size=2 face=Arial>Right, so going totally on the fly at the white board, let's 
say we have an inverter with a 45A AC output, it see's the short and pours it's 
little heart out at 45A for 0.1 sec before shutting out, delivering 4.5 A-sec of 
energy into the fault.  Meanwhile we take out a clearing time curve 
for the generic 60A breaker that the inverter would be backfeed at the 
other end of the feeder. It will deliver 10 times it's rating or 600A for 0.5 
secs before clearing. That's 300 A-sec of energy, 66 times more than the 
inverter.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=218162420-30032011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=218162420-30032011><FONT color=#0000ff 
size=2 face=Arial>So can we say that when looking at sizing the AC side of these 
inverters we need more to concern ourselves with continuous overload 
conditions and not so much with short-circuit/ground fault 
conditions?</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=218162420-30032011></SPAN> <BR><SPAN 
lang=en-us><FONT size=2 face=Arial>Mark Frye</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT size=2 face=Arial>Berkeley Solar Electric Systems</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>303 Redbud Way</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada City,  CA 
95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>(530) 
401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial> </FONT></SPAN> </DIV>
<DIV> </DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
</B>Exeltech<BR><B>Sent:</B> Wednesday, March 30, 2011 12:04 PM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] sizing a sub-panel used 
tocombinemultipleinverter outputs<BR></FONT><BR></DIV>
<DIV></DIV>
<TABLE border=0 cellSpacing=0 cellPadding=0>
  <TBODY>
  <TR>
    <TD vAlign=top>Per your question:<BR><BR><SPAN 
      class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
      face=Arial>> 1 - What does a UL1741 inverter do when it is 
      connected<BR>> to a line that is experiencing a short-circuit or ground 
      fault?<BR></FONT></SPAN><BR>Presuming a hard short, the voltage in that 
      circuit would be essentially zero, and a UL1741 compliant inverter would 
      cease producing power in less than 0.1 second.<BR><BR><BR>Dan<BR>Sr. 
      Engineer<BR>Exeltech<BR><BR><BR><BR><BR><BR><BR><BR><BR>--- On <B>Wed, 
      3/30/11, Mark Frye <I><markf@berkeleysolar.com></I></B> wrote:<BR>
      <BLOCKQUOTE 
      style="BORDER-LEFT: rgb(16,16,255) 2px solid; PADDING-LEFT: 5px; MARGIN-LEFT: 5px"><BR>From: 
        Mark Frye <markf@berkeleysolar.com><BR>Subject: Re: [RE-wrenches] 
        sizing a sub-panel used tocombine multipleinverter outputs<BR>To: 
        "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org><BR>Date: 
        Wednesday, March 30, 2011, 12:37 PM<BR><BR>
        <DIV id=yiv1283215088>
        <STYLE>UNKNOWN {
        FONT-FAMILY: Helvetica
}
UNKNOWN {
        FONT-FAMILY: Helvetica
}
UNKNOWN {
        FONT-FAMILY: Calibri
}
UNKNOWN {
        FONT-FAMILY: Tahoma
}
UNKNOWN {
        
}
</STYLE>

        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>That is a really good question Brian.</FONT></SPAN></DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial></FONT></SPAN> </DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>Mostly when thinking about these sizing issues I think about 
        overload conditions and not so much about short-circuit and ground fault 
        conditions.</FONT></SPAN></DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial></FONT></SPAN> </DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>So two questions come up:</FONT></SPAN></DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial></FONT></SPAN> </DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>1 - What does a UL1741 inverter do when it is connected to a 
        line that is experiencing a short-circuit or ground 
        fault?</FONT></SPAN></DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial></FONT></SPAN> </DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>2 - What does the feeder breaker do when it is connected to a 
        line that is experiencing a short-circuit or ground 
