Kindly bear with me as I go "back to basics". #10 cu has been my old standby for bonding the metal solar module frames but in recent years Arthur Ruden @ Sharp told me to use nothing smaller than #8. I don't know if other major PV mfr's have a similar spec or not but before I buy a spool...<br>

<br>The new (and appealing) Tyco SolKlamp product calls for solid wire only, not stranded, if I recall correctly. I've never used the solid material because of the bending difficulty but I now wonder if other grounding methods: WEEB lugs, lay-in lugs, etc. also prefer the use of a solid grounding conductor instead of stranded. <br>

<br>Opinions and education are welcomed. As always, the Wrench List is the Bomb!<br>  <br clear="all">Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>


<br><br><div class="gmail_quote">On Fri, Jan 14, 2011 at 12:45 PM, Kelly Keilwitz, Whidbey Sun & Wind <span dir="ltr"><<a href="mailto:kelly@whidbeysunwind.com">kelly@whidbeysunwind.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">

Peter,<br>
Yes the #10 XHHW (2) we use is green-jacketed, and 90˚ rated. We get it through our local electrical supply house.<div class="im"><br>
<br>
Kelly Keilwitz, P.E.<br>
Whidbey Sun & Wind<br>
Renewable Energy Systems<br>
<a href="mailto:kelly@whidbeysunwind.com" target="_blank">kelly@whidbeysunwind.com</a><br>
360-678-7131<br>
<br>
<br>
<br>
<br></div><div class="im">
On Jan 14, 2011, at 11:04 AM, Peter Parrish wrote:<br>
<br>
</div><div><div></div><div class="h5"><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Great idea Kelly! I didn't know one could get green jacketed USE or XHHW. Do<br>
you have a source? Also, do you think that we might need wire rated "-2" for<br>
90 deg C wet locations. I know that this is not a current carrying<br>
conductor, but roof tops are definitely 90 deg C wet environments. Your<br>
thoughts?<br>
<br>
- Peter<br>
<br>
<br>
Peter T. Parrish, Ph.D., President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
CA Lic. 854779, NABCEP Cert. 031806-26<br>
<a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a><br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885<br>
<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a><br>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Kelly<br>
Keilwitz, Whidbey Sun & Wind<br>
Sent: Friday, January 14, 2011 10:14 AM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] Incompatible Metals<br>
<br>
Peter,<br>
I have never understood the common practice of using bare copper<br>
ground wire on and against aluminum frames and modules. It always has<br>
been a dissimilar metals issue. Just look anywhere copper has set<br>
against aluminum for awhile.<br>
We use #10 green jacketed Cu USE or XHHW conductor and strip away the<br>
jacket at each lug, using No-Ox on that section of bare wire at the<br>
lug. The wire can be tucked in to the module frames and with the PV<br>
conductors.<br>
<br>
Kelly Keilwitz, P.E.<br>
Whidbey Sun & Wind<br>
Renewable Energy Systems<br>
<a href="mailto:kelly@whidbeysunwind.com" target="_blank">kelly@whidbeysunwind.com</a><br>
360-678-7131<br>
<br>
<br>
<br>
<br>
On Jan 14, 2011, at 7:36 AM, Peter Parrish wrote:<br>
<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
One of my students who is currently responsible for standing for<br>
inspection<br>
at their company encountered a inspector who made an interesting<br>
point about<br>
incompatible metals (i.e. copper and anodized aluminum).<br>
<br>
The PV system in question used outdoor rated lay-in lugs to bond the<br>
rails<br>
to bare copper wire (so far so good). The ground wire was then zip-<br>
tied to<br>
the rail to carry it to the point where it entered a junction box<br>
along with<br>
the rest of the PV conductors.<br>
<br>
The inspector was concerned with the fact that the bare copper was in<br>
contact with the aluminum rails and that this might cause galvanic<br>
corrosion<br>
and subsequent failure of the grounding.<br>
<br>
I have never encountered this issue before and I wonder if anyone<br>
else has<br>
and what was the outcome.<br>
<br>
As an aside: I do know that 10 AWG and 12 AWG  solid bare copper<br>
wire can be<br>
purchased "pre-tinned" (maybe not tin per se, but coated). We did so<br>
by<br>
mistake. We used it up, but not before one inspector questioned its<br>
use for<br>
the purpose of grounding our system. We showed him the UL label on<br>
the spool<br>
and scraped off the coating to expose the copper core and that<br>
satisfied<br>
him. To this day I don't know if the use of this wire for grounding<br>
was<br>
among its intended purposes.<br>
<br>
- Peter<br>
<br>
Peter T. Parrish, Ph.D., President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
CA Lic. 854779, NABCEP Cert. 031806-26<br>
<a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a><br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive:<br>
</blockquote>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive:<br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br>