      normal;"><big><big>I asked you about a generator since the future
          addition on one might influence your selected solution. <br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>The GenReady ATS does not include any
          load-shedding control algorithm based on AC input voltage
          (representing full load/overload sensing) that would have to
          be left unused. <br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>The ATS "sensing breaker" and the "XFER",
          "BAT+, and "BAT-" leads are intended to be used by a
          generator's controller board to sense a grid brownout,
          overvoltage, or failure condition, apply its internal timing
          algorithms, then activate the ATS. There are no "smarts" in
          the GenReady panel's ATS - it's a "dumb" switch.<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>I have a Generac EcoGen propane generator with
          a 2-wire start, and no internal controller. It has no internal
          "smarts" and  relies totally on the controller functionality
          internal to the PV inverter.</big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>I'm using the Generac GenReady panel at my home
          installation as follows for backing up critical loads:</big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(A) The inverter output from my XW system feeds
          the "Generator Supply" breaker on GenReady panel. <br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(B) The AC1 grid connection on the XW is
          connected to the lowest 2-pole breaker position on the top
          portion (non-protected) side of the GenReady panel.<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(C) The EcoGen generator is connected to the
          AC2 (generator) input on the XW.<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(D) In the "normal" configuration (no grid
          failure), the GenReady internal ATS (automatic transfer
          switch) is already activated, and the XW inverter's output is
          feeding local protected loads. XW PV production in excess of
          local load and battery charging requirements is connected to
          the upper portion of the GenReady panel, and is consumed by
          the local non-protected loads, or sold back to the grid.<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(E) With a grid failure, the GenReady ATS
          position does not change, and the inverter continues to feed
          the protected loads (non-protected loads are "dead"). The XW
          inverter will start/stop the generator as needed to keep the
          batteries charged.<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>(F) So what is the GenReady ATS used for? It is
          not needed with a dedicated protected loads panel, but
          provided two advantages in my situation:</big></big><br>
    </p>
    <blockquote><big><big></big></big>
      <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
        normal;"><big><big>(1) I needed to upgrade my main service panel
            anyway, so choosing a panel with an internal ATS made sense.
            Plus, I could connect a generator for the protected loads
            (non-PV solution).</big></big></p>
      <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
        normal;"><big><big>(2)  With a PV solution, I use the GenReady
            ATS to manually bypass the inverter. It's easier to do that
            to flip the four breakers in the Xantrex AC Interconnection
            Panel. I haven't done this yet, but it should be possible to
            have the XW inverter control the ATS to switch the protected
            loads back to the inverter if a grid outage occurs while the
            ATS is in the inverter bypass mode.<br>
          </big></big></p>
    </blockquote>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>I totally agree with you that having an option
          to provide a critical loads battery backup for solar
          installations is an underserved market, particularly in rural
          areas with frequent grid outages and brownouts. <br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>An integrated inverter/charger, in conjunction
          with a natural gas and/or propane generator, feeding a
          separate critical loads panel is a great solution to offer
          customers desiring an "UPS-like" configuration for critical
          loads. The battery bank sizing will be a cost tradeoff between
          hours of autonomy of the battery bank, versus size/run-time
          for the generator (if equipped).<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>Hope this helps!<br>
        </big></big></p>
    <p class="MsoNormal" style="margin-bottom: 0.0001pt; line-height:
      normal;"><big><big>Regards,<br>
          <br>
          Gary Willett, PE</big></big></p>
    <big><big>Icarus Engineering / Solar Services LLC<br>
        NABCEP Certified Solar PV Installer # 031310-246</big><br>
      <br>
    </big><font color="#000000"><span style="font-size: 10pt;"><br>
      </span></font>On 5/14/2011 4:28 PM, Allan Sindelar wrote:
    <blockquote cite="mid:4DCEF3E9.8090103@positiveenergysolar.com"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      Gary,<br>
      Thank you for the referral to this product; I didn't know it
      existed. If you reread my original post, you'll see that there's
      no generator involved; this is purely inverter- and battery-based.
      At the link you provided, I was able to download a spec sheet, but
      the spec sheet lacked some of the information to determine how
      well this would work in an inverter-based situation. It appears
      that this unit includes a load-shedding control algorithm based on
      AC input voltage (representing full load/overload sensing) that
      would have to be left unused. It's not clear to me that this could
      be set up to work as simply as a shift-to-backup on the critical
      loads section could be automatic and based solely on loss of grid
      AC. Have you used this in a GTWB installation? ?If so, what can
      you tell us?<br>
      <br>
      This unit retails around $350 and is based on a generator-based
      application. I would think that a simple series of AC critical
      load panels, that include a simple 30 or 60A 120/240 automatic
      transfer switch function in order to switch critical loads from
      utility source to inverter source, would be a product with a
      ready, small but growing market. We have requests for
      sophisticated grid-tie with backup systems, intended as
      preparation for possible permanent loss of utility electricity. <br>
      <br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        <title></title>
        <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
        <small><a moz-do-not-send="true"
            href="mailto:Allan@positiveenergysolar.com"><font
              color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
          face="Times New Roman, Times, serif"><br>
          <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
            Installer<br>
            NABCEP Certified Technical Sales Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            <b>Positive Energy, Inc.</b><br>
            3201 Calle Marie<br>
            Santa Fe, New Mexico 87507<br>
            <b>505 424-1112</b><br>
            <a moz-do-not-send="true"
              href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
        <span style="font-size: 10pt;"> </span> </div>
    </blockquote>
  </body>
</html>