        fault?</FONT></SPAN></DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial></FONT></SPAN> </DIV>
        <DIV dir=ltr align=left><SPAN 
        class=yiv1283215088828221817-30032011><FONT color=#0000ff size=2 
        face=Arial>As far as number two, thanks to all the great work we do 
        establishing low impedence fault paths back to circuirt protectors, the 
        breaker is going to trip at it's rating and protect the wire at the same 
        rating. But that doesn't mean that the conductor won't see more 
        than rated amps during the fault. It will see alot more than 
        for a very short time. During this very short time frame, the actual 
        currents flowing into the fault from the utility side of the equation 
        far far exceed the currents contributed by the power limited inverter 
        side.</FONT></SPAN></DIV>
        <DIV><BR><SPAN lang=en-us><FONT size=2 face=Arial>Mark 
        Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley 
        Solar Electric Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
        face=Arial>303 Redbud Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT 
        size=2 face=Arial>Nevada City,  CA 95959</FONT></SPAN> <BR><SPAN 
        lang=en-us><FONT size=2 face=Arial>(530) 401-8024</FONT></SPAN> 
        <BR><SPAN lang=en-us></SPAN><A href="http://www.berkeleysolar.com/" 
        rel=nofollow target=_blank><SPAN lang=en-us><U><FONT color=#0000ff 
        size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
        lang=en-us><FONT size=2 face=Arial> </FONT></SPAN> </DIV>
        <DIV> </DIV><BR>
        <DIV dir=ltr lang=en-us class=yiv1283215088OutlookMessageHeader 
        align=left>
        <HR tabIndex=-1>
        <FONT size=2 face=Tahoma><B>From:</B> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Brian Teitelbaum<BR><B>Sent:</B> Wednesday, March 30, 2011 10:02 
        AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] sizing 
        a sub-panel used tocombine multipleinverter outputs<BR></FONT><BR></DIV>
        <DIV></DIV>
        <DIV class=yiv1283215088WordSection1>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">Wouldn’t 
        a fault in that conductor between the main and the sub have a potential 
        for up to 160A of current? I would think that at noon on a sunny day, 
        the inverter system could produce 80A from one direction (albeit really 
        only the max amperage outputs of the inverters) and 80A of grid current 
        from the main into a partial fault.</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">Brian 
        Teitelbaum</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">AEE 
        Solar </SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <DIV>
        <DIV 
        style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
        <P class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Mark Frye<BR><B>Sent:</B> Wednesday, March 30, 2011 9:49 
        AM<BR><B>To:</B> 'RE-wrenches'<BR><B>Subject:</B> Re: [RE-wrenches] 
        sizing a sub-panel used to combine multipleinverter 
        outputs</SPAN></P></DIV></DIV>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">Al,</SPAN><SPAN 
        style="COLOR: windowtext"></SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="COLOR: windowtext"></SPAN> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">I would 
        say that yes the meter is a load and this goes to show the relative 
        inadequacy of the vocabulary we are using in the discussion. In the 
        example we have been using with the 80A breaker, wire and sub panel, you 
        could have up to 80A of loads installed in the sub and still not create 
        an over current condition in any of that equipment.</SPAN><SPAN 
        style="COLOR: windowtext"></SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="COLOR: windowtext"><BR></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">Mark 
        Frye</SPAN><SPAN style="COLOR: windowtext"> <BR></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">Berkeley 
        Solar Electric Systems</SPAN><SPAN style="COLOR: windowtext"> 
        <BR></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">303 
        Redbud Way</SPAN><SPAN style="COLOR: windowtext"> <BR></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">Nevada 
