    Kent and list,<br>
    And I was half awake this morning and realized my error in <font
      size="3">yesterday's</font> post to which you responded... I said
    "A battery is considered empty at 10.75V (12V), or 1.79 VPC." <br>
    No, it's at 10.5V, or 1.75 VPC, as you have correctly stated. Sorry.<br>
    Allan<br>
    <br>
    On 3/26/2011 12:01 PM, Kent Osterberg wrote:
    <blockquote cite="mid:4D8E29EA.9060208@coveoregon.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <title></title>
      Wrenches,<br>
      <br>
      I noticed an error in my reply below when Allan's second comments
      arrived. Correction: the battery is considered 100% discharged
      (not
      80%) at 10.5 volts (1.75 vpc) under the conditions of use. <br>
      <br>
      Kent<br>
      <br>
      <br>
      <br>
      Kent Osterberg wrote:
      <blockquote cite="mid:4D8D4F98.3030808@coveoregon.com" type="cite">
        <meta content="text/html; charset=ISO-8859-1"
          http-equiv="Content-Type">
        <title></title>
        William,<br>
        <br>
        I'll try to add a little to Allan's and <font size="3">Ronald
          Parades'
          comments.  Nearly every battery manufacturer specifies a
          maximum 80%
          depth of discharge (DOD); that corresponds to about 10.5 volts
          for a
          nominal 12-volt battery. Notice how close that is to the
          default
          setting used by many inverter manufacturers for starting the
          generator
          right away. For deep-cycle batteries, a cycle life in the low
          hundreds
          should be expected for a battery that is routinely discharged
          to 80%
          DOD. <br>
          <br>
          Designing for a lower DOD will result in longer battery life.
          I've got
          a table from Ronald that shows the L16RE battery life
          expectancy is
          about 7 years for a 25% daily DOD. Since that is their
          warranty target,
          it seems like they should specify a 25% daily average DOD in
          the
          battery instructions. <br>
          <br>
          If charging primarily with a generator, 50% DOD before
          starting the
          generator is good compromise (but the generator shouldn't have
          to start
          every day, every other day maybe). Fuel economy really falls
          off the
          chart while charging above 90% SOC. So if you are starting a
          generator
          at 75% and charging to 100% it'll use a lot more fuel that
          using the
          generator to charge from 50% to 80% or 85%. Trouble is that
          routinely
          charging to only 85% SOC will lead to sulfation problems. That
          can
          shorten the battery life too.<br>
          <br>
          Kent Osterberg<br>
          Blue Mountain Solar, Inc.</font></blockquote>