    Kris,<br>
    I don't know a Code-compliant solution, having not faced this. But
    I'll suggest that you not attempt to glue and seal conduit to keep
    the conductors dry, as it won't work permanently. Use wet-rated
    wire, expecting any conduit to provide only physical protection.
    THWN is wet-rated - that's the W. You might consider submersible
    pump cable also.<br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 6/9/2011 7:31 PM, Jesse Dahl wrote:
    <blockquote
      cite="mid:08C3BDF5-AC1A-4339-81B4-D0DF2E9C12D4@gmail.com"
      type="cite">
      <pre wrap="">There utility companies up here in northern MN bring power to islands all the time. The have cable underwater. Maybe contact Minnesota Power....

Jesse

Sent from my iPhone

On Jun 9, 2011, at 3:48 PM, Nathan Jones <a class="moz-txt-link-rfc2396E" href="mailto:solardude97@yahoo.com"><solardude97@yahoo.com></a> wrote:

</pre>
      <blockquote type="cite">
        <pre wrap="">Kris,
We work on boat docks on army corps of engineer lakes frequently and they have wire in direct contact with water everywhere. The lakes here are flood control and fluctuate a lot, like 50 feet in a given year. The marinas are dragging the feeder wires all over the place on rocky bottoms. We kill very few people with this insane practice but as the feeder wires age I believe the fatalities will increase. This is ground referenced service in fresh water with poor conducting capability in the water. Very dangerous yet allowed.
Your situation would be quite safe IMHO as there would be no stressing of the delivery system.
Nathan Jones
Power Source Solar
417-827-0738

On Thu Jun 9th, 2011 2:30 PM CDT Kristopher Schmid wrote:

</pre>
        <blockquote type="cite">
          <pre wrap="">I have an installation that is a ground mount on a berm with a man-made pond
between the array and the BOS.  The pond is about 4 feet deep.  How would
you wrenches make this run? in weighted conduit with primer and glued
joints? use boring and go under? out of conduit with wire directly in the
water?

Does code have anything to say about this specifically?

Thanks as always.

-- 
Thanks,
Kris Schmid

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
<a class="moz-txt-link-abbreviated" href="http://www.legacysolar.com">www.legacysolar.com</a>
<a class="moz-txt-link-abbreviated" href="mailto:solman@legacysolar.com">solman@legacysolar.com</a>
</pre>
        </blockquote>
        <pre wrap="">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>


</pre>
    </blockquote>
  </body>
</html>