    Jesse,<br>
    Don't waste your time on those batteries; they are all toast. Don't
    replace them with the same; four strings is poor design. Read the
    article about off-grid batteries in the current Home Power, and then
    sell the customer a set of 12 (or 24; either one string or two is
    OK) 2V industrial cells, such as HUPs from Northwest Energy Storage
    or K-series Surrettes. Size unknown. The existing full bank was 1400
    A/hr if the cell cases had black covers, 1600 A/hr if the tops are
    blue, to give you an idea.<br>
    <br>
    BP modules from 1998 would have most likely been 12V 75W or 85W,
    meaning 900-1000 watts; too small an array for that size battery
    bank if the home is used full-time; OK for a seasonal or weekend
    cabin.<br>
    <br>
    Only with new batteries can you even tell what the inverters are
    doing. My hunch is that the inverters aren't at fault. However,
    given the poor quality of the original installation, they likely are
    set to default setpoints, which can charge at a very high rate
    (about 220A at 28.8V for two if the gennie is big enough) but won't
    get batteries full (and can't equalize them), as the default
    setpoints are too low. And I'll bet dollars to doughnuts the default
    setpoints are in place, as the inverters have been shut down
    sometime in the last 12 years, losing any original programming
    settings.<br>
    <br>
    You might see about getting an experienced off-gridder in your
    frozen region to work with you. Maybe Darryl could consult now, then
    make one trip out to set up the system once the new batteries are
    in. This was the classic late-90s system with a later charge
    controller upgrade, but if you have never worked with this
    equipment, you're likely to set it up for a repeat failure years
    down the road.<br>
    <br>
    Just read Jamie's post - while his advice is spot on, of course, you
    need to decide if it's worth your while. I'd be more inclined to try
    his approach if the battery bank was three years old, not 12. That's
    a huge amount of time spent, working with acid and an unknown set of
    hazards, with at best the possibility of a few years' use. I'd
    suggest that unless it's your father-in-law's cabin, and you value
    the chance to hang out there for a week, it's not worth your time or
    the customer's, especially given that you acknowledge having little
    off-grid experience. <br>
    <br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="ProgId" content="Word.Document">
      <meta name="Generator" content="Microsoft Word 11">
      <meta name="Originator" content="Microsoft Word 11">
      <link rel="File-List" href="signature_files/filelist.xml">
      <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>2</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2009-12-09T22:29:00Z</o:Created>
  <o:LastSaved>2009-12-09T22:30:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>52</o:Words>
  <o:Characters>298</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>2</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>349</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
      <style>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.il
        {mso-style-name:il;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
            style=""> Sindelar</b><span style="font-size: 10pt;"><br>
            <a href="mailto:Allan@positiveenergysolar.com"
              target="_blank"><span class="il">Allan</span>@positiveenergysolar.com</a><br>
            NABCEP Certified Photovoltaic Installer<br>
            EE98J Journeyman Electrician<br>
            <b style="">Positive Energy, Inc.</b><br>
            3201 Calle Marie<br>
            Santa Fe, New Mexico 87507<br>
            <b style="">505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank">www.positiveenergysolar.com</a></span></p>
      </div>
    </div>
    <br>
    On 12/29/2010 6:34 AM, Jesse Dahl wrote:
    <blockquote
      cite="mid:009DCB97-9AF2-46F1-80CB-DD16AA5287E5@gmail.com"
      type="cite">
      <div>Wrenches,</div>
      <div><br>
      </div>
      <div>There is a MX60 charge controller with the system, 2 trace
        inverters, and ten BP modules.  Not sure the wattage of the
        modules.... There was no way to get to the roof and and check.