        City,  CA 95959</SPAN><SPAN style="COLOR: windowtext"> 
        <BR></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">(530) 
        401-8024</SPAN><SPAN style="COLOR: windowtext"> <BR><A 
        href="http://www.berkeleysolar.com/" rel=nofollow target=_blank><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">www.berkeleysolar.com</SPAN></A></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt"> </SPAN><SPAN 
        style="COLOR: windowtext"> </SPAN></P>
        <DIV>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="COLOR: windowtext"></SPAN> </P></DIV>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="COLOR: windowtext"></SPAN> </P>
        <DIV style="TEXT-ALIGN: center" class=yiv1283215088MsoNormal 
        align=center><SPAN style="COLOR: windowtext">
        <HR align=center SIZE=2 width="100%">
        </SPAN></DIV>
        <P style="MARGIN-BOTTOM: 12pt" class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Al Frishman<BR><B>Sent:</B> Wednesday, March 30, 2011 9:00 
        AM<BR><B>To:</B> 'RE-wrenches'<BR><B>Subject:</B> Re: [RE-wrenches] 
        sizing a sub-panel used to combine multipleinverter outputs</SPAN><SPAN 
        style="COLOR: windowtext"></SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">Is 
        a monitoring system installed in the Load Center to measure the 
        cumulative kWh’s of the inverter’s considered a load?  </SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">The 
        type of monitoring device I am talking about has CT’s that go around the 
        conductors and the Voltage ref is taken by attaching conductors to each 
        phase, the Neutral and the ground bar.    The digital 
        Meter has a 3-pole 5A breaker in it so the conductors in the load center 
        can be connected to lugs on the bus bar directly.</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <DIV>
        <P class=yiv1283215088MsoNormal><I><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10.5pt">Al 
        Frishman</SPAN></I><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 13.5pt"><BR></SPAN><SPAN>Aeon</SPAN><SPAN>Solar</SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 13.5pt"></SPAN></P>
        <P class=yiv1283215088MsoNormal><I><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10.5pt">(917) 699-6641 - 
        cell</SPAN></I><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10.5pt"><BR><I>(888) 
        460-2867</I><BR><I><A href="http://www.aeonsolar.com/" rel=nofollow 
        target=_blank>www.aeonsolar.com</A></I></SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 13.5pt"></SPAN></P>
        <P style="TEXT-ALIGN: center" class=yiv1283215088MsoNormal 
        align=center><I><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 14pt"></SPAN></I> </P></DIV>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <DIV>
        <DIV 
        style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
        <P class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Jason Szumlanski<BR><B>Sent:</B> Wednesday, March 30, 2011 8:18 
        AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] sizing 
        a sub-panel used to combinemultipleinverter 
        outputs</SPAN></P></DIV></DIV>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">Another 
        key is to remember that this discussion also applies to the conductor 
        between the main panel and subpanel. In a large PV system, this could 
        result in a pretty large wire between the two panels, and a significant 
        cost that is often overlooked. In some cases it makes sense to locate 
        the subpanel close to the main panel and run multiple sets of smaller 
        wires from the inverters to the subpanel.</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">And 
        because the calculation is based on the first OC protection connected to 
        the inverters, adding a main breaker (theoretically 80A in this example) 
        in the subpanel doesn’t change things. Even though this wire would be 
        theoretically protected by an 80A breaker at each end, you can’t size 
        the wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. 
