    On 6/30/2011 8:35 PM, Nick Vida wrote:
    <blockquote
      cite="mid:1309491359.76072.YahooMailRC@web112306.mail.gq1.yahoo.com"
      type="cite">
      <style type="text/css"><!-- DIV {margin:0px;} --></style>
      <div style="font-family: Courier
        New,courier,monaco,monospace,sans-serif; font-size: 12pt;">
        <div>Hi wrenches.<br>
          <br>
          I had an interesting case today that I have been thinking
          about since it happened. I dont have all the details because
          the homeownter had to leave before I was done with the service
          call, but here is what I do know. SB5000 with 2 strings of 15
          modules. String one was 437 vdc, and string 2 was 247vdc. I
          decided to look for a ground fault, and I turned off the
          inverter. I measured for ground faults and found no evidence
          of anything wrong in that regard. As the homeowner was out of
          time and wanted me to go, I re-landed the wires in the dc
          disco, and when I replaced the fuses, I noticed a minor arc
          when one of the fuses was going it. Although I had no time to
          measure it, I think that there might be a partial short
          circuit, possibly with one complete string and some panels of
          the other string, and the remaining panels on the second
          string. My mind was racing with how I could have measured for
          a partial short circuit without seeing it as an arch. I can
          imagine such a thing on a bigger system being a dramatic
          electrical event. <br>
          needless to say, I cant wait to get back there and go through
          the signal path properly and find out what the electrician
          did. And of course i realized that replacing the fuses in such
          a questionable situation was probably not the best idea.<br>
          Do any of you have any thoughts on how one would measure for
          such a thing?<br>
          <br>
          nick vida<br>
          <br>
        </div>
      </div>
      <br>
    </blockquote>
    <br>
    I'd probably use a DC clamp on ammeter.  Clamp on and measure the
    top and bottom current of each string...   What comes in ~should~
    come out.<br>
    <br>
    If it's much different on one end vs. the other end of one string,
    maybe that string is conducting around the path somehow.  Remember
    that<br>
    sometimes just turning the clamp around and measuring the opposite
    polarity may measure slightly differently than the opposite polarity
    and<br>
    that zero calibration is usually necessary.<br>
    <br>
    boB<br>