size=2 face=Arial>I think Kent and I agree. For the case where the subpanel 
is not dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I 
calculated for 3 - 50A breakers.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><BR><SPAN lang=en-us><FONT size=2 face=Arial>Mark 
Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley Solar 
Electric Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>303 
Redbud Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada 
City,  CA 95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>(530) 401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial> </FONT></SPAN> </DIV>
<DIV> </DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Kent 
Osterberg<BR><B>Sent:</B> Tuesday, March 29, 2011 9:26 PM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] sizing a sub-panel used to 
combine multiple inverter outputs<BR></FONT><BR></DIV>
<DIV></DIV>Per 705.12(D) the sub-panel could be any distribution equipment on 
the premises. So the question becomes: is the sub-panel capable of supplying 
branch circuits or feeder loads? If yes, then the sum of the breakers 
(potentially) feeding the bus is 180 amps so a 150-amp rating is required and 
the inverters would have to feed the opposite end of the bus bars. If no, the 
code is not clear on the requirement, but obviously the 80-amp breaker in the 
main panel limits the maximum current flowing through the sub-panel. 