        (not that it makes much of a difference in this example, but it still 
        must be considered)</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">At 
        least that’s how I understand it…</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <DIV>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125)">Jason 
        Szumlanski</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt">Fafco 
        Solar</SPAN><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 4pt"> 
        </SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P></DIV>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN> </P>
        <DIV>
        <DIV 
        style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
        <P class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: windowtext; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Mark Frye<BR><B>Sent:</B> Wednesday, March 30, 2011 1:33 
        AM<BR><B>To:</B> 'RE-wrenches'<BR><B>Subject:</B> Re: [RE-wrenches] 
        sizing a sub-panel used to combinemultipleinverter 
        outputs</SPAN></P></DIV></DIV>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">Opps!</SPAN></P>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">My bad, 
        I was thinking of a single phase system, not the three phase 
        system shown in the article.</SPAN></P>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">For the 
        three phase system Kent is correct in counting 180A of supply per 
        bar.</SPAN></P>
        <P class=yiv1283215088MsoNormal> </P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Mark Frye</SPAN> 
        <BR><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Berkeley 
        Solar Electric Systems</SPAN> <BR><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">303 Redbud Way</SPAN> 
        <BR><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Nevada 
        City,  CA 95959</SPAN> <BR><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">(530) 401-8024</SPAN> 
        <BR><A href="http://www.berkeleysolar.com/" rel=nofollow 
        target=_blank><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">www.berkeleysolar.com</SPAN></A><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> </SPAN> </P>
        <DIV>
        <P class=yiv1283215088MsoNormal> </P></DIV>
        <P class=yiv1283215088MsoNormal> </P>
        <DIV style="TEXT-ALIGN: center" class=yiv1283215088MsoNormal 
        align=center>
        <HR align=center SIZE=2 width="100%">
        </DIV>
        <P style="MARGIN-BOTTOM: 12pt" class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Mark Frye<BR><B>Sent:</B> Tuesday, March 29, 2011 10:17 
        PM<BR><B>To:</B> 'RE-wrenches'<BR><B>Subject:</B> Re: [RE-wrenches] 
        sizing a sub-panel used to combine multipleinverter outputs</SPAN></P>
        <P class=yiv1283215088MsoNormal><SPAN 
        style="FONT-FAMILY: 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt">I think 
        Kent and I agree. For the case where the subpanel is not dedicated 
        a PV sub-panel he is calculating for 2 - 50A breakers and I calculated 
        for 3 - 50A breakers.</SPAN></P>
        <P class=yiv1283215088MsoNormal><BR><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Mark Frye</SPAN> 
        <BR><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Berkeley 
        Solar Electric Systems</SPAN> <BR><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">303 Redbud Way</SPAN> 
        <BR><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Nevada 
        City,  CA 95959</SPAN> <BR><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">(530) 401-8024</SPAN> 
        <BR><A href="http://www.berkeleysolar.com/" rel=nofollow 
        target=_blank><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">www.berkeleysolar.com</SPAN></A><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> </SPAN> </P>
        <DIV>
        <P class=yiv1283215088MsoNormal> </P></DIV>
        <P class=yiv1283215088MsoNormal> </P>
        <DIV style="TEXT-ALIGN: center" class=yiv1283215088MsoNormal 
        align=center>
        <HR align=center SIZE=2 width="100%">
        </DIV>
        <P style="MARGIN-BOTTOM: 12pt" class=yiv1283215088MsoNormal><B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
        style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> 
        re-wrenches-bounces@lists.re-wrenches.org 
        [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
        </B>Kent Osterberg<BR><B>Sent:</B> Tuesday, March 29, 2011 9:26 
        PM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] sizing 
        a sub-panel used to combine multiple inverter outputs</SPAN></P>
        <P style="MARGIN-BOTTOM: 12pt" class=yiv1283215088MsoNormal>Per 
        705.12(D) the sub-panel could be any distribution equipment on the 
        premises. So the question becomes: is the sub-panel capable of supplying 
        branch circuits or feeder loads? If yes, then the sum of the breakers 
        (potentially) feeding the bus is 180 amps so a 150-amp rating is 
        required and the inverters would have to feed the opposite end of the 
        bus bars. If no, the code is not clear on the requirement, but obviously 
        the 80-amp breaker in the main panel limits the maximum current flowing 
        through the sub-panel. <BR><BR>Kent Osterberg<BR>Blue Mountain 
        Solar</P></DIV></DIV><BR>-----Inline Attachment Follows-----<BR><BR>
        <DIV 
        class=plainMail>_______________________________________________<BR>List 
        sponsored by Home Power magazine<BR><BR>List Address: <A 
        href="/mc/compose?to=RE-wrenches@lists.re-wrenches.org" 
        ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
        & settings:<BR><A 
        href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
        <A 
        href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
        rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check 
        out participant 
      bios:<BR>www.members.re-wrenches.org<BR><BR></DIV></BLOCKQUOTE></TD></TR></TBODY></TABLE><BR></BODY></HTML>