<DIV><FONT face=Arial size=2>I was hesitant to reply because I surely will look 
foolish, but perhaps it may help someone in the future. </FONT><FONT 
face=Arial size=2>I did something very stupid back in 2001 that caused an 
explosion. </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>The battery bank (12 volt, 660AH) was located in a 
metal cargo container next to the wall and set in a plastic container. The 
container had open doors on both ends. The battery was in the absorption cycle 
with heavy gassing. I noticed that the positive terminal was slightly loose. 
Fully aware of the danger of the task I was performing, I grabbed my socket 
wrench and began to carefully snug it down. Even though I carefully observed the 
location of the wrench, I did not think about the steel container wall as 
having a path back to battery negative. It did. I blew the top off a battery 
that I was standing over. Fortunately I was wearing safety glasses or I 
probably would not be here today typing this. There was a water hydrant 
near and I was able to flood my face and body for about 15 minutes. No 
facial scares but a lessen very well learned: Do NOT work on batteries that 
are off gassing. Gassing begins at about 2.3 volts per cell. 
</FONT><FONT face=Arial size=2>If you are a battery novice, I encourage you to 
thoroughly educate yourself and do not neglect your safety gear when working on 
batteries.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Another event I witnessed: In 2007 I was at a 
campground and heard an explosion. The owner of an RV a few spaces down from me 
was opening the battery compartment as I walked up. Inside he had  
un-vented batteries in the same compartment as the inverter and other switch 
gear. His batteries were obviously gassing when something sparked it off. The 
top was blown off a 6 volt battery and he had electrolyte everywhere and a 
damaged cargo door. </FONT><FONT face=Arial size=2>We work on hundreds of RV's 
and sadly I see this kind of poor "workmanship" every week at our 
service center.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Larry Crutcher</FONT></DIV>
<DIV><FONT face=Arial size=2>Starlight Solar Power Systems</FONT></DIV>
<DIV><FONT face=Arial size=2>928-342-9103</FONT></DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=kent@coveoregon.com href="mailto:kent@coveoregon.com">Kent 
  Osterberg</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, December 15, 2010 10:21 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Battery based 
  hydrogen incidents</DIV>
  <DIV><BR></DIV>Sounds like, in general, that the off-grid industry has been 
  fortunate to not have hydrogen explosions.  That's good.  No 
  explosions here either.  But one shouldn't take that as evidence that it 
  couldn't happen.  I don't believe this is a circumstance where it is 
  better to be lucky than good.  That's why I recommend doing the 
  calculations.<BR><BR>Kent Osterberg<BR>Blue Mountain Solar<BR><BR><BR><BR>Dana 
  wrote: 
  <BLOCKQUOTE cite=mid:003601cb9c72$8db6bfc0$a9243f40$@com type="cite">
    <META content="Microsoft Word 12 (filtered medium)" name=Generator>
    <STYLE>@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Century Gothic;
}
@page WordSection1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; COLOR: black; FONT-FAMILY: "Times New Roman","serif"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; COLOR: black; FONT-FAMILY: "Times New Roman","serif"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; COLOR: black; FONT-FAMILY: "Times New Roman","serif"
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.EmailStyle17 {
        FONT-WEIGHT: normal; COLOR: windowtext; FONT-STYLE: normal; FONT-FAMILY: "Century Gothic","sans-serif"; TEXT-DECORATION: none; mso-style-type: personal-reply
}
.MsoChpDefault {
        FONT-SIZE: 10pt; mso-style-type: export-only
}
DIV.WordSection1 {
        page: WordSection1
}
</STYLE>
<!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
    <DIV class=WordSection1>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">Ken 
    – <O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">To 
    meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan 
    into a 4” header with a matching 2.5” inlet as far away on the lowest 
    portion of the battery box.<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">In 
    22+ years in off grid installations I have yet to see or even hear of one 
    hydrogen explosion. I get repeatedly asked why we have to go to the efforts 
    we go to for box and venting. I am not able to provide even one incident 
    that I have heard rumor of.<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">Q 
    - How many battery based hydrogen incidents have happened in our collective 
    experience?<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <DIV>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">Dana 
    Orzel<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">Great 
    Solar Works, Inc<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">E - <A 
    class=moz-txt-link-abbreviated 
    href="mailto:dana@solarwork.com">dana@solarwork.com</A><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">V - 
    970.626.5253<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">F - 
    970.626.4140<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">C - 
    970.209.4076<O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">web - 
    <A class=moz-txt-link-abbreviated 
    href="http://www.solarwork.com">www.solarwork.com</A><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">"Responsible 
    Technologies for Responsible People since 1988"</SPAN><SPAN 
    style="FONT-SIZE: 11pt; COLOR: windowtext; FONT-FAMILY: 'Calibri','sans-serif'"><O:P></O:P></SPAN></P>
    <P class=MsoNormal><SPAN 
    style="COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'">Do not 
    ever belive anything, but seriously trust through 
    action.<O:P></O:P></SPAN></P></DIV>
    <P class=MsoNormal><SPAN 
    style="FONT-SIZE: 14pt; COLOR: windowtext; FONT-FAMILY: 'Century Gothic','sans-serif'"><O:P></O:P></SPAN></P>
    <DIV>
    <DIV 
    style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
    <P class=MsoNormal style="MARGIN-LEFT: 0.5in"><B><SPAN 
    style="FONT-SIZE: 10pt; COLOR: windowtext; FONT-FAMILY: 'Tahoma','sans-serif'">From:</SPAN></B><SPAN 
    style="FONT-SIZE: 10pt; COLOR: windowtext; FONT-FAMILY: 'Tahoma','sans-serif'"> 
    <A class=moz-txt-link-abbreviated 
    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A> 
    [<A class=moz-txt-link-freetext 
    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</A>] 
    <B>On Behalf Of </B>Kent Osterberg<BR><B>Sent:</B> Tuesday, December 14, 
    2010 12:07 PM<BR><B>To:</B> Wrenches<BR><B>Subject:</B> [RE-wrenches] 
    Battery Venting<O:P></O:P></SPAN></P></DIV></DIV>
    <P class=MsoNormal style="MARGIN-LEFT: 0.5in"><O:P></O:P></P>
    <P class=MsoNormal style="MARGIN-LEFT: 0.5in">Fellow Wrenches,<BR><BR>The 
    discussion about battery venting reminds me of a useful and inexpensive 
    program, <A 
    href="http://pocketengineer.design.officelive.com/battery_ventilation.aspx" 
    moz-do-not-send="true">BattMV</A>, for determining ventilation requirements 
    per EN-50272.  EN-50272 is a European standard used to determine how 
    much air flow is needed for a room, I don't know of a equivalent standard 
    used in the U.S.  It takes a surprising amount of ventilation.  
    For a 400-AH 48-volt L16 bank charged at 57.6 volts and 24 amps, it's about 
    7 CFM just to keep the %H2 down to 4%.  A 12-volt Zephyr vent is good 
    for about 5 CFM!   If you think you are venting enough, take some 
    time and study this issue.<BR><BR>Kent Osterberg<BR>Blue Mountain 
    Solar<O:P></O:P></P></DIV><PRE wrap=""><HR width="90%" SIZE=4>
_______________________________________________
List sponsored by Home Power magazine

List Address: <A class=moz-txt-link-abbreviated href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A>

Options & settings:
<A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A>

List-Archive: <A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A>

List rules & etiquette:
<A class=moz-txt-link-abbreviated href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A>

Check out participant bios:
<A class=moz-txt-link-abbreviated href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</A>

  </PRE></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>