<DIV>Good on the buss bars Wayne.  Using them removes the concerns about 
multiple strings and increases redundancy and system stability.  You won’t 
need 4/0 between single strings and the buss bar, you can probably easily use 
smaller cable, just size it for the individual string.  4/0 to the inverter 
of course.</DIV>
<DIV> </DIV>
<DIV>I echo the concern about the higher voltage bank though.  Most 
off-grid systems have some low voltage DC elements, or at least offer the 
opportunity to add them, so the higher voltage could be a problem, especially 
during equalization.  If you use the buss bars, keep system voltage high 
enough, and the batteries are well-cared for, it shouldn’t be necessary to add 
that one extra battery.</DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">
<DIV style="FONT: 10pt tahoma">
<DIV> </DIV>
<DIV style="BACKGROUND: #f5f5f5">
<DIV style="font-color: black"><B>From:</B> <A title=wayne@pureenergysolar.com 
href="mailto:wayne@pureenergysolar.com">Wayne Irwin</A> </DIV>
<DIV><B>Sent:</B> Tuesday, May 31, 2011 2:05 PM</DIV>
<DIV><B>To:</B> <A title=re-wrenches@lists.re-wrenches.org 
href="mailto:re-wrenches@lists.re-wrenches.org">Wrenches</A> </DIV>
<DIV><B>Subject:</B> Re: [RE-wrenches] 24 volt Battery Bank 
comparison</DIV></DIV></DIV>
<DIV> </DIV></DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">No 
DC loads at all. <BR><BR><FONT color=#76923c>Wayne Irwin</FONT><FONT 
color=#76923c>, EE<BR>Director of Engineering<BR></FONT><FONT color=#76923c>Pure 
Energy Solar International Inc. </FONT><FONT color=#76923c><BR></FONT><FONT 
color=#76923c></FONT><FONT color=#76923c>State Licensed Solar 
Contractor</FONT><FONT color=#76923c><BR></FONT><FONT color=#76923c>License # 
CVC56695 </FONT><BR><A 
href="mailto:PureEnergySolar@hotmail.com">mailto:PureEnergySolar@hotmail.com</A> 
<BR><A href="http://pureenergysolar.net/" 
target=_blank>http://pureenergysolar.com</A> <BR><FONT color=#76923c>352 
377-6527 Office</FONT><FONT color=#76923c><BR></FONT><FONT color=#76923c>352 
336-3299 Fax</FONT><FONT color=#76923c><BR></FONT><FONT color=#76923c>352 
316-1637 Cell</FONT><BR>
<P class=ecxecxecxEC_EC_EC_EC_EC_MsoNormal><FONT color=#76923c><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">The content of this 
message is Pure Energy Solar Confidential. If you are not the intended recipient 
and have received this message in error, any use or distribution is prohibited. 
Please notify me immediately by reply e-mail and delete this message from your 
computer system. Thank you.</SPAN></FONT></P><BR><BR><BR><BR>
<HR id=stopSpelling>
From: bob-o@electronconnection.com<BR>Date: Tue, 31 May 2011 16:59:43 
-0700<BR>To: re-wrenches@lists.re-wrenches.org<BR>Subject: Re: [RE-wrenches] 24 
volt Battery Bank comparison<BR><BR>
<META name=Generator content="Microsoft SafeHTML">Wayne, 
<DIV>I'd recommend against that. To do an effective equalization charge on that 
bank you'll need to get the voltage up to at least 2.6-2.7V per cell. That would 
mean a 13 cell pack voltage of 34-35V. Got any DC loads at all? Danger, Will 
Robinson, Danger!  Using the inverter as a charging source? I think you'll 
run out of transformer windings or at the very least reduce your amperage output 
greatly toward the end of that cycle.</DIV>
<DIV>Hopefully, Jamie can jump in with an opinion here as well.</DIV>
<DIV>Good Luck!</DIV>
<DIV>Bob-O <BR>
<DIV>
<DIV>On May 31, 2011, at 4:28 PM, Wayne Irwin wrote:</DIV><BR 
class=ecxApple-interchange-newline><SPAN 
style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; FONT: medium helvetica; WHITE-SPACE: normal; ORPHANS: 2; WORD-SPACING: 0px" 
class=ecxApple-style-span>
<DIV style="FONT-FAMILY: tahoma; FONT-SIZE: 10pt" class=ecxhmmessage>Just for a 
little extra.<BR><BR><FONT color=#76923c>Wayne Irwin</FONT><FONT color=#76923c>, 
EE<BR>Director of Engineering<BR></FONT><FONT color=#76923c>Pure Energy Solar 
International Inc.<SPAN class=ecxApple-converted-space> </SPAN></FONT><FONT 
color=#76923c><BR></FONT><FONT color=#76923c></FONT><FONT color=#76923c>State 
Licensed Solar Contractor</FONT><FONT color=#76923c><BR></FONT><FONT 
color=#76923c>License # CVC56695<SPAN 
class=ecxApple-converted-space> </SPAN></FONT><BR><A 
href="mailto:PureEnergySolar@hotmail.com">mailto:PureEnergySolar@hotmail.com</A><SPAN 
class=ecxApple-converted-space> </SPAN><BR><A 
href="http://pureenergysolar.net/" 
target=_blank>http://pureenergysolar.com</A><SPAN 
class=ecxApple-converted-space> </SPAN><BR><FONT color=#76923c>352 377-6527 
Office</FONT><FONT color=#76923c><BR></FONT><FONT color=#76923c>352 336-3299 
Fax</FONT><FONT color=#76923c><BR></FONT><FONT color=#76923c>352 316-1637 
Cell</FONT><BR>
<DIV 
style="PADDING-BOTTOM: 0px; PADDING-LEFT: 0px; PADDING-RIGHT: 0px; MARGIN-BOTTOM: 0px; MARGIN-LEFT: 0px; MARGIN-RIGHT: 0px; PADDING-TOP: 0px"><FONT 
color=#76923c><SPAN style="FONT-FAMILY: arial, sans-serif; FONT-SIZE: 10pt">The 
content of this message is Pure Energy Solar Confidential. If you are not the 
intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank 
you.</SPAN></FONT></DIV></DIV></SPAN></DIV></DIV><BR>_______________________________________________ 
List sponsored by Home Power magazine List Address: 
RE-wrenches@lists.re-wrenches.org Options & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out 
participant bios: www.members.re-wrenches.org 
<P>
<HR>
_______________________________________________<BR>List sponsored by Home Power 
magazine<BR><BR>List Address: RE-wrenches@lists.re-wrenches.org<BR><BR>Options 

settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
participant bios:<BR>www.members.re-wrenches.org<BR><BR>
<P>
<HR>
<A></A>
<P class=avgcert align=left color="#000000">No virus found in this 
message.<BR>Checked by AVG - <A 
href="http://www.avg.com">www.avg.com</A><BR>Version: 10.0.1375 / Virus 
Database: 1509/3671 - Release Date: 05/31/11</P></DIV></DIV></DIV></BODY></HTML>