<html><body><span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>If your Inspector dude specifically sited 690.4.(B), and you are talking about an AC inverter output circuit back to the main service panel, I'd say your Inspector is having a bad day (or you seriously p#ssed him off). Figure 690.1(A) clearly distinguishes between <u>PV </u>Source / Output circuits (DC) and I<u>nverter</u> Output circuits (AC). Sounds like you're dealing with the later. in which case 690.4(B) does not apply. should be the same as if you were running any two normal sub feeders (article 215, 300,110..  the usual suspects). 690.3 says 690 trumps. (that will really p#iss him off). but you do have all the 705 stuff mentioned in 690.3 to deal with (in addition to 705.60). is this in Vt?.. db<br></div><div><br></div><div><br>Dan Brown<br>Foxfire Energy Corp.<br>Renewable Energy Systems<br>(802)-483-2564<br><a href="http://www.Foxfire-Energy.com">www.Foxfire-Energy.com</a><br>NABCEP #092907-44</div><div><br><br></div>
<blockquote id="replyBlockquote" webmail="1" style="border-left: 2px solid blue; margin-left: 8px; padding-left: 8px; font-size:10pt; color:black; font-family:verdana;">
<div id="wmQuoteWrapper">
-------- Original Message --------<br>
Subject: Re: [RE-wrenches] 690.4 (B) ???<br>
From: "Kirk Herander, VSE" <<a href="mailto:kirk@vtsolar.com">kirk@vtsolar.com</a>><br>
Date: Sat, April 09, 2011 9:29 pm<br>
To: <<a href="mailto:kirk@vtsolar.com">kirk@vtsolar.com</a>>, "'RE-wrenches'"<br>
<<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
<br>
PS Does this merely mean that conductors from more than one source must be<br>
bundled("connected") together, but are allowed in the same conduit?<br>
<br>
Kirk Herander<br>
Vermont Solar Engineering<br>
802.863.1202<br>
NABCEP(tm) Certified Solar Installer<br>
NYSERDA-eligible Installer<br>
VT Solar Incentive Program Partner<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a><br>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Kirk<br>
Herander, VSE<br>
Sent: Saturday, April 09, 2011 9:10 PM<br>
To: 'RE-wrenches'<br>
Subject: [RE-wrenches] 690.4 (B) ???<br>
<br>
2008 NEC states that:<br>
<br>
(B) Conductors of Different Systems. Photovoltaic<br>
source circuits and photovoltaic output circuits shall not be<br>
contained in the same raceway, cable tray, cable, outlet box,<br>
junction box, or similar fitting as feeders or branch circuits<br>
of other systems, unless the conductors of the different systems<br>
are separated by a partition or are connected together.<br>
<br>
Can anyone describe and give an example of what "connected together" means<br>
to inverter PV circuits in the same conduit as a branch (load) circuit?<br>
<br>
I have a single existing PVC conduit to a barn with an AC load subpanel. I<br>
want to run the output conductors of an inverter combiner panel in the barn<br>
through the same conduit to get to be main building. The fill / derating<br>
calcs work to do this. The inspector says I have to run a new conduit for<br>
the AC inverter combiner because the subpanel feeder and the combiner output<br>
conductors are "not connected". But they are both connected to the main<br>
building panel. Any insight will be appreciated. Thanks. I've also been told<br>
that the NEC 2011 comments on 690.4 (B) clarify this. Can anyone comment?<br>
Obviously I am not mixing DC and AC conductors.<br>
<br>
<br>
<br>
Kirk Herander<br>
Vermont Solar Engineering<br>
802.863.1202<br>
NABCEP(tm) Certified Solar Installer<br>
NYSERDA-eligible Installer<br>
VT Solar Incentive Program Partner<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive:<br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
<br>

</div>
</blockquote></span></body></html>