So long as there is a direct neutral connection between the two systems,
the system is not separately derived.  <br><br>
At 04:15 PM 3/11/2011, you wrote:<br>
<blockquote type=cite class=cite cite=""> <br>
What's the best answer when someone asks if PV Systems are
considered<br>
separately derived systems?<br><br>
It still seems to be up to whoever is doing the considering (AHJ), and
I<br>
don't like that answer.<br><br>
I believe the answer is yes they are.  And 690.47 tells us how to
ground<br>
them.  <br><br>
"(C) Systems with Alternating-Current and Direct-Current
Grounding<br>
Requirements. Photovoltaic systems having dc circuits and ac circuits
with<br>
no direct connection between the dc grounded conductor and ac
grounded<br>
conductor shall have a dc grounding system. The dc grounding system shall
be<br>
bonded to the ac grounding system by one of the methods in (1), (2),
or<br>
(3)." <br><br>
Any help is appreciated<br><br>
~Ryan<br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake
Chamberlin<x-tab>        </x-tab>
<br>
Athens Electric<br>
OH License
44810<x-tab>        </x-tab><br>
CO license 3773<br>
NABCEP Certified PV<br>
</font></body>
</html>