/1/2011 12:12 AM, boB Gudgel wrote:
    <blockquote cite="mid:4E0D7378.6070909@midnitesolar.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      On 7/1/2011 12:07 AM, boB Gudgel wrote:
      <blockquote cite="mid:4E0D7232.80905@midnitesolar.com" type="cite">
        <meta content="text/html; charset=ISO-8859-1"
          http-equiv="Content-Type">
        On 6/30/2011 11:35 PM, boB Gudgel wrote:
        <blockquote cite="mid:4E0D6ABF.7030001@midnitesolar.com"
          type="cite">
          <meta content="text/html; charset=ISO-8859-1"
            http-equiv="Content-Type">
          On 6/30/2011 8:35 PM, Nick Vida wrote:
          <blockquote
            cite="mid:1309491359.76072.YahooMailRC@web112306.mail.gq1.yahoo.com"
            type="cite">
            <style type="text/css"><!-- DIV {margin:0px;} --></style>
            <div style="font-family: Courier
              New,courier,monaco,monospace,sans-serif; font-size: 12pt;">
              <div>Hi wrenches.<br>
                <br>
                I had an interesting case today that I have been
                thinking about since it happened. I dont have all the
                details because the homeownter had to leave before I was
                done with the service call, but here is what I do know.
                SB5000 with 2 strings of 15 modules. String one was 437
                vdc, and string 2 was 247vdc. I decided to look for a
                ground fault, and I turned off the inverter. I measured
                for ground faults and found no evidence of anything
                wrong in that regard. As the homeowner was out of time
                and wanted me to go, I re-landed the wires in the dc
                disco, and when I replaced the fuses, I noticed a minor
                arc when one of the fuses was going it. Although I had
                no time to measure it, I think that there might be a
                partial short circuit, possibly with one complete string
                and some panels of the other string, and the remaining
                panels on the second string. My mind was racing with how
                I could have measured for a partial short circuit
                without seeing it as an arch. I can imagine such a thing
                on a bigger system being a dramatic electrical event. <br>
                needless to say, I cant wait to get back there and go
                through the signal path properly and find out what the
                electrician did. And of course i realized that replacing
                the fuses in such a questionable situation was probably
                not the best idea.<br>
                Do any of you have any thoughts on how one would measure
                for such a thing?<br>
                <br>
                nick vida</div>
            </div>
          </blockquote>
          <br>
          <br>
          "<span style="font-family: "Courier New";"> I
            noticed a minor arc when one of the fuses was going it."<br>
            <br>
          </span></blockquote>
        <br>
        I see what you were saying.   When the fuse was going "IN" ...
        Into the fuse holder.<br>
        <br>
        Could it be that the inverter was connected (but turned off
        otherwise) and it arced as the inverter input capacitors were
        charging up ?<br>
        <br>
        If so, then the current would die to nothing soon after the fuse
        was in place.  A clamp meter would show<br>
        that too.<br>
        <br>
      </blockquote>
      <br>
      <br>
      ONE more thing on this...   Because the strings were at slightly
      different VOC's, it's possible that the<br>
      higher Voc string will  back feed the lower voltage string and you
      may very well see a small arc if the fuse<br>
      is connecting the two strings together.   No ground fault needed
      for that to happen.<br>
      <br>
      boB<br>