         I have only been there once, it was in October.  The array was
        partially shaded at 1:45pm......</div>
      <div><br>
      </div>
      <div>The batteries (rolls 6V) are the original batteries (12 years
        old....) some have visibly bulged from the freezing. There are
        16 batteries, 4 sets of 4.(24 volts).  </div>
      <div><br>
      </div>
      <div>The cables were a problem in my opinion.  When I was there,
        only 8 batteries were being used.  So there were disconnected
        cables in the battery room.  Cable lengths varied from bank to
        bank, and they were just run across the floor.  </div>
      <div><br>
      </div>
      <div>I will post some photos that I took later today.  And more
        generator information, I'm in my fish house right now and don't
        have my camera!!!!</div>
      <div><br>
      </div>
      <div>Thanks for the help,</div>
      <div><br>
      </div>
      <div><br>
      </div>
      <div><br>
      </div>
      <div>Jesse</div>
      <div>Sent from my iPad!!!</div>
      <div><br>
        On Dec 28, 2010, at 5:20 PM, "Starlight Solar, Larry Crutcher"
        <<a moz-do-not-send="true"
          href="mailto:larry@starlightsolar.com">larry@starlightsolar.com</a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <div><font size="2" face="Arial">Jesse, </font></div>
          <div> </div>
          <div><font size="2" face="Arial">It looks like you said the
              battery was replaced with Rolls. If so, good choice.
              Without extensive regular testing, keeping a log book,
               and possessing the knowledge to do it right, you will not
              really know if you are fully charging the battery to 100%
              SOC. From the information in your post, it leads me to
              think that this is the case.</font></div>
          <div> </div>
          <div><font size="2" face="Arial">IMO, the single most
              important thing you can do for this customer is install a
              battery monitor system. I recommend the trimetric. While
              this will not take the place of skilled battery testing,
              it will give you far more information than you have ever
              had. This is where to start. You will then know how high
              and low the voltage got each day. You will see how many AH
              are removed and replaced each day. You will have eyes to
              see your battery health like never before.</font></div>
          <div> </div>
          <div><font size="2" face="Arial">Please post the size of the
              battery bank, the cables and length used to connect the
              inverter and all the generator information. Perhaps we can
              help more.</font></div>
          <div> </div>
          <div><font size="2" face="Arial">Larry</font></div>
          <div> </div>
          <div> </div>
          <div> </div>
          <div> </div>
          <div>----- Original Message ----- </div>
          <blockquote style="padding-right: 0px; padding-left: 5px;
            margin-left: 5px; border-left: 2px solid rgb(0, 0, 0);
            margin-right: 0px;">
            <div style="background: none repeat scroll 0% 0% rgb(228,
              228, 228); font: 10pt arial;"><b>From:</b> <a
                moz-do-not-send="true" title="dahlsolar@gmail.com"
                href="mailto:dahlsolar@gmail.com">Jesse Dahl</a> </div>
            <div style="font: 10pt arial;"><b>To:</b> <a
                moz-do-not-send="true"
                href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
            </div>
            <div style="font: 10pt arial;"><b>Sent:</b> Tuesday,
              December 28, 2010 11:04 AM</div>
            <div style="font: 10pt arial;"><b>Subject:</b> [RE-wrenches]
              Trace inverters undercharging batteries.</div>
            <div><br>
            </div>
            <div>Wrenches,</div>
            <div> </div>
            <div>I have been in contact with a person living off-grid in
              Northern MN.  She had some problems with her system and
              called me.  I teach a solar class at a local community
              college and have been helping her in my free time (free of
              course!).  </div>
            <div> </div>
            <div>Some of her batteries froze last winter and she said
              she dumped out the electrolyte and put new in........ (6 V
              Rolls)</div>
            <div> </div>
            <div>Her main concern was the batteries never fully
              charging.  She has a very nice Kohler gen, but from what I
              have been told, the Trace inverters may be part of the
              problem with the batteries undercharging.  I have limited
              experience with off grid applications and any help would
              be greatly appreciated.  </div>
            <div> </div>
            <div>Jesse</div>
            <p> </p>
            <hr> _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive:
            <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Home Power magazine</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Options & settings:</span><br>
          <span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List rules & etiquette:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out participant bios:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>