<br><font size=2 face="sans-serif">Hi Mark,</font><font size=3> <br>
</font><font size=2 face="sans-serif"><br>
We have stock of them here...</font><font size=3> <br>
</font><font size=2 face="sans-serif"><br>
Part # 808-0232-01</font><font size=3> <br>
</font><font size=2 face="sans-serif">call, 866-519-1470 to order. </font><font size=3><br>
</font><font size=2 face="sans-serif"><br>
Cheers,</font><font size=3> <br>
</font><font size=2 face="sans-serif"><br>
Mark<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Mark Edmunds, P.Eng.</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Renewable
Energies Business</b>  |   <b>CANADA</b>  |   <b>Director
- Advanced Engineering</b> <b><br>
Phone:</b> +1-604-422-2609  |   <b>Fax:</b> +1-604-420-1591  |
  <b>Mobile:</b> +1-604-613-3285 <b><br>
Email:</b> </font><a href="mailto:mark.edmunds@schneider-electric.com"><font size=1 color=blue face="Arial"><u>mark.edmunds@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href=http:/// target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/renewable-energies </u></font></a><font size=1 face="Arial"> 
|   <b>Address:</b> 8999 Nelson Way, Burnaby, BC, V5A 4B5, Canada
<br>
</font><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"Mark Dickson" <mark@oasismontana.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">"'RE-wrenches'" <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">03/02/2011 08:29 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches]  XW Temp sensor</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=2 color=#000080 face="Arial">Does anybody happen to have
a temp sensor for a Xantrex XW inverter?  This is the type that bolts
onto the negative battery terminal.  I am not sure but I think the
Magnum temp sensor may work as well.  We have been trying for weeks
to track one down for a customer from our distributors and Schneider—everyone
says they have it but they don’t. . .</font>
<br><font size=2 color=#000080 face="Arial"> </font>
<br><font size=2 color=#000080 face="Arial">If so, shoot me a message off
list and I will take it.  Used is fine. . .</font>
<br><font size=2 color=#000080 face="Arial"> </font>
<br><font size=2 color=#000080 face="Comic Sans MS">Best regards,</font>
<br><font size=2 color=#000080 face="Comic Sans MS"> </font>
<br><font size=2 color=#000080 face="Comic Sans MS">Mark Dickson,</font>
<br><font size=2 color=#000080>NABCEP Certified Solar PV Installer ™</font>
<br><font size=2 color=#000080 face="Comic Sans MS">Oasis Montana Inc.</font>
<br><font size=3 color=#000080 face="Times New Roman"> </font>
<br><font size=2 color=#000080 face="Arial"> </font>
<div align=center>
<br>
<hr></div>
<br><font size=2 face="Tahoma"><b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[</font><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=2 face="Tahoma">mailto:re-wrenches-bounces@lists.re-wrenches.org</font></a><font size=2 face="Tahoma">]
<b>On Behalf Of </b>Maverick Brown [Maverick Solar]<b><br>
Sent:</b> Tuesday, March 01, 2011 6:58 PM<b><br>
To:</b> 'RE-wrenches'<b><br>
Subject:</b> Re: [RE-wrenches] Home Brew Frequency Switch</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">"I have considered using
a drop out contactor to isolate the inverters from the generator following
a loss of line voltage."</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">I suggest that method above as
the best. Generators can change frequencies under load and other conditions,
etc. so there would not be such a precise control.</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">Line voltage coil relays are also
cheaper and easier to get as compared to frequency controls.</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">The voltage drop out contactor
might be easier to implement using the KISS method.</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">Good Luck!</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=blue face="Arial">Maverick</font>
<br><font size=3 face="Times New Roman"> </font>
<div align=center>
<br>
<hr></div>
<br><font size=2 face="Tahoma"><b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[</font><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=2 face="Tahoma">mailto:re-wrenches-bounces@lists.re-wrenches.org</font></a><font size=2 face="Tahoma">]
<b>On Behalf Of </b>Mark Frye<b><br>
Sent:</b> Tuesday, March 01, 2011 11:20 AM<b><br>
To:</b> 'RE-wrenches'<b><br>
Subject:</b> [RE-wrenches] Home Brew Frequency Switch</font>
<p><font size=2 face="Arial">Folks,</font><font size=3 face="Times New Roman">
</font>
<p><font size=2 face="Arial">I am back on the project where I want to install
grid tied inverters (Enphase) on a feeder located downstream of a generator
and ATS.</font>
<p><font size=2 face="Arial">I have considered using a drop out contactor
to isolate the inverters from the generator following a loss of line voltage.</font>
<p><font size=2 face="Arial">As an alternative, how well might it work
to reset the generator frequency so that it is outside the inverter range?
In this way the inverter would always see the generator as "bad"
energy and therefore would never connect to the generator, only the utility.</font>
<p><font size=2 face="Arial">The nominal frequency range for the inverter
is 59.3 to 60.5.</font><font size=3 face="Times New Roman"> </font>
<p><font size=2 face="Arial">What is the effect on the loads in the household
if the generator frequency is adjusted to say 58 or 62 hertz? Would the
higher or lower number be better? Would this fry everything in the house?
I can't see that making a relatively small change like this would effect
the overall impedance such that a problem with current capacities would
be a problem. It seems like the frequency would be more of a problem for
some devices.</font>
<p><font size=2 face="Arial">Anyone have experience with deliberately adjusting
generator frequency away from 60 hertz as described above?</font><font size=3 face="Times New Roman">
</font><font size=3 face="Arial"><br>
 </font><font size=3 face="Times New Roman"> </font><font size=2 face="Arial"><br>
Mark Frye</font><font size=3 face="Times New Roman"> </font><font size=2 face="Arial"><br>
Berkeley Solar Electric Systems</font><font size=3 face="Times New Roman">
</font><font size=2 face="Arial"><br>
303 Redbud Way</font><font size=3 face="Times New Roman"> </font><font size=2 face="Arial"><br>
Nevada City,  CA 95959</font><font size=3 face="Times New Roman">
</font><font size=2 face="Arial"><br>
(530) 401-8024</font><font size=3 face="Times New Roman"> </font><font size=3 color=blue face="Times New Roman"><u><br>
</u></font><a href=http://www.berkeleysolar.com/><font size=2 color=blue face="Arial"><u>www.berkeleysolar.com</u></font></a><font size=2 face="Arial">
</font><font size=3 face="Times New Roman"> </font>
<p><font size=3><br>
________________________________________________________________________<br>
This email has been scanned for SPAM content and Viruses by the MessageLabs
Email Security System.<br>
________________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Options & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<p>
<p>