<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">I'm with you Ray,<div><br></div><div>If indeed there is high terminal temperature(s) then I think the issue is in the cables.</div><div>And if they were soldered incorrectly it can actually cause them to have higher resistance than without soldering.</div><div><br></div><div>( was told by a engineer that the only true way to soldier a big lug is by dipping into liquid lead)</div><div><br></div><div>Were the terminals cleaned of oxidation before assembly?</div><div>How many terminals are hot?</div><div>Are the cables new?</div><div><br></div><div>jay</div><div><br></div><div>peltz power</div><div><br><div><div>On Apr 20, 2011, at 1:38 PM, R Ray Walters wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite"><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><div><div>Sounds like problem connections, if all the cells are an even 2.12 v. </div><div>I wouldn't solder 4/0 connections, the solder can run back up the cable stranding, and make the cables too stiff to fully connect with the battery terminal. </div><div>I had a battery terminal meltdown due to this. We quit using thick bussbars, soldered cables, and stiff (THHN) cables at battery terminals.</div><div>Also if not soldered properly, you can actually create more resistance in the connection due to oxidation and pockets of flux.</div><div>Cables from the manufacturers (HUP, Outback, Trace) are not soldered BTW. </div><div><div>Its possible that heating the terminals when soldered (with a torch?) may have created a layer of oxidation that is causing the resistance (internally or externally)</div><div>Sand the contact surfaces, and see if that helps.</div></div><div><br></div><div>Get an infrared thermometer (fairly cheap these days at Sears or automotive store) and check all the connections under load.</div><div>Also, check the voltage drops on your cables under load, you should be able to find where all that voltage is going, and it should match your infrared readings.</div><div>I'd also take out another set of cables to see what that does.</div><div><br><div>
<span class="Apple-style-span" style="border-collapse: separate; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; -webkit-text-decorations-in-effect: none; text-indent: 0px; -webkit-text-size-adjust: auto; text-transform: none; orphans: 2; white-space: normal; widows: 2; word-spacing: 0px; "><div>R. Walters</div><div><a href="mailto:ray@solarray.com">ray@solarray.com</a></div><div>Solar Engineer</div><div><br class="khtml-block-placeholder"></div><div><br class="khtml-block-placeholder"></div><br class="Apple-interchange-newline"></span>
</div>
<br><div><div>On Apr 20, 2011, at 1:15 PM, Bob-O Schultze wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite"><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">Rich,<div>It sounds like you've got a rotter or two. Given the short age of the pack, that's my suspicion. Try checking the individual battery voltages when under load and fairly well discharged. I've seen a new battery bank all show good SG and individual voltages while resting but one or more batteries tank badly under load. Poor manufacturing QC is the cause.</div><div>good luck, Bob-O</div><div><br><div><div>On Apr 20, 2011, at 12:03 PM, Rich Nicol wrote:</div><br class="Apple-interchange-newline"><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; font-size: medium; "><div lang="EN-US" link="blue" vlink="purple"><div class="WordSection1" style="page: WordSection1; "><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">RE Wrenches<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; text-indent: 0.5in; ">My question regards a system (installed by homeowner / friend) where they recently upgraded their t105 battery bank to Trojan RE series L16 2 volt cells.  The battery bank consists of 6 batteries in series for a 12 volt system.  The interconnects are 12” long 4/0 cables with crimped and soldered lugs.  Main cables are 6’ long 4/0 cables.<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; text-indent: 0.5in; ">The first issue is high terminal temperature during periods of heavy draw (~100 amps @ 12v when water pump is on).  Due to the issue the owner has been only running the water pump when charging the batteries with his generator since the transfer switch on the Outback inverter has transferred his household circuits from the battery bank to the generator.  Obviously this is an inconvenience. Before the end of life on his T105’s he had no issues with the 6 volt cells in series/parallel using only #2 AWG interconnects.<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; text-indent: 0.5in; ">Most recently he’s experienced an issue where the inverter will not come on at all and when attempted to come by switching on his main DC breaker  the voltage at the batteries sags from 12.5 to ~5V!  This issue is not with the inverter since I loaned him a back up Trace DR I keep around as a loaner but it too would not come on and voltage sagged as well.  This sag is with no demand since it sags immediately when the DC breaker is switched on when connected to the inverter even though the inverter has not been switched on. <o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; text-indent: 0.5in; ">I stopped by this AM to check out the situation, specific gravity of all cells is good, open circuit voltage on each cell is matched at 2.12  volts.  The battery bank is only about 4 months old.<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">Any insight would be greatly appreciated.<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; "><o:p> </o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">Battery specs:<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">2 volt, Rated Capacity @ 5 Hr rate=909 AH, 20 hr rate = 1110 AH, 100 hr rate = 1235.<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; "><o:p> </o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">Thanks for your help!<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; ">Rich<o:p></o:p></div><div style="margin-top: 0in; margin-right: 0in; margin-bottom: 0.0001pt; margin-left: 0in; font-size: 11pt; font-family: Calibri, sans-serif; "><font class="Apple-style-span" face="Helvetica"><span class="Apple-style-span" style="font-size: medium;"><font class="Apple-style-span" face="Calibri, sans-serif" size="4"><span class="Apple-style-span" style="font-size: 15px;"><br></span></font></span></font></div></div><br></div></span></div><br></div></div>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></blockquote></div><br></div></div></div>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></blockquote></div><br></div></body></html>