Very good. Thank you Peter.<br><br><div class="gmail_quote">On Fri, Feb 11, 2011 at 2:44 PM, Peter Parrish <span dir="ltr"><<a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Short answer: DC/PV side two factors of 1.25; AC side one factor.<br>
<br>
Reasons: the common factor of 1.25 is due to the treatment of PV systems as<br>
continuous sources of power, the second factor of 1.25 is for the "cloud<br>
effect". It is entirely possible to get more than 1,000 W/m^2 on a PV module<br>
if there are large cumulus clouds that don't block the sunlight but act as<br>
pretty good reflectors of sunlight.<br>
<br>
As a result you need to increase Isc (times the number of combined strings<br>
if that is the case) by 1.56, and all computed AC currents by 1.25. Same<br>
goes for and switches and OCPDs.<br>
<br>
Then of course you need to compute the ampacity of the wire being used,<br>
taking care to apply the temperature  correction and conduit fill correction<br>
before comparing to the "maximum current" calculation.<br>
<br>
- Peter<br>
<br>
<br>
Peter T. Parrish, Ph.D., President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
CA Lic. 854779, NABCEP Cert. 031806-26<br>
<font color="#888888"><a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a><br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885<br>
</font><div><br>
<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a><br>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of<br>
</div><div><div></div><div><a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br>
Sent: Friday, February 11, 2011 11:03 AM<br>
To: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
Subject: [RE-wrenches] Calculation of Maximum Circuit Current<br>
<br>
In studying for NABCEP certification I am a little confused about whether<br>
you multiply the short circuit current by 1.25 once or twice (1.56) in order<br>
to calculate maximum circuit current in determining wire size. Same for<br>
overcurrent protection.<br>
<br>
I have always done it twice (1.56) for both PV source circuit and PV output<br>
circuit. Once for over irradiance and once for continuous use.<br>
<br>
But a handout at a recent seminar that I went to totally confused me.<br>
<br>
Can anyone spell it out very clearly?<br>
<br>
Thank you.<br>
<br>
Larry Liesner<br>
Wirewiz<br>
Westport, CT<br>
Phone: 203-644-2404<br>
Fax: 203-557-0556<br>
<a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br>
<a href="http://www.wire-wiz.com" target="_blank">www.wire-wiz.com</a><br>
<br>
<br>
<br>
</div></div><div><div></div><div>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive:<br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br clear="all"><br>-- <br>Larry Liesner<br>System Design<br>Elektron Solar, LLC<br>16 Ketchum St.<br>Westport, CT 06880<br>203-557-3127 (office)<br>203-644-2404 (cell)<br>203-549-0977 (fax)<br>

<a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br><br>